Rewiring 2 120V legs to one 240V leg for oven elements

01/02/2010 6:54 AM

Hello Everyone and Happy new year.

I am into a project and I need some opinions and help.

I have a USA Whirlpool oven/microwave. I moved to Europe and I am facing the 240v->120v issue. The issue is basically on the fact that the oven has 2 Live cables and a neutral cable thus I cannot use a regular step down transformer. I researched for centertapped transformers as well as other methods. I ended up in studying the schematic and it seems to be a solution which I need your opinion and help. It seems that the oven is using the second 120v leg L2 for the oven's elements only (L1 120v-L2 120v out of phase -->240v). I think I can isolate the supply wiring L1/L2 that powers up the elements. Attached is the official Whirlpool schematic. I highlighted with color lines the different cabling supplying the different components of the oven. Please take a look at it and let me know if this is possible. Please note that the specs written on relay A, and Switch B & C (see diagram) are rated at 240V. If I cut the wire at point 1 on diagram and supply 240V Live(L) as well as cut the wire at point 2 on diagram and connect it to Neutral(N) will this solve my problem. It looks like a simple cabling especially since the switches and relay work at 240v-30A. Are the USA elements capable of handling 240V L to N instead of 240V L1-L2? If it is going to work then I can supply L1-N with a heavy duty 1500W step down transformer which I have for just the electronics, fans, circuitry and microwave. Also do you think that I will need to disconnect the Electronic Filter (upper right corner of schematic), since there will be nothing connected to L2? Thank you in advance. Lambros

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Dec 2006
Location: South Africa
Posts: 200
Good Answers: 1
#1

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/02/2010 6:06 PM

Hi. Sorry to be the one to tell you this, but to my opinion I think you will be better off buying a new oven/microwave. Store the old one for the day you move back to the States, then you sell the new one or bless a friend with it. The time and effort plus the costs of the heavy duty step down inverter.... Then if something goes wrong you will end up buying a new oven anyway and then you have the step down inverter -expensive paperweight. Good luck on the decision.

__________________
"Remember... if women don't find you handsome, at least let them find you handy." - Uncle Red
Register to Reply
Member

Join Date: Nov 2009
Posts: 7
#2
In reply to #1

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/03/2010 4:08 AM

Hi. Thanks for your reply.

Buying a new oven is always a solution, but I was wondering if my idea stated above will work. If any of you have any opinions please let me know. Lambros

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/03/2010 4:37 AM

Have you thought about the lite bulb,transformers and other low voltage wiring and USA appliances are made for different cycle. Sell it or store it for you may have foregotten the low volt transformers and circuit board and clock.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#4

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/03/2010 6:38 AM

Please please please note to all readers, if you are moving to or from a region with completely different mains voltages and frequencies, DO NOT TAKE ANYTHING either electronic or electric with you.

Even some cell phones may not work either due to varying standards.....

I have met several US Citizens that have emigrated to Germany and brought their cars!!! Often major investment is needed to get them legally on the road.....its simply not worth it.....Sell or store before moving.......

Marking as off Topic.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 4)
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#6
In reply to #4

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/03/2010 11:24 PM

Why off topic?

Certainly for major appliances, I agree.

On the other hand, many devices (including the Mac I'm typing on) now come with power supplies rated for 100-240VAC 50/60 Hz. Such devices should work almost anywhere. These devices also are very forgiving on wave shape. I've used this Mac many hours in my car, powered by a cheap 12V inverter with a square-wave output.

Hopefully, the vast majority of people reading this forum are capable of reading (and some level of understanding) the power requirements on their electrical devices...

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#7
In reply to #6

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/03/2010 11:55 PM

Modified or square wave is suitable for most consumer electronics

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #6

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/04/2010 5:41 AM

I felt it was easier for all concerned to err on the side of safety.

Naturally there are some devices that will work anywhere.....your example was excellent.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Anonymous Poster
#5

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/03/2010 10:23 AM

I'm not sure but i think you have to consider the hrz of us 60 and overseas being 50

Register to Reply
Member

Join Date: Nov 2009
Posts: 7
#9

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/04/2010 6:56 PM

Hello all and thanks for your replies.

The topic here was the attached ckt and possible rewiring.

The reason I started this topic was to get your opinions and share with you my and your thoughts after you study and evaluate the ckt.

So please if you can read the ckt and have any opinions on my idea regarding supplying the element with direct 240V, please reply and comment on this thread.

Kindly, Lambros

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#10
In reply to #9

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/04/2010 8:58 PM

Unfortunately, your diagram isn't quite readable at CR4's standard resolution. Also unfortunately, most of us don't understand how a couple of people have succeeded in posting much higher resolution images.

If you succeed without blowing something, I'll be most surprised! A 1500W transformer is marginal at best for most microwave ovens.

I agree with the others: store it and buy a new unit. Your life just might depend on it!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Power-User

Join Date: Feb 2009
Location: TORONTO, CANADA
Posts: 134
#12
In reply to #9

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/04/2010 11:36 PM

From what I see of the circuit L1&L2 is the 240 v supply. your 240 v supply is the same thing! Wether one leg is "neutral" doesn't matter to the heater elements. I would keep the 240 (L1 & L2) as 240 and resupply the electronic control. I think I see another control transformer for the electronics (center of diagram?) either change this or supply 120v from another transformer. As to the micro wave can't see enough!

What everyone says is correct if you do changes and happen to have a fire, guess who doesn't have insurance coverage. All of these appliances have to go thru testing for safety and you would be short circuiting that all out. For an exoeriment in a shop (controlled conditions) maybe OK, but at home with the smarter half and the young ones NOT OK.

__________________
Bin there, done that, then done that again and again and now I forgot where I was.Is this what it means to get old?
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#13
In reply to #9

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/05/2010 2:50 PM

Personally I cannot read the diagram well enough to be helpful....sorry.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#11

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/04/2010 10:09 PM

As DKWarner, and others, have mentioned, you life may hang on not doing this.

May I offer... unless you live in a fully self contained fully detached housing unit, you may be putting the life of others at risk as well. This you do not have the right to do.

Standards for electrical products were implemented to protect the silent majority from people who tinker.

If your residence is fully stand-alone... then the risk you take is yours to take. If you live in an attached dwelling unit, such as an apartment or row housing, you must not ask others to assume that risk on your behalf.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14
In reply to #11

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/05/2010 2:51 PM

His house insurance will be null and void if anything happens too.....that might be the least of his problems!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#15

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/05/2010 2:54 PM

I nwould like to remind you of an old Southern German saying, translated by me of course:-

  • "He saves money no matter what it costs!"
__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Member

Join Date: Nov 2009
Posts: 7
#16
In reply to #15

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/05/2010 5:51 PM

Hello all....it seems that it is hard to read the ckt due to the resolution. I will try to post a better one. Meanwhile...and as I said before...I started this thread in order to discuss an electrical matter. I am not trying to save money or anything like that. I am an Engineer and I don't like giving up as easy as some of you guys. I expected more professional answers than the above comments!!! Thanks again to those who tried to help.

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#17

Re: Rewiring 2 120V legs to one 240V leg for oven elements

01/06/2010 10:25 AM

Well...

This may be a place to get more information: http://www.fixya.com/support/whirlpool

I am not certain they will be as enthusiastic about your project as you are, but maybe.

__________________