Winding Insulation Resistance

12/10/2009 10:36 PM

hi every one,

i need help on my transformer, we have measured the value winding insullation resistance of secondary-ground of our transformator and the value was 0.1 MegOhm,

the transformator is 1600 KVA, primer 20 KV to secunder 400 Volt,

my question is , is it possible to have 0.1 MegOhm reading, the transformator is still running just fine (not short)?is it not suppose tobe short? when the reading 0.1 MegOhm of secunder-Ground winding insullation resistance?

thank you

regards,

jaeson

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: winding insullation resistance

12/10/2009 11:22 PM

400 volts ÷ 100,000 ohms = 0.004 amps = 4 ma. This is a ground fault (not exactly a short yet) that might not be sensed by any ground-fault detection you may have. But it may be an accident waiting to happen. The next thing it might turn into is an arcing ground fault (not so easily detected, either). Then, when some more insulation burns away--full-bore short.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jul 2008
Posts: 93
#8
In reply to #1

Re: winding insulation resistance

12/19/2009 4:13 PM

Does the "winding insulation resistance test" can replace the " Hi-Pot test " ?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9
In reply to #8

Re: winding insulation resistance

12/19/2009 5:35 PM

The terms "winding insulation resistance test" and "hi-pot test" seem to overlap each other.

For example, see this link: http://cirris.com/testing/guidelines/hipot_testing.html.

This describes 3 sorts of hi-pot testing (dielectric breakdown, dielectric withstand, and insolation resistance). The last of these would be a typical megohmmeter ("Megger(TM)" test. The other two use even higher voltages, I think; thus the winding resistance test would not substutute for the more stringent types.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#2

Re: Winding Insulation Resistance

12/12/2009 9:53 AM

It is not a good reading you have a problem somewhere. what was the insulation test for the primary winding, one would expect similar readings for both windings .Have you checked the oil moisture content it could be a problem?

This unit is heading for a failure.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Associate

Join Date: Oct 2009
Location: kuruman NC. SOUTH AFRICA
Posts: 51
Good Answers: 1
#3

Re: Winding Insulation Resistance

12/12/2009 1:34 PM

i could advise you to check you protection relay for correct operation because definetly you should have expirenced a trip due to the leakage fault current.

__________________
Dan Segami
Register to Reply
Member

Join Date: Jul 2007
Posts: 6
#4

Re: Winding Insulation Resistance

12/12/2009 11:28 PM

Does the secondary have a ground tap, if so did you isolate it?

Register to Reply
Anonymous Poster
#5

Re: Winding Insulation Resistance

12/13/2009 6:16 AM

The standard formula in finding the minimum winding insulation resistance is:(Vrated + 1000)/1000.Therefore, the mininmum secondary winding resistance of your transformer should be 1.40 Mega-ohm.Before taking a winding insulation resistance, the windings per phase should be isolated or disconnected from each other(whether it is connected in wye or delta).

May this answer will help you,merry Christmas!

Register to Reply
Commentator

Join Date: Jul 2008
Posts: 93
#6

Re: Winding Insulation Resistance

12/13/2009 1:47 PM

I think .1 MegOhm is too low value.

The transformer insulation in not good.

Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#7

Re: Winding Insulation Resistance

12/18/2009 10:10 AM

Re: Winding Insulation Resistance

we have measured the value winding insullation resistance of secondary-ground of our transformator and the value was 0.1 MegOhm,

the transformator is 1600 KVA, primer 20 KV to secunder 400 Volt,

Dear jaeson

You can used the following formulae

( Ref : A Guide to Transformer Maintenance by. JJ. Kelly. S.D Myer )

XFMER INSULATION RESISTANCE

R = Insulation Resistance of Winding to Ground at 20oC

C = 0.8 for oil filled transformer at 20oC

C = 16 for dry compound filled or un tanked oil filled transformer

E = Voltage rating of winding under test

KVA = Rated Capacity of winding under test

Insulation Resistance Calculation that still permissible for this XFMER

HV Side

R = ( 0.8 x 20000 ) / √ 1600

= 16000 / 40 = 400 MΩ at 200C


TEMPERATURE CORRECTION FACTOR WITH BASE 20OC

FOR OIL-FILLED TRANSFORMER

OC

OF

CORRECTION FACTOR
0320.25
5410.36
10500.50
15590.720

20

68

1.00

30861.98
401043.95
501227.85

If temperature measurement at 300C ( check the temperature winding indicator) the Insulation Resistance result should be corrected to with based temp 300C, see table.

R at 300C = 1.98 x 400 MΩ = 792 MΩ

For LV Side with V = 400 V

R = ( 0.8 x 400 ) / √ 1600

= 320 / 40 = 8 MΩ

R at 300C = ± 16 MΩ

Those values are the minimum Insulation resistance that still acceptable for safe operations.

Note ;

- These Insulation resistance value valid when the winding in the tank with oil filled

- When the winding at out side the constant "C = 16"

PI / Polarization Index

Polarization Index can be determined by the ratio of 10 minutes resistance to the 1 minute resistance value. Since the leakage current is increases at a faster rate with moisture present that does the absorption current, the polarization index is lowered for insulation in poorer condition.

Polarization Index guide for evaluation of transformer condition

Condition

PI (Polarization Index)

DangerousLess than 1.0
Poor1.0 to 1.1
Questionable1.1 to 1.25
Fair1.25 to 2.0
GoodAbove 2.0

Be careful your XFMER status in the dangerous zone, check also by step voltage test with voltage megger® with Ratio 1:5, ==> used 500 V and 2500 V megger with reverse polarity (negative to copper winding, positive to ground), each test do 1 minute. Its useful to identified the water absorption in the insulation. Result of these measurements 25 % (decrease or increase) at the higher test voltage is presence of excessive moisture.

I used this standard since 1980, to repair / rewind of Power Transformer up to 150 kV, and success....

Rgds

Siswanto

__________________
LOVE FORUM AND DISCUSSION
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard