Anonymous Poster

Clamp Meter to Find Current Drawn

12/10/2009 2:18 PM

To find the current drawn from a 250A supply, using a clampmeter do you just measure each phase individually and then add them up... Or do you perhaps just add two currents...


Thanks in advance.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Clampmeter to find Current drawn

12/10/2009 2:37 PM

Current is just current. You would not add anything, we typically are concerned only with the highest current in a circuit. So if someone asked "What is the current draw on this machine?", the answer they are looking for is probably the highest of the measurements because they are asking in order to know if something, such as your 250A service, is getting over loaded.

But if you are looking at wanting to calculate POWER or POWER CONSUMPTION on a 3 phase system, you would want to look at average current.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Anonymous Poster
#2

Re: Clampmeter to find Current drawn

12/10/2009 2:53 PM

Thanks thats a great answer..

But if i then measured 200A on one phase how much more current could I pull ..

The other phases may have a 150A reading

Could I just say 50A is left in the supply at that instant ? I'm guessing it's not that simple

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Clampmeter to find Current drawn

12/10/2009 4:14 PM

Well, if you are in the US, you can only load a circuit to 80% of it's rated capacity continuously, so assuming you have a 250A breaker ahead of this panel, 200A is it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Anonymous Poster
#4

Re: Clamp Meter to Find Current Drawn

12/10/2009 8:56 PM

Unfortunately it is not that simple. You are working in three phase (I assume) - unbalanced load.

If the loads are individual then you can load the other phases/ redistribute the loads.

But if you are on three phase loads (or majority is three phase) then you have to pause and find the reason of the unbalance.

For single phase loads, you can approximately take average (assuming the supply is balanced and the power factors are almost same for all the three)

Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#5
In reply to #4

Re: Clamp Meter to Find Current Drawn

12/10/2009 11:25 PM

Average is not quite right. Square root of (average of squares) is more appropriate. Unless it is a balanced load, in which case, square root of (average of squares) will be equal to average...

Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#6

Re: Clamp Meter to Find Current Drawn

12/12/2009 5:52 AM

It is assumed that the supply is a balanced 3 phase,if u clamp on any phase and you get thesame reading say L1-100A, L2-100A, L3-100A, then yr current drawn is 100Amps,but if one of the three is higher say 105A, take yr current drawn to be 105Amps.

If you dont have a balanced load, u may not get accurate result or information.

Patrick Whowha

__________________
Patrick Whowha
Reply
Participant

Join Date: Oct 2009
Posts: 3
#7

Re: Clamp Meter to Find Current Drawn

12/12/2009 11:59 PM

Hi, if a balanced 3 phase load is connected, all 3 phases- R, Y and B, will show the same current drawn,so the current drawn(I) will be I=Ir=Iy=Ib. If an unbalanced load is connected, the 3 phases will show different currents. The answer to the question of how much current is being drawn should then be Ir in phase R, Iy in phase Y, and,Ib in phase B. This is so because one needs to know the current drawn mainly to find out how much more load can be connected. In a 3 phase supply, lets say a 200A supply, one can connect at max 200A load in each phase. To understand it more clearly, think of the fact that 1 three phase transformer can be formed from 3 single phase transformers. Suppose the rating of a single phase transformer is (supply side)100A:200A(load side). Just like you can connect a 200A load in this transformer, similarly, in a three phase transformer of same rating , you can connect a 200A load in each of the 3 phases.

Reply
Reply to Forum Thread 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); cwarner7_11 (1); JRaef (2); maniac (1); Patrick Whowha (1)