Transformer Effect

12/11/2009 12:42 PM

Hello to all

Can you tell me if 300 to 400 metres of 5 core 6mm square cable on a winch cause a transformer effect because of being wound together. The application is to run two three phase motors, 4.8 kw each 9.6 kw together. The motors will be run through a purpose made variable speed controller which will control them in sequence. I have been told that a possible cure is to use a type a of choke? can you tell me the type of divice a choke is and how it works. The problem is only when the cable is fully on the winch, also is it possible to use a type of gismo connector to connect the cable in 50m lengths to pass through large blocks on a A frame.

Cheers

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Re: Transformer Effect

12/11/2009 3:50 PM

?

Are you running electrical current through the winch cable? Is it insulated? If the answer to either is, "no," then the answer you seek is, "no."

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Anonymous Poster
#2

Re: Transformer Effect

12/11/2009 10:45 PM

The transformer effect is when the magnetic flux of the cable wires interact with the cable. (At the same place - auto or self inductance)

Assuming your cable is getting wound on a drum, and also assuming it is a 3 phase cable (with neutral), the fluxes of each phase will cancel each other, so that the magnetic flux leaking out of it will be almost zero (theoritically exactly zero)

In this case whether it is wound or kept straight may not matter much.

But unbalanced phases (2 phase, single phase etc) it will have the transformer effect (or high inductance) that you may have to compensate.

But then why choke? I would have expected a capacitor somewhere.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#3

Re: Transformer Effect

12/12/2009 4:08 AM

simple answer..... No!

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User

Join Date: Mar 2009
Location: Northeast corner of the sphere
Posts: 310
Good Answers: 7
#4

Re: Transformer Effect

12/12/2009 8:12 AM

Shouldn't if the phases are in balance. Not sure? Take temperature readings on the drum; if it's warming up, you have a transformer.

__________________
How can you be two places at once when you're actually nowhere at all?
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#5

Re: Transformer Effect

12/12/2009 8:36 AM

having read this again. the burning question is why? are you trying to kill your self or someone else? Safety issue are what... ignored??

and any answer you get should tell you its NOT a good idea, never mind if phases a balanced etc. buy a transformer and be safe, failing that, which church yard do I send flowers

__________________
The square root of nothing is what you make it!
Register to Reply
Anonymous Poster
#8
In reply to #5

Re: Transformer Effect

12/12/2009 12:45 PM

I don't think (And sincerely don't hope) that he is using the cable as the winch rope or vice versa.

During the travel of the head, the drive cable some times are provided a drum so that the lengths don't hang down.

Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#6

Re: Transformer Effect

12/12/2009 10:08 AM

I think you are implying that your motors function properly when the cable is unwound, but not when the cable is wound. If that is the case, could you provide a descriptin the problem?

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#7

Re: Transformer Effect

12/12/2009 10:27 AM

The chokes you have been advised to use are for dampening down harmonics which can be a problem on variable speed drives, however there should be no problem with the winch drum as previous posters said.

As for running a cable connector through blocks they would have to be very large to avoid damaging the connector especially with 350 Mt of cable hanging down somewhere. Also what about wrapping them round a winch drum presumably you will have a support cable to go with it how is this going to lay in with the electric cable.

Normally this would be a purpose designed umbilical cable with no joints and self supporting a very expensive item unless there are some off the shelf umbilicals available.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Active Contributor

Join Date: Jun 2009
Posts: 20
#9

Re: Transformer Effect

12/13/2009 12:47 PM

Cheers Guys

Let me start by saying that safety is not a problem with this type of cable. it is made from polyurethane outer and has a kevlar inner, which is made to take high loads of line pull. It's used through out the offshore industry because of the quality so there is no possibility of electric shocks. When in use it will carry about 16 amps with all phases in balance. The winch that will be used has a radius of 600mm so the bend radius for the cable is well within the manufacturer specifications . Like I mentioned before the control unit will be the first time this type of equipment has been used with it just so there is more controll over the speed. It will have a short duty cycle so the motors and the cable shouldn't have to much of a problem from heat. I will get some spec on the cable just to see if you can give any more information on this subject.

Bully

Register to Reply
Anonymous Poster
#10
In reply to #9

Re: Transformer Effect

12/14/2009 1:39 AM

Anyway your question is answered- electrically no effect.

mechanical and safety aspects ?

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#11
In reply to #9

Re: Transformer Effect

12/14/2009 8:00 AM

You will have a temperature build up in the cable if running your motors at full load with large amount of coils on the drum, you might have to de rate the cable and could end up with not enough current capacity to put full load on your motors.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Active Contributor

Join Date: Jun 2009
Posts: 20
#12

Re: Transformer Effect

12/14/2009 3:39 PM

I found out today that the cable has a flash point of 4000 volts. Also it is used to run very high voltage and current equipment such as deep tow fish and boomer plates for deep sea survey. I have done some calculations for the size of the winch drum size needed for the length of cable. a= number of layers required on drum,b= diameter of drum barrel and c= width between the flanges. so a=200mm b=500mm and c=700m. L=(A+B)x A x C divide by K which is a constant developed for rope. so 700x200x700=98,000,000 divided by 326000= 300 meters. The manufacturer said a drum of 500mm would be fine, this will save money on fabrication and power requirements. after reading all of your comments I am happy the cable will run with out any problems. Total load should be 24 amps not 16 as i said before. 9600 watts, 400 volts. 9600/400=24 amps.

Bully

Register to Reply
Active Contributor

Join Date: Jun 2009
Posts: 20
#13

Re: Transformer Effect

12/15/2009 9:59 AM

Back again. the actual amps will be 18 not 24. I forgot to add in the power factor.

Register to Reply
Anonymous Poster
#14
In reply to #13

Re: Transformer Effect

12/15/2009 11:03 AM

You said 3 phase Then what is 9600/400 ?

The current will be 9600/400√3pf = 17.3A (assuming a pf of 0.8)

Register to Reply
Active Contributor

Join Date: Jun 2009
Posts: 20
#15
In reply to #14

Re: Transformer Effect

12/15/2009 11:11 AM

The motors are 9600 watts combined and 400 volts

Register to Reply
Anonymous Poster
#16
In reply to #15

Re: Transformer Effect

12/15/2009 12:54 PM

P=√3VICosΦ for 3 phase (balanced) system.

= VI CosΦ for single phase.

P = 9600W

V=400 V

CosΦ known/ assuming 0.8

Unknown: I

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#17

Re: Transformer Effect

12/15/2009 7:38 PM

You will have a voltage drop of about 40 Volts at 9.6 Kw trying to attain lull load with this length of cable.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Register to Reply 17 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); Bill (1); brich (2); bullvine (4); garth (3); Jerry New Hampshire (1); welderman (1)

Previous in Forum: Synchronising with the Grid in Saudi Arabia   Next in Forum: Voltage Drop Calculations
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement