Induction Motors and Undervoltage Conditions

11/23/2009 10:33 PM

Dear All,

Induction motor 3ph-380V 50hz 15kW is running on its full-load, then suddenly voltage drop down to 3ph-300V balance. What will happen to motor? Ignore any protection devices.

Same case as above, but motor is solo-running without loads connected, what will happen to motors?

cheers,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Motors in undervoltage?

11/23/2009 11:25 PM
Register to Reply Score 1 for Good Answer
Anonymous Poster
#2

Re: Motors in undervoltage?

11/24/2009 1:05 AM
Register to Reply
Active Contributor

Join Date: Nov 2009
Posts: 14
Good Answers: 3
#3

Re: Induction Motors and Undervoltage Conditions

11/25/2009 12:07 AM

Induction motor 3ph-380V 50hz 15kW is running on its full-load, then suddenly voltage drop down to 3ph-300V balance. What will happen to motor? Ignore any protection devices.

Same case as above, but motor is solo-running without loads connected, what will happen to motors?

Hi,

In both cases above, Iwill answer "What should happen to the motor" instead of "What will hapen to the motor".

In the first case.......If the voltage drops to 300v , The motor speed should drop.If the motor speed does not drop and the voltage drops further, there comes a time when the speed WILL drop.For all practical purposes we can say that the motor speed will drop.Lets continue....When the motor speed drops, the line current will increase.Asthe line current increases, the temperature will increase. This current increase, if sufficently large enough the overload protection will trip and your motor is protected.If this current increase is NOT large enough to trip the overload protection, then the motor will slowly overheat and burn itself.

Should we ignore the protective device, then unless the maintenance guy turn the motor off, the motor temperature will increase and burn itself up.

In the 2nd case.........On no load the motor speed should not drop. For all practical purposes we can say The motor speed will not drop. Should the voltage drop low enough the speed will drop, the current will increase .......and the 1st case senario takes effect.

The motor will run normally. nothing will hapen to the motor

I have a question for you.

The speed of an induction motor is governed by the formula

n is equal to 120 f /p where

n is the speed of the motor in rpm

f is the line frequency

p is the number of poles.

The speed of an induction motor according to the formula is independant of the voltage. So why in case 1 above,the speed dropped when the voltage dropped.

Regards

Register to Reply
Anonymous Poster
#4
In reply to #3

Re: Induction Motors and Undervoltage Conditions

11/25/2009 1:12 AM

That was good (the also part) let the person think.

But even better - for this home works you had limited to the last part only then based on answer elaborated.

He is certainly going to write verbatim your answer (cut and paste ) and hope the professor does not ask for explanation.

Do you think he is going to be back?

Register to Reply Off Topic (Score 4)
Commentator

Join Date: Aug 2009
Posts: 97
Good Answers: 2
#5
In reply to #3

Re: Induction Motors and Undervoltage Conditions

11/25/2009 7:53 AM

The speed dropped because the rotor lag increased.In a normal motor , there is a certain amount of rotor "slip".If there is no slip, there is no current draw,and consequently, no work being performed.The more slip, the more the rotor current lags the field current, and the more current the motor draws, and under normal conditions, the more work is performed.However, when the voltage drops, rotor slip increases due to insufficient current, initially, and the motor perceives this as an increase in load.As the slip increases, the current increases, and the losses of the motor increase,along with the temperature of the windings.This damaging conditon will eventually lead to motor failure.Thermal damage is accumulative.30 minutes overtemp today plus 30 minutes overload tomorrow has the same effect as 1 hour of overtemp all at once.(given the same temp each time). It does not "heal" when the motor cools down.

If the electrical supply capacity is insufficient to supply the motor at full load, the voltage will drop.In the case of a bad bearing,combined with full load, this may occur if the system capacity is overloaded.

(Disregarding OL, short circuit, and Thermal protection)

Even though the motor is inherently designed for a certain RPM, described by the given formula, when the motor is overloaded by excessive load,or falsly overloaded by low voltage or improper frequency, the rotor slip exceeds a full revolution, and the RPM drops.

A motor actually is more efficient at 10% overvoltage than at 10% undervoltage.

Hope this helps

EZ Street

__________________
I'm too old to know it all, and too young to stop learning.
Register to Reply
Anonymous Poster
#6

Re: Induction Motors and Undervoltage Conditions

11/25/2009 9:00 AM

draws more amps--should maintain the speed because that's determined by phase, not voltage. Forcing more amps through wires designed for lower amperage will cause wires to heat up--not necessarily overheat, but they will get hot. Smell of burning rubber will enter the room as volatiles in insulation turn to gas. Insulation throughout the windings will become more brittle and less effective as complex molecules break down and more carbon is left in its place. Carbon is a conductor, so some power will begin leaking across the windings, causing the equipment to need even more amperage. At some point windings will begin to fuse, insulation will begin to smoke, and if you truly lack any safeguards like overloads or circuit breakers or fuses, you'll wind up with a fire on your hands, a shorted-out motor, and a big rewinding job. An 80 volt drop might not have such dire results, but it will weaken the motor and make it more vulnerable to failure. Engineers tend to design motors like this with only a 10% margin of error, which would have been exceeded after voltage dropped to 342v. Engineers, please make equipment 20-50% tolerant.

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: Induction Motors and Undervoltage Conditions

11/25/2009 11:45 AM

Good answer, and regarding your request; they did make such equipmet in the past decades, but it was oversized and non cost effective.

