% Impedance

01/01/2010 12:26 AM

what should be the percent impedance of a three phase, 250KVA, 11/0.415kV transfromer?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#1

Re: % Impedance

01/01/2010 3:01 AM

Dera Sir,

The transformer % impedance of 250 kVA, 11kV/0.415kV can be defined by testing in manufacturer shop test. The manufacturer itself shall follow the standard for a certain kVA rating.

Refer to Tabel 1 of IEC 60076-5, Impedance voltage at rated current, given as percentage of the rated voltage of the winding to which the voltage is applied.

So,the above transformer (250 kVA)shall follow transformer kVA range rating "Up to 630 kVA" and the impedance voltage is 4%".

The manufaturing tolerance on the above transformer percent impedance voltage is ± 10% for two winding transformers.

For short-circuit caculation we can use this value if there is no other information of transformer impedance available.

Regards,

__________________
RSM Elect Specialist
Reply Score 1 for Good Answer
Anonymous Poster
#2
In reply to #1

Re: % Impedance

01/03/2010 4:50 AM

If you are using the ANSI standard, you could use 5.2%.. You could solve it if you have the allowable maximum short circuit current you expect the transformer to hold. But always see to it that it falls in the range given by the standards you are using.

Reply Score 1 for Good Answer
Member

Join Date: Nov 2009
Posts: 8
#3

Re: % Impedance

01/05/2010 4:38 AM

According to me if you want to calculate the % impedance of 250KVA then u have to give us details of short circuit test like value of load loss at ambient temperature, applied rated current , ambient temperature and wheather transformer winding is of copper or alluminium. According to IS Standard:2026 rated % impedence is 4.5% +/-10% IS Tolerence.

Reply
Reply to Forum Thread 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); rasam.syamsudin (1); saurabhpareek002 (1)

Previous in Forum: Megging wiring   Next in Forum: Voltage potential discovered across pipes in hot water heating system

Advertisement