Capacitor Bank Calculations

12/12/2009 5:10 AM

have 500kva generator and P.F 07 INEED CONNECTION THE CAPACITOR BANK ,to improvemen power factor to.92

PLS determin the value of KVAR AND TYPE OF CONNECTION

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#1

Re: CAPACITOR BANK CONNECTED WITH GENERATOR

12/12/2009 5:39 AM

Please review your calculations and the total concept of power factor.

YOU have a half megawatt generator and you're asking for help. (Or really an anonymous opinion.)

YOU have the generator. How can it have a p.f of 0.7? (Unless you're out of synch with the grid)

Is the power factor leading or lagging?

Typically it would be considered that the load has the power factor issue, not a generator.

Is your generator a "synchronous" machine? (If yes, then you might investigate the impact of changing the relative phase of the excitation voltage. If no, then it really shouldn't be connected to grid.)

If you had a motor, the answer would be relatively simple.

__________________
Just an Engineer from the land down under.
Register to Reply
Member

Join Date: Dec 2009
Posts: 5
#2
In reply to #1

Re: CAPACITOR BANK CONNECTED WITH GENERATOR

12/12/2009 5:56 AM

power factor of load .7

Register to Reply
Member

Join Date: Dec 2009
Posts: 5
#6
In reply to #1

Re: CAPACITOR BANK CONNECTED WITH GENERATOR

12/12/2009 8:46 AM

Ihave only one generator without network,load power factor .7Lagging,and i have motors

Register to Reply
Anonymous Poster
#3

Re: Capacitor Bank Calculations

12/12/2009 8:05 AM

What is meant by type of connection?

KVAa = KVA Cos Φ

KVAr = KVA sin Φ

Register to Reply
Anonymous Poster
#4
In reply to #3

Re: Capacitor Bank Calculations

12/12/2009 8:07 AM

Also there are quite a few threads on pf compensation. take some time to go through them.

What is the load ? 0.7pf looks to be too lo for any properly designed system, unless it is under quite significantly under-loaded, and then the KVA too will be low.

Register to Reply
Anonymous Poster
#5
In reply to #4

Re: Capacitor Bank Calculations

12/12/2009 8:08 AM

And why that number 0.92?

Is it a homework?

Register to Reply
Anonymous Poster
#7

Re: Capacitor Bank Calculations

12/13/2009 1:29 PM

It is homework.

Register to Reply
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#8

Re: Capacitor Bank Calculations

12/13/2009 10:43 PM

Dear Mogahed,

Would you please to consider other comments related this subject. I give you the KVAR required without knowing your maximum and minimum loads.

Generator rating 500 kVA. PF1 = 0.7 and PF2 required = 0.92.

Based on data above:

angle of fi1 = 45.573 degree (from PF1 = 0.7), and angle of fi2 = 23.074 degree (from PF2 = 0.92).

KVAR required = kVA x PF1 x [tan(fi1) - tan(fi2)]

= 500 kVA x 0.7 x [tan(45.573) - tan(23.074)] = 207.97 kVAR.

Regards,

RSM

__________________
RSM Elect Specialist
Register to Reply
Active Contributor

Join Date: Nov 2008
Location: Bangalore
Posts: 22
#9
In reply to #8

Re: Capacitor Bank Calculations

12/14/2009 12:00 AM

You can not apply PF correction directly to generator, it is applicable only for the load.

Required KVAr= KW(Tan phi1-Tan phi2)

KW= Desired Load

Phi1=Cos-1 initial pf angle

phi2=Cos-1 desired pf angle

__________________
Let Noble Thoughts Comes to Us From All The Sides
Register to Reply
Anonymous Poster
#10
In reply to #9

Re: Capacitor Bank Calculations

12/14/2009 12:18 AM

determine the point of connection capacitor bank after main circuit breaker

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#11

Re: Capacitor Bank Calculations

12/27/2009 4:49 AM

Dear Mr.mogahed,

You have not mentioned the power leading whether it is leading or lagging. if it is lagging, the solution is simple to add capacitor near to load. If it is leading the capator to be removed. In both cases the value of KVAR will remain same. the basic equation you know it.

DHAYANANDHAN.S,

INDIA.

Register to Reply
Member

Join Date: Dec 2009
Posts: 5
#12
In reply to #11

Re: Capacitor Bank Calculations

12/27/2009 5:47 AM

lagging power factor