PLEASE GIVE ME SOME BASIC INFORMATION ABOUT THE INTERLOCKING SYSTEM OF TWO CIRCUIT BREAKERS.ONE IS FOR NORMAL SUPPLY AND THE OTHER ONE IS FOR GENERATOR SUPPLY.THANKS A LOT FOR ALL YOUR INFORMATION....
If the generator is intended to be a Stand-by power source (i.e.) the generator will be made ON only when the EB Supply is not available, then the following interlocks are suggested:
i) Mechanical Interlocks using Castell Key Interlocks - Two Locks with one key such that only one breaker can be made ON at a time and the key can be removed from the lock only when the breaker is in OFF condition.
(or)
ii) Mechanical Interlock using Clutch wires between the two breakers so that only one breaker can be made on at a time.
iii) Electrical Closing interlock, such that the breaker auxiliary N.C. of one CB is wired in series in the closing circuit of the other CB.
iv) Electrical Tripping Interlock, such that breaker auxiliary N.O. of one CB is wired in the Trip Circuit of the other CB.
v) Ready to Close signal: The N.C. auxiliary of one CB is wired in teh Ready to Close CB of the other CB.