Condenser Motor

12/31/2009 2:07 AM

Hi.......Could I use condenser motor 750w, 960rpm (400V/60Hz) instead of 580w, 900rpm (415V/60Hz) motor? Does other effect could arise if I decide to use this motor? Please advise.tq

__________________
Kimie
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Condenser motor

12/31/2009 3:21 AM

In principle, yes electrically, though the arrangement will be less energy-efficient. The larger motor will be doing a smaller percentage of its available output. Starting currents will be higher, and this needs to be taken into account in the design and selection of the motor overload protection device, the power circuit protection device and the power circuit conductor sizes.

Mechanically, why is there a difference in speeds, and does this matter to what is being driven?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#2

Re: Condenser Motor

12/31/2009 9:41 AM

You could not if it were vice versa. But as it is, you can simply put a restriction to the air flow to avoid overcondensing, if necessary.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Condenser Motor

12/31/2009 6:48 PM

Are you using the same fan blade, moving it from the old motor to the new? (If it is the same blade, 580 (960/900)3 ≈ 704 W < 750 , so this aspect looks okay.)

If the new motor will use a different blade, you should compare the air flow of the old and new combinations; the new one should have equal or a bit greater flow.

The difference between 400 and 415 volts may be within the permissible range of either motor, but you might want to check that, too.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.