This is a little longwinded and I will try and fully explain the situation so please bear with me.
I am in Iraq, our living accommodation and shower/toilet units are CHU's (containerised housing units)
Where possible we use 5 wire systems for all CHU's
The electrical installations are tested periodically, now every CHU has its own CPC running with the main SWA cable, the armouring are not used as the 5th wire but are bonded to ground at one end. Each CHU has a ground rod 10 feet long and 3/4 of an inch thick, the ground rod is connected to the frame of the CHU with a 10mm ground. The CDP (consumer distribution panel) has an equipotential bond of 10mm cable from the ground bar to the frame of the CHU.
Now we carry out earth fault loop impedance tests along with visual inspections for signs of overheating and general electrical breakdown.
Today while I was testing a shower unit, all of the efli readings were virtually the same , around 1.6 to 1.9 ohms with 190 ish amps, they were all type c rcbo's protecting the circuits, with a 63a 100ma main 4 pole rcd, the readings are all just over the limit for the type c breakers so I investigated further, I removed the connection for the ground rod and retested - 64 ohm's 4 amps :), there was no main cpc coming into the abb unit, I traced the cpc and found it was disconnected in the abb unit socket (all feeds to chu's are on mk commando plugs with sockets on the outsides of the units).
I reconnected the ground rod and i realised the toilet abb unit had a ground rod 18 inches from the shower abb unit, so the fault path was down the shower abb unit ground rod through the ground 18 inches and up the toilet abb unit ground rod back to the SDB using the toilet cpc.
Now everything is on generator power with the generators bonded at the centre tap to ground.
My question is if I take a Zdb reading at the panel using the fluke 1653B as it has the high current option so I only need to use the red and green lead, can I take the live + ground efli reading and reference it to a live + neutral efli reading to prove if the CHU's have a main cpc connected rather than having to disconnect the ground rod to check? I realise over length the R1 + R2 reading will slightly differ from the R1 + R1 reading, I also realise that I will have to make sure the main breaker is off at the CDP so I don't get any readings through equipment. But realistically the ground and neutral have exactly the same potential back at the transformer so unless i am missing something the readings should be vertually identical unless the main cpc is missing?