Anonymous Poster

Peak Demand Calculation - Stuck on U

12/09/2009 9:10 AM

Hi all..

I'm working out maximum demand for power consumption on a 3 phase system.

I've got to:

I= (KVA x 1000) / U

= 72.64x1000 / 1.73x230

what I'm stuck on is whether U is as above or whether it is 1.73x415

This is for our 6 way 3 phase board being sourced from the power company.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#1

Re: Peak Demand Calculation - Stuck on U

12/09/2009 10:10 AM

I = 1000,000VA/(1.73x415)V = .....A, for S = 1000 kVA, 3 phase, 415 V.

I = 1000,000VA/230V = ....A, for S= 1000 kVA, single phase, 230 V,

__________________
RSM Elect Specialist
Reply
Anonymous Poster
#2

Re: Peak Demand Calculation - Stuck on U

12/09/2009 10:57 AM

makes a big difference on consumption so

72.64x1000/1.73x230=182.56A VS 72.64x1000/1.73x400=105A

Where did I get 1.73x230 from ??? I'm sure it is used

Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#3

Re: Peak Demand Calculation - Stuck on U

12/09/2009 11:24 AM

??? Your main supply is either 230 V or 415 V. Which is it?

P. S. I is for one leg.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Anonymous Poster
#4

Re: Peak Demand Calculation - Stuck on U

12/09/2009 11:46 AM

So as I have 3 phase 415 supply, 105A is correct ?

72.64x1000/1.73x230=182.56A VS 72.64x1000/1.73x400=105A

Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#6
In reply to #4

Re: Peak Demand Calculation - Stuck on U

12/10/2009 2:00 PM

So as I have 3 phase 415 supply, 105A is correct ?

72.64x1000/1.73x230=182.56A VS 72.64x1000/1.73x400=105A

Why are you even using the 72.64X1000/230Xsqrt3? It doesn't apply! The "230" is volts!

105 Amps is correct.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Anonymous Poster
#5

Re: Peak Demand Calculation - Stuck on U

12/10/2009 7:20 AM

Or to put it another way when I use 1.73x230 what result is that giving me ..?

Reply
Anonymous Poster
#7
In reply to #5

Re: Peak Demand Calculation - Stuck on U

12/10/2009 2:37 PM

Thanks v.much Bill I didn't know if by using 230V what I was getting. Using 400V gives me a lower reading than I expect. As the supply cable is quite warm to touch ..

kva x 1000/1.73 x E =Amps ..

Reply
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#8

Re: Peak Demand Calculation - Stuck on U

12/10/2009 9:34 PM

Dear All,

As shown in the formula;

I = (kVA x 1000)/U, then the calculation is using 72.64 multiplication factor.

Can someone explain me how to get this multiplication factor?

I am really do not understand where is 72.64 factor coming from? What I am thinking, the formula above is only for finding the current. Please correct me if I am wrong.

See below what I understand in finding the peak load demand.

For selection and sizing of the electric equipment such as Gas Turbine Generator (GTG) and Emergency Diesel Generator (EDG), we apply the following formula (may be different with others, but it is look like similar with ETAP).

Peak Load Demand = (Continuous running loads x A) + (Intermittent running loads x B) + (Standby loads x C) + the biggest standby load.

in which diversity factor A=100%, B=50% and C=0%.

Running loads, intermittent loads and standby loads are listed in load list.

Regards,

__________________
RSM Elect Specialist
Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#9
In reply to #8

Re: Peak Demand Calculation - Stuck on U

12/11/2009 8:46 AM

72.64 would be the number of kVA's. Where did you get the number? I assumed that you knew the number of kVA's your equipment required is 72.64 . . .

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#10

Re: Peak Demand Calculation - Stuck on U

12/11/2009 9:01 AM

Hi guest,i believe u guess right or very sure of the information u have given us above.

U as above is 415volts. Why 230v,415v and 400v guess? and root3(1.732)?

In a 3 phase network system,determining factor is root3=1.73. If yr network 3phase voltage is 415v,single phase will be 415/1.732=240v; If it is 400v,single phase will be 400/1.732=230v; and if it is 380v,single phase will be 380/1.73=219v(220v).

Assuming we have 415v 3 phase supply (not 240v single phase),KVA-72.64;I-unknown, Our U will be 415v.

Apparent power S=root3 x U x I (For 3 phase system); I = S/root3.V =72.64 x 1000/1.732x415 =72640/718.78 =101 Amps.

This is the current value u need.However,with the above amperage,the board main breaker may be in the range of 150A-200Amps mccb.200Amps prefarably.

Patrick Whowha

__________________
Patrick Whowha
Reply
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#11

Re: Peak Demand Calculation - Stuck on U

12/11/2009 10:13 PM

Thanks Bill, I am realize that 72.64 is kVA system instead of multiplicatin factors, and thanks also for Patrick that your explanation can be accepted by us.

__________________
RSM Elect Specialist