01/05/2010 2:16 AM
A few weeks ago I posted a question about the load bearing capacity of a slab floor on a bldg. I'm considering using as a warehouse. Thanks to prompting of this forum, I actually found the blueprints for the building (1920!)
The rebar configuration is called Spiral Mushroom Reiforcement--basically concentric circles of 3/8" rebar on a radial matrix. Above this mushroom is a perpendicular grid of 3/8" rebar, approx 12" o.c. and above this another similar grid oriented on the diagonal (45 degrees)
The first floor slab is 8.5" thick, is supported from basement by pillars approx. 22 ft o.c. and is labelled: "designed for Live Working Load of 150#/sq.ft"
The second floor slab is 7.75" thick , similar pillars as first floor, and is labelled "designed for Live Working Load of 100#/sq.ft."
The portion of bld. I'd use as warehouse has 10.5" thick slab, with no load labelling.
4 questions:
1. What does "Live Working Load" mean? Hard to believe so much steel and concrete would support so little weight/ sq.ft. Or maybe the question is: in layman's terms, what does "Live Working Load" mean?
2. If 7.75" slab has capacity of 100#/sq/ft. and 8.5" has capacity of 150#. sq. ft., what would be the capacity of the 10.5" slab?
3. My use for bldg. would be to have 3 80 ft. lines of pallets racks approx. 20 ft. o.c., each having a max. load of 475 lb./sq. ft. So about 25% of the floor would be occupied by pallet racks, the other 80% would be open aisles, used only by the occasional 3000 lb. forklift moving around a 2500 lb. pallet. So my "average" load would be something like 100 to 150 lb/sq. ft......but something tells me "average" isn't the way engineers think.
4. What I still want to know is: do I need to forget about this building because the slab is no where near sufficient for my use, or am I in the ballpark , but still an need an engineer so you all sleep at night?
thanks for your consideration (again),
dave
Pathfinder Tags: understanding concrete slab
Good Answers: 213
Re: Concrete Slab Questions Revisited
01/05/2010 11:35 PM
From what I recall from your original post, there was some discussion of apparent failure in the slab (sagging). A 1920's building that has been used for heaven knows what over the years could very easily have degraded concrete. Original design loads in this circumstance are pretty meaningless. An engineering inspection and actual strength testing is the only way to be sure (other than stacking up a bunch of pallets until the whole thing caves in...)
01/06/2010 12:34 AM
Live Load is comparible to Dead Weight. Dead weight is not moving, Live load is moving. 90 year old concrete? is it still suporting itself? Don't forget your racking is loading on 4 legs, not divided over the whole rack area.
Bin there, done that, then done that again and again and now I forgot where I was.Is this what it means to get old?
01/06/2010 1:55 PM
thanks for reply.
Bldg. and slabs are definitely still supporting themselves. Bldg. has been in continuous use by a number of commercial and retail enterprises over the decades. Most recent occupant was a furniture and appliance store (since the 1940's or 50's). They definitely had many tons of carpets on racks on the second floor. As for cracking, etc. There are surprisingly few,...unlike the slab on grade floors in my garage and equipment sheds! But the bldg. slabs do have a very occasionally hairline cracks that definitely seem more like surface curing cracks rather than structural cracks. But obviously an engineer's eyes need to be found.
01/06/2010 12:38 AM
Congratulations on finding those prints and labels.
Are your racks loaded at 475 psf throughout? (I don't know if it might be permissible to use an average or some other load factor. Just a thought.)
In the layout of your racks between the existing columns, there might be a way to add some intermediate columns, such as between back-to-back racks. E.g., saw holes in bottom floor, pour footings, build up from there. (Another random idea.)
I don't recall deflection problems from your earlier thread on this; I believe that was a project CaptMoosie was working on.
I would run these ideas by a structural engineer before trying anything, but maybe you have some viable options.
01/06/2010 8:21 AM
Without getting into the complex details of reinforced slab floor design, I would consider the following.
1. Live working load is any persons or objects the floor has to support. It does not include the floor structure itself, its concrete, steel, etc.
2. Although tempting, I would not use a linear relationship to guess at the load capacity of the 10.5" slab. If the original designers left the capacity out, there must be a good reason.
3. A 3000# forklift carrying 2500# = 5500#/4 tires = 1375#/tire * tire/0.34 sf = 4044#/sf.
4. I have inspected a number of similar old buildings, and they've all had cracks. I would investigate other opportunities for your venture, and leave this 90-year old building for someone else's purpose.
01/08/2010 7:26 PM
Sorry a 3000# rated forklift (carring 2500#) therefore 3000# rated probably weighs in as 5600 to 9000 lbs! Just for the fork lift. Then the total load onthe floor is somewhere about 10,000 lbs. This load is concentrated in a small area (the forklift footprint) and is a Live Load!
