MANTENANCE OF ELECTRIC EQUIPMENTS IN HAZATDOUS AREA

I'm working in petroleum company which we use many electric equipments in hazardous areas so it should be follow the international stander.

We use electric junction boxes with type of explosion proof protection EEXd "flame proof" but it was too old " more than 30 years". The strategy of maintain this equipments according to the manufacture was difficult because almost of them have certification number on name plant but it is difficult to get the manufacture maintenance procedure from web sites, so we try to do this maintenance program to be near to stander and the idea of replace all of them not seems to be practical because the large no of them and the production continuity.

So I have an idea which needs to review it mainly depend on prevent the present of flammable mixture around the defected EEXd boxes by using metal ball which divided into tow parts "two hemispheres" with flanged end and have a small valve in one side of the ball half part "see fig 1", and but it around the EX box with some care about the cable entry to EX box then we can get out all gas around the box by using suction pump through the valve and after certain period to be sure that all gas get out we can close the valve.

This idea knows in the 18th century with Air Ball. The air outside the two half of ball makes strong pressure in all direction on the outsides of ball to inside the ball so it is difficult to open it and by this we can approve a vacuum around the EEXd boxes until the new one arrived and replace it according to lone time plan.

But there are some questions:-

1- IF this idea effect the internal component inside the EX box or the box structure it self?

2- If an explosion occurred what is the expected response inside the ball sides?

3- Can this idea consider safe solution for this situation as partial solution until performing long time solution?

4- If there is any other idea to solve this problem?

EEXD

BOX

SMALL VALV
TWO HEMISPHER SHAP
AN EEXd INSIDE THE TWO HEMISHPAR PARTES
FIG 1
Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Maintaining Electrical Equipment in Hazardous Areas

11/23/2009 9:51 PM

This won't work!

Reply
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#2

Re: Maintaining Electrical Equipment in Hazardous Areas

11/23/2009 10:02 PM

Your Idea seems interesting, but over complicated. As I understand it the purpose of an explosion / flame protected junction box is to contain the flash or explosion resulting from shorted wires or other electrical malfunction. All you really want to do is to contain the problem so you don't ignite possible fuel vapors outside your electrical components.

Check the seals on your old equipment and replace as necessary. You don't need to re-invent the wheel, just change the tires on what you have!

All you should need to ensure compliance with international standards is to make sure your junction box is rated for the equipment within.

Drew

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Maintaining Electrical Equipment in Hazardous Areas

11/23/2009 10:10 PM

The short answer is NO! This modification to an Ex d 'flameproof' enclosure (if I read your comments correctly and you want to leave the metal ball connected to the flameproof enclosure) is not acceptable due to the pressure piling effect (and the fact it is a totally uncertified modification).

http://en.wikipedia.org/wiki/Pressure_piling

What exactly is the problem with the flameproof enclosures on your site? Have the flameproof boxes got damaged flame paths or gland seals (or something)?

Please provide more information on the exact nature of the damage.

__________________
jack of all trades
Reply
Guru
Safety - ESD - New Member Popular Science - Cosmology - Amateur Astronomer Technical Fields - Technical Writing - Writer India - Member - Regular CR4 participant Engineering Fields - Optical Engineering - New Member

Join Date: Dec 2007
Location: 18 29 N 73 57E
Posts: 1390
Good Answers: 31
#4

Re: Maintaining Electrical Equipment in Hazardous Areas

11/23/2009 11:11 PM

1. In your post figure has not appeared. Did you forget to paste it?

2. Your idea will not work. When you try to create vacuum, the explosive gases are bound to enter inside your ball. Besides, it is not only the safety, but complying to current standards (which have surely great sense) is mandatory. Your idea can not comply to the standards.

3. Instead of creating vacuum, if you purge it continuously with fresh air drawn from safe area, and get the ball certified under Ex p, it can work, safe and complying to standards.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Maintaining Electrical Equipment in Hazardous Areas

11/24/2009 3:02 AM

The posted idea is absurd, as pointed out by others above.

Maintenance of EEx d equipment is routinely carried out by de-energising and carrying out the required tasks under Permit-to-work systems. The operation should have maintenance procedures in place for this sort of thing, which will be found in a manual. RTFM applies.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#6

Re: Maintaining Electrical Equipment in Hazardous Areas

11/24/2009 7:26 AM

Perhaps you are not aware that flame proof equipments be it EXd or Ex e Or E xn have to be certified by authrised labs like Baseefa,Chesi .No modification is allowed.If there is a minor change made to the design you need to get the tests done again and get a certificate.So pl. do not entertain such ideas.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Aug 2007
Location: Toronto
Posts: 239
Good Answers: 9
#7

Re: Maintaining Electrical Equipment in Hazardous Areas

11/24/2009 4:46 PM

An altogether bad idea! First of all, only qualified people should be allowed to perform electrical maintenance in any situation, and especially so in a hazardous area. Secondly, anyone properly qualified would know that there are maintenance/service manuals available as required by the standards and installation procedures. Thirdly, I'm amazed that the petroleum company's safety committee and management would allow something like this. Are they prepared to face the consequences of allowing untrained personnel to put the whole plant at risk?

Mind boggling!!

Reply
Anonymous Poster
#8

Re: Maintaining Electrical Equipment in Hazardous Areas

11/25/2009 10:01 AM

CONSIDERING U GET NECESSARY CERTIFICATION FOR UR MODIFICATION (U WONT)

1-SHOULD NOT AFFECT THE INTERNAL STRUCTURE IF SUITABLY REINFORCED

2-INCASE OF FAILURE OF SEALS, UR BALL WILL SUCK DANGEROUS GAS INSIDE AND WILL CAUSE A POTENTIAL RISK.

3-THE SOLUTION IS DANGEROUS AND WILL NOT BE CONSIDERED A SOLUTION

4-JUST CHANGE THE SEALS FROM A CERTIFIED COMPANY, EVEN IF THE PRODUCTION COMPANY IS CLOSED IAM SURE SUITABLE ALTERNATIVES AVAILABLE. JUST NEED SOME SEARCHING.