Hi guys.
I need to measure 250V – 500V range by A/D that
Powered from single 3.3V supply.
The problem is that I need a good accuracy and
The range of 250V is "map" to 0 – 3.3V.
I know that I can do that with resistor divider but
Do someone have any other good idea how to do that?
Pathfinder Tags: A2D
Re: Mesuring High voltage (500V)
01/10/2010 7:44 AM
You don't say if it's ac or dc.
If AC you could of course use a transformer.
If it's DC you could maybe chop it and use a transformer.
Or use it to drive an opto coupler and measure the shift in output, you'd need precision resistor to limit the current of course.
For more ideas please insert another coin or send tuna.
01/10/2010 7:59 AM
soory it is DC voltage
01/10/2010 7:50 AM
Any particular reason why you don't want to use a simple resistor divider? I think you'll find any other solution will be more complex & expensive, and no more accurate.
01/10/2010 8:13 AM
Thanks friend
if we go on resistor divider.
What do you think on differential measurement
Instead on single ended?
01/10/2010 8:48 AM
You could divide the input down to 0 to 6.6V (for 0 to 500V at source) and use a 3.3V reference for the low side of the differential measurement (assuming your ADC will take above 3.3V in common mode). Alternatively, use an op-amp to subtract 3.3V from the 0 to 6.6V before the ADC (you may need to protect against the ADC input going negative).
01/10/2010 8:56 AM
Thanks friend
God bless.
01/10/2010 7:54 AM
Use Voltage Null Method
01/10/2010 8:01 AM
Thanks friend
Can you explain yourself.
01/10/2010 8:14 AM
01/10/2010 8:28 AM
Thanks friend
Do you have this article on hand?
01/10/2010 8:36 AM
Yes, I'm holding it up to the screen now. Can you see it?
Tell me when to turn the pages, OK?
01/10/2010 9:03 AM
Friend
You can be more friendly when you trying to help
Otherwise don't do that.
01/10/2010 9:37 AM
You have had lots of help from lots of people given willingly.
I'd respectfully suggest you should accept a little humour with good grace.
01/10/2010 9:47 AM
Sorry, but at that point I wasn't trying to help.
Thanks Del.
01/10/2010 10:30 AM
A simple voltage divider will likely be your best bet to step down these voltages to a usable range for your A/D card. But you leave out a lot of critical information to design a suitable divider network.
  • What is the input impedance of your A/D card?
  • What is the anticipated source impedance?
  • How accurate do your measurements need to be?
  • How much resolution does your measurement require?
  • How noisy of an environment will this be?
That's all that I can think of for now, but I'm certain I forgot something.
01/10/2010 10:37 PM
Another solution is to use an electrometer amplifier with a very large value input resistor in a current to voltage converter configuration. This way you do not have to deal with a divider arrangement and a very high value input resistor can be used. Analog Devices makes some good electrometer amps or even a very high input impedance op-amp can be used if configured correctly.
01/11/2010 9:26 AM
Adding any active component will always add additional error sources. If you don't know how accurate the measurement has to be or the resolution required then you cannot say that the errors will not be significant.
01/11/2010 10:29 AM
Yes you state what is very obvious. The basic request was for alternative methods which is the suggestion fulfills. Whether it is suitable for the particular application we must leave to the person with all the details. In my answers I assume the asker to be capable of evaluating the suitability of the response. I don't have time to second guess all the possible unknowns.
Hobbies - Musician - Tube Amps Only Please!
01/11/2010 4:58 AM
I would use your voltage divider with good quality resistors (look into wire wround) that are not to sensitive to temperature changes since this changes resistance. Then I would use a 10 turn high quality pot to balance trim +- say 2%. This will allow for temperature changes and tolerances in the voltage divider and therefore you can trim to 0% or as close as possible. Calibrate as needed.
Regards, Maveric Manic - 'Knowledge is Power and Wisdom is knowing how to use it'
Engineering Fields - Electrical Engineering - New Member United States - Member - New Member
Re: Measuring High voltage (500V)
01/11/2010 8:58 AM
A company by the name of Caddock makes precision voltage divider networks that are used in many of the high-end voltage sensing applications (voltmeters, etc.). The multiple taps of the resistor network correspond to the different ranges on the voltmeter. Please see their website for more information, the link below is to the product page for their precision divider networks.
Caddock Resistors
Hope that helps,
Tom
01/11/2010 12:38 PM
The OP doesn't define "good accuracy". Please define that. If it is within 1%, I also vote for a simple voltage divider. If it is higher than this, then you can still use a "trimmed" voltage divider as mentioned by others. At 500V you can get and choose components that will not vary much due to temperature and/or voltage. Don't make things more complicated than is necessary.
01/11/2010 5:21 PM
Use a high voltage probe. Here is a URL for a Tektronix P5100 (about $ 400 list).
http://www2.tek.com/cmswpt/psdetails.lotr?ct=PS&ci=13471&cs=psu&lc=EN