commissioning of LT heater

12/06/2009 1:02 AM

I have to commission the LT heater of 30KW through LT MCC. while meggering the heater(phase to earth) shows value zero. but no connectivity. heater drawing not available. the tank having heater is filled with water. how to megger and proceed further.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: commissioning of LT heater

12/07/2009 3:40 AM

If the phase-to-earth resistance is <...zero...>, then there is a short circuit fault and the circuit, if switched on in this condition, will take out the circuit protective device.