Register to Reply
Commentator

Join Date: Aug 2009
Posts: 97
Good Answers: 2
#8
In reply to #6

Re: Induction Motors and Undervoltage Conditions

11/25/2009 1:42 PM

I can speak from experience, and theory. The speed will drop.It is the drop in speed of the rotor that causes the increase in amps.The induced field in the rotor is lagging the winding speed.This is called slip.

A 1200 rpm motor does not actually turn 1200 rpm, if it did, it would consume no power. All a/c motors are designed to have a certain amount of slip.

That is why the name plate will state:1175 rpm, 1725 rpm, etc.

The rotating magnetic field, however (the windings) are actually rotating at the ideal theoretical speed (1200 rpm, 1800 rpm, etc.).

A sychronous motor is an exception, but it must have external excitation.These motors are sometimes used for power factor correction.

__________________
I'm too old to know it all, and too young to stop learning.
Register to Reply Score 1 for Good Answer
Anonymous Poster
#9
In reply to #8

Re: Induction Motors and Undervoltage Conditions

11/25/2009 8:37 PM

need a bearing?

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#15
In reply to #9

Re: Induction Motors and Undervoltage Conditions

10/02/2013 8:35 AM

EZ STREET is correct.

Study A/C motor theory.

Learn.

Add a new wrinkle.

Live long and prosper.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#13
In reply to #8

Re: Induction Motors and Undervoltage Conditions

10/02/2013 8:29 AM

Exactly right.

GA!

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Anonymous Poster
#10

Re: Induction Motors and Undervoltage Conditions

11/25/2009 10:18 PM

Im most cases the moter will over heat and burnup

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#14
In reply to #10

Re: Induction Motors and Undervoltage Conditions

10/02/2013 8:32 AM

True statement.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Commentator

Join Date: Aug 2009
Posts: 97
Good Answers: 2
#11

Re: Induction Motors and Undervoltage Conditions

11/25/2009 11:43 PM

"It ain't what people don't know that makes them ignorant.It's what they know that just ain't so"

_ Abraham Lincoln

__________________
I'm too old to know it all, and too young to stop learning.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#12

Re: Induction Motors and Undervoltage Conditions

10/02/2013 6:10 AM

Dear Mr.AbuKhansa,

The Power developed will fall which can be calculated as (300/380)^2= 0.6232 OR 62.32% of the power at 380 Volts.

Speed will slightly fall, i.e. SLIP will INCREASE. Over Heating of Motor will take place. When Load is not on the Motor, NO SIGNIFICANT change will be noticed, except more warm of the motor since the Power Factor is LOW and Heating will be more.

DHAYANANDHAN.S

Register to Reply
Member

Join Date: Aug 2015
Posts: 6
#16

Re: Induction Motors and Undervoltage Conditions

09/01/2015 1:33 AM

A 15 kW, 380 V, 50 Hz motor is running at its rated load/full load and drives a constant torque load. Suddenly system voltages drops from 380 V to 300 V. What would happen to the load?

Nameplate of the motor is: 15 kW, 380 V, 50 Hz, 31.5 A, P.F 0.85, 1465 RPM (Efficiency: 85 %)

When Voltage drops, following will change :-

· Motor Output power

· Motor Torque

· Motor speed

At 380 V and at Full Load:-

Mechanical Power delivered to the load: 15 kW

Electrical Power Consumed by motor: 17.64 kW

Load Torque: 97.82 N.m

Speed of motor at 380 V : 1465 RPM (Slip380V = 1500 -1465/1500 = 2.33 %)

When Voltage Drops to 300 V:-

Torque of motor at 300 V:-

T300V = T 380V (V300 V/V380 V) 2

T300V = 97.82 (300/380) 2

T300V = 60.966 N.m

Motor is able to deliver only 60.966 N.m. It means Torque delivering capability of motor is reduced by 37.68 %.

Speed of Motor at 300 V:

Increase in Slip is

Slip 300V = 1/(V300V/V380 V) 2

Slip 300V = 1.60 or 160 % = 1.6 x 2.33 = 6.06 %

Speed at 300 V = 1409 RPM

Due to increase in Slip, RPM of motor reduces from 1465 RPM to 1410 RPM.

Mechanical Power Delivered to Load at 300 V:-

PM at 300 V = T300 V x Speed 300V

PM at 300 V = 8.997 kW

Mechanical Power delivering capability of motor reduces (40 %) from 15 KW to 9 KW.

Summary:-

Sr #

Parameters

At 380 V

At 300 V

Remarks

1 Mechanical Power (kW) 15 8.997 Reduced by 40 %
2 Torque (N.m) 97.832 60.966 Reduced by 37.68 %
3 Speed (RPM) 1465 1410 Reduced by 4 %

Motor could not drive the load and trips on overload.

"abi bhi jis ko sumhaj na aye ooo khutyy da putur hae"

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17

Re: Induction Motors and Undervoltage Conditions

03/20/2023 8:32 AM

A1) One cannot <...ignore...protection devices....>; there is every chance that the <...motor...> will stall and a <...protection device...> will disconnect it from the supply.

A2) Probably nothing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (6); dhayanandhan (1); EZStreet (3); HiTekRedNek (3); PWSlack (1); shafi niazi (1); Taslim (1); wareagle (1)

Previous in Forum: Maintaining Electrical Equipment in Hazardous Areas   Next in Forum: How to Calculate Locked Rotor Current
You might be interested in: AC Motors, Brushless Motors, Linear Motors

Advertisement