Conductivity of DM Water in Storage Tank

12/30/2009 11:07 PM

Dear All,

We are operating Gas Based Combined Cycle power plant. We have 2 streams of DM Plant with Solid Contact Clarifier as a Pre Treatment of raw water.

We are producing DM Water at 30 M3/Hr. flow with < 0.1 microsiemens/cm conductivity. This DM water is stored in 500 M3 air tight storage tank. Although this storage tank is provided with KOH Breather,the Conductivity of this DM water reached to 0.65 microsiemens/cm. Due to this Cation Conductivity of Live Steam remains 0.24 microsiemens/cm which is higher than recommended value 0.20.

What action can be taken to bring down the Conductivity of DM water in Storage tank outlet. Please suggest.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Conductivity of DM Water in Storage Tank

12/31/2009 3:07 AM

What is the temperature in the tank?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Dec 2009
Posts: 4
#5
In reply to #1

Re: Conductivity of DM Water in Storage Tank

01/03/2010 10:24 PM

Temperature in tank is Atmospheric @ 35 Deg. C

Register to Reply
Power-User
Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Sep 2009
Location: Tulsa, Oklahoma
Posts: 123
Good Answers: 4
#2

Re: Conductivity of DM Water in Storage Tank

12/31/2009 10:37 AM

What material is storage tank made of?

Is the tank lined with a coating?

What sources of water other than from the DM system goes to the tank?

Is the tank well grounded/earthed?

What type DM System?

Is the DM water . . . also de-ionized? (Demineralization may not de-ionize!, in fact it may ionize the water, depending on how DM is done)

Look at all fittings and connections, dissimilar metals build an ionization cell, strip ions from one and depositing on the other . . . the water becomes the electrolyte (even if very pure)

If you pump the water with a centrifugal pump . . . seals may be allowing air inleakage.

Is your water source contaminated by hydrocarbons or solvents . . . materials that may not show up on the monitoring system . . . but do breakdown into ionic contaimation?

__________________
A government big enough to give you everything you want, is strong enough to take everything you have.
Register to Reply
Participant

Join Date: Dec 2009
Posts: 4
#6
In reply to #2

Re: Conductivity of DM Water in Storage Tank

01/03/2010 10:41 PM

Storage Tank is made of M.S (IS2062)

Tank is lined with coating.

Other than DM System source to the storage tank, recirculation line of DM Water feed pump is also connected to the DM Storage tank.

Tank is well grounded.

It is conventional De-Mineralization Plant.

DMF ---> ACF ---> SBA ---> DE-GASSER ---> SAC ---> MIX BED ---> DM STORAGE TANK.

DM is also De Ionized. The Conductivity of inlet DM water to storage tank is about 0.03 MicroSimens/cm.

How can we assure ionization of dissimilar fittings & connections in DM Water.

Register to Reply
Anonymous Poster
#3

Re: Conductivity of DM Water in Storage Tank

01/01/2010 7:51 AM

conductivity reduces in storage . better use on line as far as practicable.

Register to Reply
Participant

Join Date: Dec 2009
Location: Allentown, PA
Posts: 2
#4

Re: Conductivity of DM Water in Storage Tank

01/01/2010 8:54 AM

While not a direct correlation to your application, this may provide a useful suggestion. During a deionized water plant upgrade for an FDA-regulated cosmetics plant, we also had a large storage tank to store our purifed water. When water was not flowing thru the tower system, we also noticed a degradation of water quality, so we implemented a recirculation loop just prior to the tank to continually polish the water quality when new water was not being processed. When the tank called for water, a valve would open and new water would be processed to fill the tank. As another note, conductivity is very temperature dependent, and instrumentation to measure purified water is typically done at ambient temperatures, not at elevated temperatures. Likewise, sampling containers can immediately add contamination to the water, so depending on how you are sampling and then measuring the conductivity from the steam, you can be introducing contamination into your sample that is giving you false readings. Making, storing, handling, and testing of purifed water is a very sensitive undertaking, and many sources of contamination / errors can be introduced.

Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#7

Re: Conductivity of DM Water in Storage Tank

10/25/2011 7:54 PM

I am from Pharmaceutical industry, and understand that for your application SS 316 L tanks which we normally use is over kill. I think maintaining the conductivity, that too below decimal point is very difficult. In our inductry we find it difficult to maintain below 1.0 micro semens/cm. We generate conductivity at about 0.06 micro siemens and by the time water reaches to the storage tank, conductivity goes to 0.7 micro siemens/cm. We do come across situation when the even glass vials for injection fluids start releasing contents in the product, not sure ehetehr epoxy will hold its integrity.

I was lookign up whetehr the Nitrogen blanket over the tank will help OR a KOH bretaher will be helpful, and came across this discussion group.

Will look for some help from group members.

Register to Reply
Participant

Join Date: Dec 2011
Posts: 2
#8
In reply to #7

Re: Conductivity of DM Water in Storage Tank

12/19/2011 5:37 AM

The conductivity depends on the value of the pH, on the temperature of measurement and on the amount of CO2 which has been dissolved in the water to form ions.

You need to reduce CO2 from the air coming through the breather in the tank.

Using CO2 scrubber for water tanks for Pharmaceutical industry is better and safer then Nitrogen blanket. There are several types of CO2 scrubbers. Scrubbers with soda lime can not keep the stable CO2 level after scrubber and you need to change the scrubbing material often. So most preferable is automated system for water demineralization through the removal of CO2 from supply air. CO2 Scrubber for tanks is to be installed at the tank vent to prevent CO2 entrance in to the DM water storage tank. The intention is to avoid CO2 present in the air entering the tank. If you keep CO2 level in incoming air at 5 ppm, you can keep water PH stable.

Register to Reply
Participant

Join Date: Dec 2011
Posts: 2
#9
In reply to #7

Re: Conductivity of DM Water in Storage Tank

12/19/2011 7:11 AM

Here is the abstract from one research paper :

In the pharmaceutical,semiconductor, food/beverage, and power generation industries, pure water is often exposed to air (and CO2), thereby increasing its conductivity and giving the appearance of a contaminant in the water.

In ultrapure water, dissolved CO2 from the atmosphere causes increased conductivity and decreased pH relative to the expected values of 0.0550 mS/cm and 7.00 pH at 25°C. For example, the conductivity of ultrapure water increases to approximately 1 mS/cm and the pH is lowered to 5.7 when water is exposed to air with a CO2 content of 0.033%, a typical value for pure air. The other primary components of air do not form ionic species and do not affect the water conductivity.

All the research information you can get here

http://my-mt.com/thornton/pdf_files/tech_pubs/cond_CO2.pdf

So to keep conductivity on desirable to need level you need to keep temperature lower then 25°C, you need to lower CO2 level in incoming air to 5ppm and keep it stable.

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Alfaintek (2); Anonymous Poster (2); nukesub629 (1); PWSlack (1); rmaurer (1); Technical Man (2)

Previous in Forum: chainsaw oiler question   Next in Forum: I Have a Hobby

Advertisement