WE HAVE ONE AIR CIRCUIT BREAKER 3200AMP MAKE GE IN FACTORY MAIN SUPPLY.WE SHOULD LIKE TO SET AT LOW RATING BECAUSE OUR FACTORY LOAD IS 800KVA IT IS POSSIBLE IN THIS CIRCUIT BREAKER.PLEASE SUGGEST IT.
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing
Re: air circuit breaker
12/10/2009 2:01 AM
DEAR FRIEND,
YOU CAN USE IT BY RESETTING OF METERING/OC-SC-PROTCTION WITH CHANGE OF SUITABLE RATING CTS.
Good Answers: 170
12/10/2009 7:28 AM
Please let me know the CT Taps available & the range of the protection release settings.
12/16/2009 12:22 AM
dear friend
Assuming it is secondary of tr connected having 800 KVA, in this case at 415 v FL A shall be 1114.28Amp and you may opt near by ratio of cT say 1200/1 , 50 intanat over current relay /51 IDMT over current , 51 N Inverse time earth fault relay protection shall be adequate.
down stream and up steram protection needs to be relay cordinated