how can we calculate a ct ratio if we dont know
Hobbies - Hunting - Deer and Birds Hobbies - HAM Radio - Achieved Ham Radio license in 2008 Hobbies - Fishing - Fisherman United States - US - Statue of Liberty - Know freedom, no tyranny.  Know tyranny, no freedom. Hobbies - DIY Welding - Beginner
Good Answers: 19
Re: ct ratio
11/30/2009 12:37 PM
Since it's the ratio of primary, input, current to secondary, output, current, then you would need to know how many amps are going in and how many are output. For example a CT ratio of 1000:10 would be 10 amps of output current when the primary current was 1000 amps.
Go green, use a solar powered light saber...
Re: ct ratio
11/30/2009 12:39 PM
inject current on primary side and measure it in secandary side then the ratio is
n= (Iprimary / I secandray)
ex 100/5
ex 600/5
Good Answers: 170
Re: ct ratio
12/01/2009 7:44 AM
The primary current of the CT should be as close as possible but not less than the load current or the rated current of the feeder. The secondary current may be either 1A or 5A depending upon the relay or meter that you use on the secondary.
Re: ct ratio
12/02/2009 3:53 AM
Hi, The other partcipents answered very well. But if you want to calculate the undesignated CT, then please do the following steps to calculate the installed unknown CT ratio;
1. Install a ampere mater on CT. An ampere meter always gives full dial reading on 5 Ampere. Note the reading of the ampere meter Say X=?
2. Check the ampere of power cable (which is passed through CT) by Ampere Clamp meter. Its reading will be Say Y= ?
3. Use this Formula
CT Ratio = ((Y/X)*5):5
Regards