UPS PM Standards

11/25/2009 12:34 PM

My company performs biannual Preventive Maintenance on a UPS system. There are 72 cells in the system. The owner thinks that PM includes battery replacement. We dissagree on that point. What is normal in the industry?

__________________
Timothy P. Gregg
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Active Contributor

Join Date: Nov 2009
Posts: 11
#1

Re: UPS PM Standards

11/25/2009 12:51 PM

The UPS doesnot need much maintenance but you can inspect it regularly.The battery need not to be changed unless you have a problem.The battery maintenance biannually is too long.You can do it once in three months.

Register to Reply
5
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: UPS PM Standards

11/25/2009 1:40 PM

The industry standard does not matter. What does matter is what your contract and component warranties say. If your contract is ambiguous, then I would expect you would provide the labor for any battery replacements found to have prematurely failed along with any documentation or assistance for the battery owner to have the battery manufacturer to honor their warranty. Any additional charges of shipping and/or battery life prorating must be paid by the battery owner. If your contract is not clear and a single post warranty battery has failed, then you must get an executive business decision as to what should be done. Your management may decide that business with this client is so important that regardless of what the contract says the battery will be changed for no charge. Your management may decide that this client is trying to pull a fast one and nothing more than the exact obligations of your contract will be honored. Then again your management may decide that an intermediate response of replacing this one battery will be done as a gesture of good will but the owner must pay for any future battery failures. At this point your management may suggest that all of the batteries may need to be replaced soon and you and your company will be glad to negotiate a fair price.

But you must refer to your contract to answer the fundamental question.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 5)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#5
In reply to #2

Re: UPS PM Standards

11/26/2009 4:04 AM

Regards.

GA for correct answer.

I like to add:

If the UPS is purchased batteries installed & conditions of Warrantee agreed then Supplier & Purchaser have to accept the conditions.

In Pakistan we have provision of purchasing on our own and Warrantee of Battery manufacturer is valid, & that is its value decreases with life of battery.

Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#6
In reply to #2

Re: UPS PM Standards

11/27/2009 1:39 AM

Where the batteries are concerned I absolutely agree with redfred.

Batteries, Capacitors and Fans are consumables and unless the UPS is a leased unit where the supplier is responsible for the "UPS Function" or the maintenance contract is comprehensive and\or specifically covers them (this is unlikely), the cost to replace the batteries is a Cost of Ownership expense.

For the over all maintenance regime, this will depend on the business criticality of the systems supported by the UPS.

For the sites I have UPSs on, I implement the following program: -

Two (2) Online maintenance visits six (6) months apart.
These are usually December and June. This service is a visual inspection, a thermal scan and Battery check with a five (5) minute battery discharge test.
This a "General Health Check"

Two (2) Offline maintenance visits six (6) months apart.
These are usually March and September. This service is all the above, plus the unit(s) are taken offline and an impedance test done on the batteries, the inside is vacuumed and the technicians can check the capacitors and have a general look see as the unit is fully de-energized.

This is because the UPSs are supporting financial institutions or life support or preservation functions.

Ultimately the client will have to decide how important the UPS is to them and how much they are prepared to pay.

The contract will then have to be adjusted to change and they will have to pay for that privilege.

For any UPS battery I use the following rule of thumb: -

If the battery is designed to last for X year, I replace all of the batteries at 75-80% of X years.

On the second or third battery replacement, replace the UPS(s) with current technology. It has payed its way by this stage.

Regards,
Sapper.

__________________
It's all about the Boom! - MythBusters
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#3

Re: UPS PM Standards

11/25/2009 11:50 PM

What is the size of this system, each cell?

Large batteries are made to a standard and must be maintained and charged properly to have a warranty, and for that warranty to be valid.

Batteries are a consumable, and will have a limited warranty, however, the huge batteries to maintain large mainframes are often made with very high quality batteries(compared to car batteries) that will have some sort of warranty/rebuild procedure.

I would not normally think routine maintenance, terminal cleaning, voltage checking, would be contracted to include free batteries, after all most batteries are dead and gone in 4-5 years. There will also be the repair of the high power inverters, if they fail, again, that would not be part of routine maintenance.

http://www.google.ca/#hl=en&source=hp&q=ups+%2Bbattery+%2Bwarranty&btnG=Google+Search&meta=&aq=f&oq=ups+%2Bbattery+%2Bwarranty&fp=768bb7f9acd45c0b

__________________
Per Ardua Ad Astra
Register to Reply
Associate

Join Date: Nov 2009
Posts: 34
#4

Re: UPS PM Standards

11/26/2009 12:38 AM

It is probably tight to the battery warranty. If the warranty is 24 months, you have no reason to leave old batteries. If the warranty is 36 months, you can discuss battery replacement with the owner so that you do all the rest of your PM now and in a year you will just change the batteries. If the warranty is 48 months or more, it is throwing money away to change them every two years.

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

aurizon (1); Haajee (1); pskaran (1); redfred (1); repnitskiya (1); Sapper (1)

Previous in Forum: motor/driver prob   Next in Forum: Help with a toroid

Advertisement