CO2 emission savings from PFC

01/06/2010 3:05 PM

I want to calculate the CO2 emission savings created by installing Power Factor Correction equipment at a site whicha has a monthly maximum demand of 296Kva @ a PF of 0.547.

The CO2 emission factor for NSW Australia is 1.07kg/Kwh.

Register to Reply
Pathfinder Tags: Co2 emissions Power Factor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#1

Re: CO2 emission savings from PFC

01/06/2010 4:11 PM

Ando,

You will probably not see any CO2 Savings, but your equipment will run cooler and more efficiently.

You may also save the penalty applied to your bill for the poor power factor, Intergral and Energy Australia both penalise for worse than PF=0.8 if your load is high enough.

Regards,
Sapper.

__________________
It's all about the Boom! - MythBusters
Register to Reply
Active Contributor

Join Date: Jan 2010
Location: NSW Australia
Posts: 12
#3
In reply to #1

Re: CO2 emission savings from PFC

01/06/2010 6:50 PM

Sapper,

Country Energy does not appear to have an enforcement policy on PF. They have been taking customers from demand tarrifs and placing them om Kwh tarrifs. Thus there is not financial incentive to to reduce PF.

My understanding is that are the nil or minimal CO2 savings on site, but there should be less energy generated by the generators to supply this inefficient site.

ie: 1000Kva @ 0.5 power factor only gives you 500Kw of usable energy? Therefore the unusable Kvar has to be generated?

This is out of my scope of expertise and any assistance is greatly appreciated.

Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#6
In reply to #3

Re: CO2 emission savings from PFC

01/06/2010 9:48 PM

Ando,

They will certainly penalise you if your load is high enough at that PF.

In Section 1.10.11 of the "Service and Installation Rule for NSW 2007 Amendment" they certainly have the authority to apply penalties to consumers with a poor PF in the form of a "Demand Charge" applied to the bill.

I would check your bill and the tariff notes, you may find a nasty lurking there.

AS 3000 - Wiring Rules and the Service and Installation Rules book would be a good investment if you are covered by Country Energy.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
2
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: CO2 emission savings from PFC

01/06/2010 6:33 PM

Ando quote "I want to calculate the CO2 emission savings created by installing Power Factor Correction equipment at a site whicha has a monthly maximum demand of 296Kva @ a PF of 0.547."

In theory, you won't change the KWH's by improving the power factor. However, in reality you do see a decrease in line losses which equate to KWH's. Your load is so small that the losses will also be small and no great savings.

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Jan 2010
Location: NSW Australia
Posts: 12
#4
In reply to #2

Re: CO2 emission savings from PFC

01/06/2010 6:56 PM

I understand that there will be reduced line losses and at such a small load there will be minimal savings.

If a site runs at a Power factor of 0.5 does the generation plant have to supply twice the Kva to this site than if it had a power factor of 1?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #2

Re: CO2 emission savings from PFC

01/07/2010 7:32 AM

GA.

It is suspected that the electricity supplier, rather than the electricity user, will be rather more interested in this calculation and will encourage the user to help by imposing tariff charges for low power factor on electricity consumed.

The original poster needs to check the tariff charges and evaluate whether power factor correction equipment is a worthwhile investment to reduce these charges. It is only after this evaluation has been carried out that CO2 emission reductions could be estimated from the reduced supply line losses. The user calculation then becomes an economic one upon which equipment investment decisions can be made.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: CO2 emission savings from PFC

01/06/2010 7:29 PM

Ando you said "The CO2 emission factor for NSW Australia is 1.07kg/Kwh."

If the savings are based on KWH's, then the savings will be very small. If the power factor is 0.547, the generation plant does have to supply more KVA. If the present load is 296 KVA at 0.547 PF, the load would be 162 kva with a PF = 1.0 but the KWH's did not change. Well it changed a little.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2010
Location: NSW Australia
Posts: 12
#7
In reply to #5

Re: CO2 emission savings from PFC

01/06/2010 9:49 PM

This is correct

Does Kvah = Kwh?

Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#8
In reply to #7

Re: CO2 emission savings from PFC

01/06/2010 10:22 PM

Ando,

kWh = kVAh * PF

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2010
Location: NSW Australia
Posts: 12
#9
In reply to #8

Re: CO2 emission savings from PFC

01/06/2010 10:57 PM

Thanks Sapper

Is there any real environmental advantage of installing PFC?

What is the benifit to the generation plants by correcting PFC?

cheers

Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#10
In reply to #9

Re: CO2 emission savings from PFC

01/06/2010 11:13 PM

Ando,

Yes, The Closer we get to achieving prefered Power Factor, the more efficiently the system as a whole will run.

From a site perspective, your switch gear, cabling and protective devices will all run cooler which will promote a longer lifespan and therefore a smaller carbon footprint for the site.

I do encourage power factor correction where is is cost effective for this reason, or if you see penalties appear in your bills.

