Contactor Coil Vibration

12/13/2009 7:51 AM

i have a wye-delta starting contactors group for 160 kw three phase Squirrel cage motor.

there is high vibration with sound in all contactors all time.

i want to know the reasons for contactors vibration, how to repair ,and is it dangerous or not?

contactor coil is 220 volt.

thank you.

Register to Reply
Pathfinder Tags: contactor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: contactors vibration

12/13/2009 8:23 AM

Have you checked that you're actually getting 220V at the coils?

Has the vibration started recently? Did it starting coincide with any changes or maintenance work?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Participant

Join Date: Aug 2009
Posts: 4
#2
In reply to #1

Re: contactors vibration

12/13/2009 8:55 AM

i checked that 225 v.

the motor stored for one year then we operated it recently.

no changes or maintenance work occured.

i have cleaned the contacts and i raised the volt from 209 to 225

the vibration still exist

Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#3

Re: Contactor Coil Vibration

12/13/2009 2:21 PM

Two possibilities spring to mind :

1) Some dirt or debris has got in between the pole faces and is preventing them from closing. This causes the poles to vibrate heavily.

2) Damage to, or loss of one of the shading rings that are fitted to the pole faces. This also causes the poles to vibrate heavily.

__________________
paulusgnome
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4
In reply to #3

Re: Contactor Coil Vibration

12/13/2009 6:24 PM

Those also came to my mind, but 1) the contacts have been cleaned, and 2) it seems that all of the contactors are evidencing the vibration - unlikely that they've all been damaged.

I'm at a loss.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#9
In reply to #3

Re: Contactor Coil Vibration

12/14/2009 12:35 PM

Point 1) is more valid as the rusting during idle condions after operation.

point seems not as valid as during storage [that is un-used period after some operatin it is the remotest probability.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5

Re: Contactor Coil Vibration

12/13/2009 10:42 PM

As others have said, a broken shading ring or a dirty magnet is most likely to be the cause in most cases. But not here i guess, since you say all contactors are vibrating. Hold on though ... all three? In a wye-delta starter, at any time, only TWO contactors should be on. If all three are ON at any time, there will be a short circuit....?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: Feb 2009
Location: TORONTO, CANADA
Posts: 134
#6

Re: Contactor Coil Vibration

12/14/2009 12:40 AM

Dirt or damaged shading rings is correct answer. 1 coil vibrating may fool you into thinking all coils are vibrating. loss of full contact of the coil laminations will cause higher coil currents eventually burning the coil out. Try disconnecting the mains and energising each coil seperatly to find the bad one.

__________________
Bin there, done that, then done that again and again and now I forgot where I was.Is this what it means to get old?
Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#7

Re: Contactor Coil Vibration

12/14/2009 8:16 AM

For some time now,u hv nt been using this contactors and no maintenance has been done,so they are likely to vibrate(unusual humming) more than usual.

1) Check and makesure yr A1/A2 coil contact terminals are cleaned for good contact.(2) Check the contactor core surfaces and makesure they are properly cleaned with emery paper and they are well seated,and there is no gap or insulation inbetween upper and lower surfaces.(3) Clean the laminations properly and ensure there is no dirt.(4) Check if the core springs are still active or weak and change spring if possible.(5) Makesure u maintain good 220volts potential at the A1/A2 energising terminals of the coils,even when the motor must have started and running.The coils should not be underfed and not overfed with voltage.(6)Test each contactor seperately and check the vibration(humming) sound,energise and de-energise each several times and vibration would minimise or stop.It may nt be all the contactors that are vibrating,so u can change the one affected.(7) If all is giving u too much vibration,then change their coils and cores or rather change all the contactors,and who knows if the contactors are inferior contactors,u may have to change all,but first,test with a new quality contactor and makesure its okay.Also check if the contactors are appropriately rated to handle the load.

If u dont want to change the contactors despite this unusual vibration,due to cost or any other reason,use them until the noise minimise with time,but ensure that u protect yr motor with good undervoltage and phase failure relay should any line/delta contactor fail.This is not a good option remember.

Patrick Whowha

__________________
Patrick Whowha
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#8

Re: Contactor Coil Vibration

12/14/2009 11:23 AM

May not the panel itself that holds the contactors be resonating, because close to the motor?

Register to Reply
Power-User

Join Date: Oct 2009
Location: Istanbul. European side
Posts: 151
Good Answers: 4
#10

Re: Contactor Coil Vibration

12/15/2009 9:50 AM

Pls. make a trial.

Cut off te power line by loosing the motor outputs. This trial will allow you to eliminate the bad contact effects and avoid the confussion.

And now press start to pull the contactors. Two of the three contactors must be pulled at the same time.

Check for any vibration. If yes it may be sourced due dirt on the magnetic surfaces or the shaded pole ring has been broken due the impacts by the time.

You can visually check the (Copper) rings.

Kindest Regards

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: Contactor Coil Vibration

12/15/2009 12:06 PM

My experience on situations like this is;

If it WAS working fine before storage, and you have already eliminated a control voltage problem (*or did you? see below), and NOW it is making noise, and it is TRULY making noise on ALL 3 CONTACTORS, then this is going to be rust on the pole faces of the armatures in the contactors. In my entire 30+ year career I have seen exactly 3 broken shading coils, so the likelihood that you have broken shading coils on ALL 3 CONTACTORS is astronomically small. If it was working before being put in storage, that eliminates the possibility of a bad design, incorrect sequence etc.

* But when you checked the coil voltage, did you check it WHEN the contactors were operating? One issue that comes up a lot is that Star-Delta starters are often used on larger motors, which is sometimes the EXACT reason why you get a voltage drop. So if you checked the coil voltage when the motor was Off, the value is essentially meaningless because the very act of energizing that 160kW motor may in fact cause a severe voltage drop that eventually gets to the control circuit.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate

Join Date: Nov 2009
Posts: 39
Good Answers: 4
#12

Re: Contactor Coil Vibration

12/16/2009 7:36 AM

Apply varnish to the coil and the laminations, it will solve the problem. I had a good experience with the same kind of probem. and I got good results

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#13
In reply to #12

Re: Contactor Coil Vibration

12/16/2009 8:00 AM

Spare the mating-faces

Register to Reply
Anonymous Poster
#14

Re: Contactor Coil Vibration

06/15/2010 5:39 PM

I think the problem is caused by a relay used to turn on the contactors, perhaps in the control circuit.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15

Re: Contactor Coil Vibration

04/26/2024 3:10 AM

<...how to repair...>

Some possibilities:

  • Clean its insides.
  • Tighten anything that is loose.
  • Replace it.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

anand.mandarapu (1); Anonymous Poster (1); Haajee (2); JohnDG (2); JRaef (1); kvsridhar (1); MIKE L. (1); nezihozfirat (1); Patrick Whowha (1); Paulusgnome (1); pennokio (1); PWSlack (1); Yuri B. (1)