HVAV Chilled Water System

12/16/2009 8:03 AM

An Engineer by Default has designed a chilled water HVAC system with DRV/Balancing walve in the inlet of chiller. Does anybody approve of this?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: HVAV-Chilled water system

12/16/2009 8:05 AM

What is, "An Engineer by Default"?

Register to Reply
Commentator

Join Date: Jul 2008
Posts: 63
#6
In reply to #1

Re: HVAV-Chilled water system

06/04/2010 1:40 AM

U r using computer and asking me what is "BY DEFAULT"

Register to Reply
Active Contributor

Join Date: Dec 2009
Location: Malaysia
Posts: 14
#2

Re: HVAV-Chilled water system

12/16/2009 8:19 AM

What is engineer by default define? for which applications were reported too? could you please describe in details on where these been address? e.g. ASHRAE, ANSI or etc. provide us with the detail description.

__________________
LifeCycle of Engineering
Register to Reply
Commentator

Join Date: Jul 2008
Posts: 63
#3

Re: HVAV-Chilled water system

12/16/2009 8:54 AM

An Engineer by Default is a Butcher who is not professionally qualified but aways acts as one going arount butchering things he has no knowledge.

DRV/Blancing valves are installed in a HVAC system Chiller out let water line. If you install in the inlet, there will be turbulance in chiller and it will not be flooded with water which is must for super heating refrigerant to leave to compressor. U can see in CRANE valve cataluges the postion where this has to be installed.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: HVAV-Chilled water system

12/16/2009 9:03 AM

<...install in the inlet, there will be turbulance in chiller and it will not be flooded with water which is must for super heating refrigerant to leave to compressor...>

Does the installation agree with the "for construction" P&ID?

  • If not, then change the installation so that it does.
  • If it does, then query the process and controls design with the relevant designer(s).
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #3

Re: HVAV-Chilled water system

12/16/2009 9:11 AM

Thanks for the explanation. Butcher I understand. So, this Butcher put the goesoutta valve on the goesinna side?