At this point I would suggest you get a local Electrical Engineer to do a cost\benefit analysis for you, specific to your site if you are really worried about it.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Anonymous Poster
#11

Re: CO2 emission savings from PFC

01/06/2010 11:20 PM

The advantage to installing PFC correction is that your utility company will charge you less for your electricity.

What really happens as PF drops is that the 'real power' current-carrying capacity of your feed line from the utility drops. A given line is rated for a given current at a standard temperature. If temperature is taken out as a factor, then your utility-feed line can only carry so much current, which is the trigonometric sum of the 'real' current AND the 'reactive' current.

For example, let's say that your feed line can pass 100 A. If you draw 100 A at PF =1, then your line will be maxed out at 100 'real' amps; it won't be able to carry any more 'real' or 'reactive' amps. Likewise, if your PF=0: you'll still draw 100 A and your line will STILL be maxed out; but it won't be transmitting any 'real' power. For in-between cases, you'll have to do the trigonometric math.

So, what would happen if your utility were to feed you 100 A of reactive-only current when your PF would be zero? First, your utility would have to generate that reactive powerm, which would cost the utility. Secondly, if your plant is being charged for 'real' power only, then your power-meter would be reading zero consumption .. and that DESPITE the fact that your utility would be providing you power (albeit reactive). That's why utilities that charge you for 'real' power (current) only will penalize you if your PF gets too low ... you're costing them. Not only will you be forcing your utility to spend on generating reactive power (current), which does nothing 'useful', you'll also be adding 'useless' load on your utility's transmission network and possibly congesting it.

Cheers!
DZ

Register to Reply
Active Contributor

Join Date: Jan 2010
Location: NSW Australia
Posts: 12
#13
In reply to #11

Re: CO2 emission savings from PFC

01/07/2010 12:37 AM

Dz,

This is where I am coming from.

The site I am looking at is only charged Kwh (real power). Their utility company does not penalise them for low Pf.

ie: If we have a Demand of 1000Kva @ 0.5PF we will have 500Kw of real power being consumed on site. The other 500Kw must be generated due to the Pf of 0.5?

As say it is costing the utility extra to produce/generate this extra reactive power.

If this usage was constant for 1 hour then we would need to generate 1000Kwh to use 500Kwh. Thus the reactive power is 500Kwh. We then multiply this by 1.07kg/kwh to obtain a CO2 emission?

Register to Reply
Commentator

Join Date: Dec 2009
Posts: 70
#12

Re: CO2 emission savings from PFC

01/07/2010 12:15 AM

CO2 has to do with combustion efficiency and PF corrections may or may not mean nothing.

I would suggest you Aussies plant trees down under and enjoy the additional trees that can be fed off the additional CO2. Also the additional CO2 could go into the oceans and help build your coral reefs, (CaCO3) and eventually would lead to limestone deposits when the ocean plates climb on your pile of dirt you downunders wear out limiting plant food. Or if you have an emergency call Algore. He may decide to use his higher than Aussie intelligence to help you down unders out. His cap and trade process would even help you finance his life style. Algore, BHO, Hope and Change that is my motto. It should be yours also.

Register to Reply
Commentator

Join Date: Sep 2009
Location: INDIA
Posts: 92
#14

Re: CO2 emission savings from PFC

01/07/2010 2:01 AM

as P.F . improvement is to reduce the energy losses.how it is related to CO2 emission saving can any one guide mi?

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#16
In reply to #14

Re: CO2 emission savings from PFC

01/07/2010 3:33 PM

The losses in the distributions network and in your plant will be reduced by a few percent of the KVA reduction. It is difficult to get an exact number but 2-5% is probably a reasonable guess.

If you bring your 300KVA at PF=0.5 to a PF=1, you will save 150KVA.

Multiply this by 5% you get 7.5KW of losses. (Evaluated the I2R losses in the distribution network to supply the KVA. Not pure math but likely a good assumption)

This means that you will save 7.5KW * 1Kg/KWh = 7.5Kg/h of operation. This mean 180Kg per day using high value of 5% losses.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Active Contributor

Join Date: Jan 2010
Location: NSW Australia
Posts: 12
#17
In reply to #16

Re: CO2 emission savings from PFC

01/07/2010 4:38 PM

Thanks marcot

I have used a detailed calculation based on this information. I understand by reducing the demand, we will reduce line losses etc. As a simple estimate I have been told the 2 - 5 % is in the ball park unless a more detailed investigation is carried out.

But, at the generation plant, there must be extra production to supply this inifficient site.

I thank evreyone for their time and comments.

Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ando (6); Anonymous Poster (1); Jack Marcotte (1); luv123 (1); marcot (1); PWSlack (1); Sapper (4); wareagle (2)

Previous in Forum: Measurement of Transformer Losses by 3 Wattmeter Method   Next in Forum: Breakers on a ring-bus?

Advertisement