Anonymous Poster

LT Generator or HT Generator?

12/16/2009 3:03 AM

I am working on a turbo generator sized at 3.5 Mwe. Is is advisable to use LT generator ( 415 V ) or HT at 11 KV. Technical and economical suggestion in selection on either HT or LT generator based on 3.5 Mwe.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Generation Voltage selection

12/16/2009 3:05 AM

The distance from the generator to the load is a factor.

The sizing of cables for those two voltages is a factor.

The value of any step-down transformer at the load end is a factor.

The location on the planet is a factor.

The value of local labour is a factor.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Feb 2009
Location: India
Posts: 155
#2

Re: LT Generator or HT Generator?

12/16/2009 11:16 PM

LT generator will be bigger and heavier than HT generator for the same MW capacity. Pl check. I am only mech engr.

Reply
Anonymous Poster
#3
In reply to #2

Re: LT Generator or HT Generator?

12/17/2009 1:43 AM

check yourself cable size and number of cable runs required to handle fault currents and electrical safety protections needed that has to be catered if you go for 3.5MW Lt generator you could decide yourself

crm

Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#4

Re: LT Generator or HT Generator?

12/17/2009 3:58 AM

If u use LT Generator,u will be handling a heavy current of about 4869 Amps.

If u use HT Generator,u will be handling a lower current of about 183.7 Amps.

Handling lower current to do same job is safer and materials are cheaper among other reasons.

Use HT Generator

Patrick Whowha

__________________
Patrick Whowha
Reply
Anonymous Poster
#5
In reply to #4

Re: LT Generator or HT Generator?

12/17/2009 2:11 PM

hi,

if use HT generator u will be handle lower current means low losses, less requiremet of cooling, less requirement of space,less maintenance,& cheap as compare to lt generator because of generator winding weightis low so may factors constrin & easy to transport electricity with high voltage with less line losses .

so thats why preffered HT generator

tmp