Good Answers: 179
01/06/2010 8:51 AM
Hello David,
First off, congrats on finding those old blue prints of the building you were looking at! You're having better luck in that regards then I am!!! LOL
Just a world of caution obtained from years of experience: be a little leery about what is shown on old blue prints. They may be the original Architect's set prior to submission to the Building Inspector or issuance to the Contractor, or they may be a rare find indeed if they are a "Contract Record Drawing" set that actually shown any field changes made during the construction period. But, many times those changes were never recorded at al. It all depends on the individual Architect, Contractor, Engineer or any of their subordinates or a hired construction superintendent.
Quick question for you David: You mentioned that the column centers were 22' o.c.. Is dimension valid in both directions, and that you have square column bays? If that is the case, you may have what is typically called a Two-Way Slab system in your building. Be very careful how you load up those slabs, especially with rack systems due to sensitive shearing locations.
Now, back to your description of the rebar as I'm a little confused about what you're trying to describe to us here. Are what you are describing in your posting the rebar for the columns? It sounds to me like it is and that the top of the columns feature a thickened panel, either square or round that look like a "thickened slab section"? Is that what is in that building? Column diameters? I expect that these would get larger as you progress down floor by floor to the foundation. How many stories? Full basement or mechanical equipment tunnels? Any long term water damage? Ground water problems in the basement if one exists? Outside shell material, brick or concrete? Condition and weather tightness?
Now, how is the condition of the concrete throughout the building, including the roof slabs? Do you see any spalled concrete, cracking?
To me, it sounds like a very interesting and magnificent structure! I'd love to see some pics of it if they are available!!!! Too bad I'm half-way across the USA or I'd take a little trip our to see it...
Based on what I've read so far from your postings it appears that you can proceed to the next stage in your project and hire a Licensed Professional Engineer/Structural Engineer who is VERY experienced in the assessment and analysis of older reinforced concrete buildings (pre-World War II era), especially when it comes to two-way concrete slab behavioral analysis.
Just meeting with and walking through the building with this engineer will well worth spending a few thousand dollars just to hear what he/she has to say to you through your walk-through. I recommend finding a PE/SE that is older and experienced and won't do a song and dance routine for you and later clobber you with a outrageously high billing. Find someone you can talk to you that won't pull any punches. IMHO, don't even bother working with an Architect regarding the structural elements of this building because it is way beyond their limited structural engineering knowledge. Just think of Architects as "Frustrated Artists", and you'll see what I mean. IN ADVANCE: I apologize to all of you Architects out there that read this, but "I calls 'em like I See's 'em". You guys and gals can make pretty buildings et all, but ya don't know nuttin' about how they stand up and stay there! LMAO
Next, if the PE/SE feels that your projected business operations can be met with this building without costing you a fortune, then I'd proceed with obtaining some Windsor Compression Tests. These are non-destructive penetration tests to determine what the actual concrete compressive strengths are in the columns, walls and floor slabs. The PE/SE may also want to obtain concrete core samples. It is vitally important that the engineer get the results of these tests. Yes, I know it's money out of your pocket, but those test result finding will help your engineer figure out if your building structural elements are as strong as those blue prints say they are or vice-versa that it's a piece of crap and just have it torn down.
If the Windsor Tests results come back reasonably well and what was expected, then you may want to hire the PE/SE to perform detailed analysis of the floor systems, the roof and the columns. Also, don't forget the foundations! I strongly recommend that you have to hire a Geotechnical Engineer and testing lab to determine load carrying capacities of the in-situ soils around and under that building. Both Engineers will most likely issue Engineering Reports to you with their findings and recommendations.
All-in-all David, if it was me I'd go for it and see what the engineers you hire have to say about the existing building conditions and it's load carrying capabilities as well as taking into account how you are going to use the building. You may have to modify the slabs to accept those heavy rack systems, or arrange them in such a manner as to avoid high slab punching shear stresses and high 1-way and 2-way shear stresses. I'd also be very leery about the maximum axle loads/wheel loads of those folk lifts. A detailed structural analysis (and possibly performance simulations0of those rolling loads is critical, especially if you have more than one operating per floor.......you may find out that you may have to downsize the weigh and carrying capacity of the forklifts, but also how they are employed.
Also, talk to the engineer how how you are going to store items on the floors if not on the rack systems, say from backlogs, etc.
Forgot to ask these questions: (1). freight elevators? (2). If yes, Number, rated capacities, & sizes? This is another critical area that the engineer has to look at. (3). concrete ramps floor to floor?
That's it for now. Have a great sunny day!
01/06/2010 1:29 PM
Wow! Thanks for all the info, details, and the time! If you are ever in Montana, you should come by for a look.....and a good Montana micro brew. No hurry. The bldg. has been there and in use since 1920, so I'm guessing it'll still be there in 2020...occupied or not.
