Current-Carrying Capacity of Underground Cables

12/13/2009 6:20 AM

is there any general rule that underground cables current carrying capacity is always lower than overhead one? or vice versa? as far as i know ccc for underground ones is lower since heat dissipation is harder. But some charts says it is opposite and i am confused.. How might a undeground cable have higher ccc ??

__________________
jinxnao
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Current-Carrying Capacity of Underground Cables

12/13/2009 10:28 AM

Conductors in conduit or direct buried?

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#2

Re: Current-Carrying Capacity of Underground Cables

12/13/2009 10:40 AM

ccc of "in conduit underground > overhead> direct buried ?"

__________________
jinxnao
Register to Reply
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#3

Re: Current-Carrying Capacity of Underground Cables

12/13/2009 10:55 PM

Cables are rated according to the Regulations pertinent for the country. The Laws of Physics being universal, however, in general you will find that cables are rated for a given ambient air and soil temperature. Here in NZ, for example, the ambient air is 30°C (yeah right ) while soil is 15. Thus a cable in ambient air is rated lower than one buried in soil. Soil has a better thermal conductivity than air so the cable rating is higher.

Burying the cable in a duct diminishes the thermal connection to the soil so the current rating goes down.

Thus in NZ buried direct > buried in duct > overhead

In Australia the ambient air is rated at 40. However there are other ground conditions (like sandy areas) and these must be checked wrt cable rating.

Obviously the ratings for your relevant country and the pertinent Regulations must be applied. While ground temperature remains fairly constant, air temp varies considerably. Thus in Alaska I assume

overhead > buried in duct > buried direct.

Alaskans please comment!

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Current-Carrying Capacity of Underground Cables

12/14/2009 3:21 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#5

Re: Current-Carrying Capacity of Underground Cables

12/14/2009 7:34 AM

You have answered your own question. Given that the comparison is between two matching conductors. Underground conductors will always be rated for lower current carrying capacity.

Which charts say otherwise?

Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#6

Re: Current-Carrying Capacity of Underground Cables

12/14/2009 2:54 PM

If u are not satisfied with the answers given so far,pls refer to various regulations and also yr local regulation.

Patrick Whowha