how to culculate the suitable emergency diesel genrator for a hospital including A/C electric motors ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: emergency power generator

01/10/2010 3:47 AM

For a highly critical life-support application like this, you will need to consult some specialists. It would take many pages to spell all of this out, which is not readily suited for semi-informal forums such as here. Much of the answer will also depend on local code requirements.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: emergency power generator

01/10/2010 6:02 AM

Hire a qualified electrical contractor. If it's not done right and people die, you can sue him.

Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#3

Re: emergency power generator

01/11/2010 7:34 AM

The emergency diesel generator kva can be calculated by getting the total hospital load which include all hospital ectronic and electrical equipment of which the A/Cs and electric motors are inclusive.

When u get your total load in kw,using kw=√3vicosφ,if by calculation,find your i(current) value,where v is your voltage and √3 is determining factor for a three phase network supply system and cosφ is your power factor.Use kva=√3vi to calculate your emergency diesel generator apparent power rating(KVA) required for the hospital.Further step up this kva value by a 25% margin to take care of unneccessary overloading in the hospital.

Makesure u buy a good emergency diesel generator from well known names like caterpillar,cummins,mitsubishi etc.Also ensure that in the installation,u follow appropriate regulations or local regulations to ensure safety.

If u are not qualified enough to handle the project,get qualified or professional personnel to handle it while u learn from them.

Patrick Whowha

__________________
Patrick Whowha
Register to Reply
Member

Join Date: Jan 2010
Posts: 9
#4

Re: emergency power generator

01/11/2010 7:40 AM

I would contact the generator supplier...they will be able to help with sizing by a site survey and probably current electric bills.