Kva reduction

01/16/2010 4:10 PM

If I install power factor correction on an Industrial site it will reduce the Kva Demand but not the Kwh consumed.

My undertanding is that electrcity is generated in Kva. By reducting the Kva on site, will this reduce the energy required to power this site?

Would this reduce the CO2 emissions required to supply this site at the generation plant?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Kva reduction

01/16/2010 5:58 PM

Quote Ando "If I install power factor correction on an Industrial site it will reduce the Kva Demand but not the Kwh consumed."

Yes

Quote Anso "My undertanding is that electrcity is generated in Kva. By reducting the Kva on site, will this reduce the energy required to power this site?"

No. This is answered above.

We have already been through this before. You asked the same question below.

http://cr4.globalspec.com/thread/48750/CO2-emission-savings-from-PFC

Register to Reply
Active Contributor

Join Date: Jan 2010
Location: NSW Australia
Posts: 12
#2
In reply to #1

Re: Kva reduction

01/16/2010 6:09 PM

cheers

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Kva reduction

01/16/2010 7:06 PM

PF correction might save a tiny amount of CO2 emissions, just enough to keep such a claim from being false. Thus it is an excellent candidate for hyping as "green," or for creating borderline scams.

PF correction has its proper and economically justifiable place, but this might not be it.

I too thought the question sounded familiar.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: Kva reduction

01/16/2010 10:42 PM

"In vino veritas; in cervisia carmen; in aqua E. coli."

In wine is truth; in beer is song; in water are bacteria. Did I get that right?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Kva reduction

01/17/2010 12:04 AM

Yes! (Adapted from the slogan of a microbrewery som friends owned.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster
#11
In reply to #5

Re: Kva reduction

06/15/2010 2:24 PM

In vino veritas; in cervisia carmen; in aqua E. coli.

!!! In wine is thruth, in beer is songs, and in water ... bacterias ?

:-) Great phrase !!

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#6

Re: Kva reduction

01/18/2010 12:44 AM

The power trangle should be the basis for ur understading. KVA is a vectorial summation of KW and KVAR. By installing a cap bank, u are reducing the size of the KVAR which has a dual effect of reducing the KVA and Phase Angle. By reducing ur phase angle ur improving ur pf. The KW is at all time ur reference total none reactive load power when unity pf is attained. All inductive loads are rated in KVA for the presence of the real (true) power (KW) and the reactive power (KVAR). KW remains what u have as ur true power and is not affected by introducing a cap bank (ref. power trangle)

A clamp ammeter on load wire will show apractical view of the important of ur cap equipment. It relieves the generator and reduces the maximun demand charges.

Kamah D.

Abuja Nigeria

__________________
There is peace in silence and achievement in plans.
Register to Reply
Anonymous Poster
#9
In reply to #6

Re: Kva reduction

01/18/2010 3:58 AM

Thanks for all the relevant information suplied.

I have a much clearer understanding now

cheers

Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#7

Re: Kva reduction

01/18/2010 3:39 AM

If your pf is low,it means u have large reactive power kvar,which need to be reduced by correcting the power factor.

Note that if pf is corrected, the value of kva is reduced accordingly.The current drawn is reduce,as such the energy consumed is also reduced.

Patrick Whowha

__________________
Patrick Whowha
Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#8

Re: Kva reduction

01/18/2010 3:49 AM

Pf correction will reduce the energy consumed by the site loads.It will not reduce the energy required to power the site,except when you did not meet the required kva to power the site loads initially.

Patrick Whowha

__________________
Patrick Whowha
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#10

Re: Kva reduction

01/18/2010 11:23 AM

Quote Pat "Pf correction will reduce the energy consumed by the site loads.It will not reduce the energy required to power the site,except when you did not meet the required kva to power the site loads initially."

Please explain how the improvement in PF reduces the energy consumed by the site loads. I would think that if you reduce the load energy requirements, you would reduce the site energy requirements.

Register to Reply