Generator Harmonics

01/16/2010 10:46 PM

Will third harmonics present in the generator supply increase the generator winding temperature significantly. What is the pole pitch of the generator winding with 108 slots, 8 pole and a coil throw of 0 to 11?

Register to Reply
Pathfinder Tags: Generator Winding Harmonics
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#1

Re: Generator Harmonics

01/17/2010 11:42 PM

Yes, the Third Harmonics will be present substantially @ 29 % current Harmonics, in case the stator winding is of Full Pitch or 5/8th Pitch.

Because of this Harmonics the Harmonic Current will flow through the Main Stator Winding in addition to the Load Current, Hence the Main Stator Winding Temp Rise will Increase.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#2

Re: Generator Harmonics

03/14/2010 12:50 PM

We have been taught in the college days that the 3 rd Harmonics are eliminated by star connection of the generator winding, and 5th Harmonics is of magnitude of 1/5^2 which is qual to 4 Percent and reduced by SHORT PITCHING OF WINDING to the required LEVEL OF CONTROL.

There was some thread on this matter and I do not remember when it appeared, It can be searched out in CR4 LINK. Thehttp://cr4.globalspec.com/thread/49265/How-to-convert-m3-hr-into-Nm3-hr?frmtrk=CR4digest CR4 MEMBERS may also comment on this point.

DHAYANANDHAN.S,

CR4 MEMBER,

INDIA

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#3
In reply to #2

Re: Generator Harmonics

03/14/2010 1:04 PM

In my reply I have intended to convey that " SOME TIME BACK THERE WAS A REFERENCE ABOUT THIS HARMONICS MATTER AND I DO NOT REMEMBER THE CR4 LINK/PATH AND I DO NOT REMEMBER THE DATE. OTHER CR4 MEMBERS CAN ALSO COMMENT ON THIS."

BUT TO MY SURPRISE SOME OTHER LINK - is found in my comment/reply. How it happened is not known to me.

Some CR4 MEMBER might have had a similar experience and advise how to avoid this.

Thanks,

DHAYANANDHAN.S,

CR4 MEMBER,

INDIA