NGR Sizing for Three Parallel Generators

12/27/2009 9:52 PM

Hi Guys,

I have currently 3 generators operating in parallel and i would like to design a common grounding system for these 3 generators.

I intend to connect the neutral of the 3 generators to a common neutral busbar and then from the neutral busbar connect to a common NGR panel.

As such, i would like to know how to size the NGR panel suitable for this application and what should be the rating for the CT used for this application.

The generators are operating at a system voltage of 6.6kV.

Your help is much appreciated !

Thanks and Best Regards

__________________
There is no limit towards how much one can learn.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: NGR Sizing for Three Parallel Generators

12/29/2009 3:18 AM

NGR sizing depends on what % of winding you want to protect through differential protection and the remainning by REF,

Register to Reply
Anonymous Poster
#2

Re: NGR Sizing for Three Parallel Generators

12/29/2009 4:07 AM

Hi,

First of all the system protction is need to be performed for your three Generators that are going to be operated in parellel condition. To do so, the basic short circuit current calculations should be performed, then only we can select of the type of NGR to be used and CT ratio.

You have to provide the existing soil resitivity, cable size & type, cable race-way and complete electrical data for all appliences.

And further, the most important is your power reqirement. Total capacity of your generators (6.6 KV) and type of power utalization.

SK Engineer India

Register to Reply
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#3

Re: NGR Sizing for Three Parallel Generators

12/31/2009 1:56 AM

Dear Sir,

If I am not mistake you ask about the NGR sizing.

Used this formula: I ground fault = {V/(Z1 + Z2 + Zo + 3R)}

in which Z1 is a positive sequence, Z2 is negative sequence and Zo is Zero sequence impedances. You have to get those data from your generator manufacturer, R is NGR sizing. Assumed fault located at generator feeder.

In common practice we have to decide the ground current current first, let say 40 Amps for 10 seconds (It is implemented on 6.6 kV, 1.8 MVA diesel generator).

For a certain condition the generator impedance is too small compared to R, and the calculation result is only slightly different. So, we can conduct simple calculation by eliminating Z1, Z2 and Zo for estimation purpose.

R = [Vln/I]. Vln = voltage line to neutral = 3.81 kV. I = 40 Amps

R = 3.81kV/40A = 95.25 Ohm.

Note: If three generators are operated in parallel, each generator will contribute 1/3 of groundfault current. So, you have to set generator protection refer this value (lower), if higher than this value, your generator protection cannot see the groundfault.

Where will you put the CT?

You can select the CT ratio 50/1 located between common ground busbar and generator star point (for better coordination).

Also you have to select the relay range setting consider the generator running paralel or stand alone.

If you put the CT between common busbar and NGR you cannot make a good coodination. CT located at this location cannot recognize which the generator fault to ground.

We can implement both locations if it is justified.

You can contact the generator and NGR manufacturer for more comprehensive calculation.

__________________
RSM Elect Specialist
Register to Reply
Anonymous Poster
#4
In reply to #3

Re: NGR Sizing for Three Parallel Generators

06/18/2010 11:04 PM

Ok so a guy has three generators all three are different wattages say between 1000 and 1500 watts and 110 to 120 volts.

The cycle is not even the same b/c the rpm of the generators hasn't been set, which is a easy thing to due with two light bulbs in line plugged into the generator and a household outlet.

Anyway if a resistance load device, such as a heating element equivalent or a little less to the generators output is used in line with the three connected to a common bus bar what's the problem??

You might have one heating element slightly warmer then the others.

Geets_room@hotmail.com

Register to Reply
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#5
In reply to #4

Re: NGR Sizing for Three Parallel Generators

06/20/2010 9:00 AM

I do not understand with your opinion. See the main topic as written by first posting above.