I actually did take some photos of bldg inside and out, so could e-mail them.
dave
01/06/2010 2:42 PM
Blue prints. These look like originals submitted by architects, but my game is organic specialty grains, not construction. Great point about "what you see may not be what is there." Of course nobody from the original building crew would still be around to ask.
Columns. They they are essentially the same spacing in both directions
Rebar. No, the rebar configuration is that of the slabs themselves. Basically concentric rings of re-bar centered over the pillars (radiating out about 5 ft and tied to 8 radial rebars beginning at center) , with 2 x 90-degree grids above these rings going all the way across the bldg. slabs (bldg dims.: 80 ft. x 140 ft) . first grid is North-South/ East-West, second grid is at a diagonal to the first NW-Se/NE-SW. (Wish I had a huge scanner, I'd send you a copy of the slab prints, which would do a better job than my layman's attempt at describing them)
Pillars. Top of pillars do have a square "thickened slab section". Pillars are about 2ft square with thickened slab section probably about 4 ft. where it meets the slab ceiling. I don't have the blueprints handy for exact dims., but this is pretty close. I didn't check column dims on each floor.
Stories. Full Basement + 2 stories above.
Ground water problems. City of Conrad does have ground water issues seasonally due to everyone (over)watering their lawns.
Outside structure. 1 ft. concrete walls--faced w. brick on the 2 sides that face street.
Forklift options. Smaller forklift would certainly be a possibility.....plus that would allow me to put in another row or two of pallet racks. (just joking.... I don't want anyone to have a stroke!)
Freight Elevator. Yes there is one, but no capacity plate. It employs a 1.5" or 2" cable, but I'm guessing you couldn't get more than about a ton of furniture on because it is about8 ft. square.
a sunny day would be good. It was just above zero here this morning.
thanks, so much for your questions and thoughts.
d
Good Answers: 179
01/06/2010 3:59 PM
Hello David,
You're very welcome! Glad to have helped any way that I could give you, especially given the limited resources we have available to transmit information between us.
Now, all the additional information is making it easier for me to visualize where your concerns and interests weight in with regard to applicability of this building to your needs. A microbrewery (and pub/restaurant) makes perfect sense in an old rustic concrete and brick structure like you have there in Conrad. I've been a quite a few very nice ones in Albany, Troy and Saratoga NY where old warehouses, department stores or factory buildings have been successfully rehabbed/modified into brew pubs. Even in a deep recession like what we've been weathering through these places are still rather busy and successful! With the proper forethought and building a cohesive Architectural and Engineering team you will end up with a very interesting brew pub. Don't forget to cut-in new skylights and multi-story light vaults mixed with live vegetation, hardwoods and brass adornments in the restaurant and bar(s).
A problem that you're going to face is how to support large copper (or stainless steel) vats and the tanks without greatly impacting the floor slabs. One way I'd do it is to suspend the vats and tanks above the existing floors on new structural steel framing and required catwalks/handrails. Of course you'll have to support these new frames with numerous columns (due to the vat and tank weights plus liquid/grain weights) passing down through successive floor slabs (via newly constructed openings....try to miss the rebars!) to newly constructed reinforced concrete foundations located in the basement.
What you have described regarding the radiating and concentric rebar placement call-outs at the column capitals is VERY unique. Not once in my 32 years in this business have I even encountered such an unusual rebar layout in a Two-Way slab!!! That sort of layout makes some sense, and I'd be very curious to know who the design engineer was. Either he was a pure genius or a lunatic! **LOL** Most likely he was an European-trained structural engineer..possibly a German or other northern European that emigrated to the USA. Say, is the City of Conrad a former mining town, as in underground mining??? That may be the true origin of your structural engineer or from another mining town in Montana or other neighboring state.
David, many thanks for the offer to look over the building and visit Conrad! I really wish I could do that......just pack-up and jet out there in a whim! LOL I've never been to Montana, but always wanted to before I kick the bucket. Beautiful Sky Country indeed!
You can seen scanned pics to my private email address, but first you must contact me via my CR4 Forum mailbox. I would love to see the pics!!!!
Have a great day!
Good Answers: 93
01/10/2010 4:36 PM
Captain Moosie is definitely racking up the GA votes on this one.
I have to say David as well, I for one appreciate the tone of your inquiries.
Where and how did you find the plans?
All that rebar, thickness of the slab, and 100 pound per square foot live load strikes me as oddly low, too.
I worked in a Motion Picture Studio mainly built of wood where we were warned that the floors were only good for 200 pounds per square foot, so find the floor rating according to plans strange in comparison, regardless of whatever the rebar shaping and cross laydown.
Frankly it sounds like a sturdy building to me.
Thanks for getting back to us with some more of the story.
Hope you will post some pictures for all of us to see.
P.S. Since you got ahold of the plans, and there must be some names on them, and the architects, and engineers likely worked in your area on more than one building, is there any other building with a history to compare?
You don't get wise because you got old, you get old because you were wise.