Steam Turbine is Hunting

01/18/2010 3:07 AM

Dear All,

My question is related to Hunting at Steam Turbine. We have A small Turbine manufacture by Dresser-Rand Model is RLHB19, Power 132KW, Governor Woodward Model TG-17.

When we start the turbine and before it reached to operating speed which is 1790rpm, it will start hunting at 1750rpm then we start close the valve slowly then hunting will stop. Unfortunately I don't have much experience in Turbine Governor and I seek your support to share with me your experience to solve this issue.

Thanks in Advance,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor
United Kingdom - Member - New Member

Join Date: Jan 2010
Posts: 11
Good Answers: 1
#1

Re: Steam Turbine is Hunting

01/18/2010 11:13 AM

SEE THE MANUAL OF YOUR TURBINE,,,,,IF 1750RPM IS CRITICAL SPEED OF YOUR TURBINE THEN ITS OK. BECAUSE IN ALL TURBINES THERE IS A CRITICAL SPEED AND VIBRATION IS HIGH AT SUCH SPEED. ONCE YOUR TURBINE PASSED THROUGH CRITICAL SPEED ITS VIBRATION REDUCE TO NORMAL VALUE. SO WHAT YOU HAVE TO DO IS THAT 'NEVER STAY AT CRITICAL SPEED, JUST PASS THROUGH IT' IJAZ AHMAD

Register to Reply
3
Guru
Popular Science - Evolution - New Member

Join Date: Jul 2006
Location: India-Chennai.
Posts: 722
Good Answers: 30
#3
In reply to #1

Re: Steam Turbine is Hunting

01/19/2010 12:02 AM

Yes, checking the manual is the best to get the right values.

Locate the 'Droop Adjusting lever' and make the adjustment as recommended. The important point here is: The adjustment should be done very carefully and very minimally every time. Increasing the droop too much would cause heavy surging and if the load is less, might trip on over speed. It could be better that way, rather having an accident on high speed. So test the 'Over Speed Trip Test' on solo run, before adjusting the droop on load.

__________________
A picture worth thousand words: needless to say if it is animated.
Register to Reply Good Answer (Score 3)
Commentator

Join Date: Sep 2009
Location: Saudi Arabia
Posts: 74
#4
In reply to #3

Re: Steam Turbine is Hunting

01/19/2010 1:01 AM

thanks Yesyen, your comment is highly appreciated

Register to Reply
Commentator

Join Date: Sep 2009
Location: Saudi Arabia
Posts: 74
#6
In reply to #3

Re: Steam Turbine is Hunting

01/20/2010 5:45 AM

Dear Yesyen,

We used to decouple the Turbine and it was run to operating speed, as result the respond of turbine was perfect no hunting was occurred! that means only with load, hunting will occurred! What does that mean?

Now Governor will be flashed with light oil then will be fill with new oil..if you have any suggestion let me know please..

apprecite every body feedback..

Register to Reply
Guru
Popular Science - Evolution - New Member

Join Date: Jul 2006
Location: India-Chennai.
Posts: 722
Good Answers: 30
#7
In reply to #6

Re: Steam Turbine is Hunting

01/20/2010 12:11 PM

Droop adjustment will reduce the hunting. You can adjust the droop on load, but taking enough care and precautions. One important precaution, I suggested, was to conduct 'over speed trip test' (in decoupled condition).

__________________
A picture worth thousand words: needless to say if it is animated.
Register to Reply
Participant

Join Date: Apr 2019
Posts: 4
#11
In reply to #3

Re: Steam Turbine is Hunting

04/02/2019 11:23 PM

We have 2*38.5 MW coal based steam turbines, both always runs at 25 MW individually, Auxiliary consumption 5 MW and inter connection cement plant 9 MW and export to GRID is 36 MW Whenever grid disturbance occurred the grid circuit breaker opening and plant came to home load at TG-1: 3.5 MW and TG-2: 5.8 MW after that points are noted as bellow 1. TG-1 load rapidly dropped to 0 MW and Generator tripping on reverse power protection.( if we are in alert position TG-1 breaker manually opens while load dropping condition and saves from Turbine trip) 2. Whenever TG-1 load dropping, TG-2 load raising rapidly. 3. TG-2 withstanding home load at 9.5 MW ( 5 MW power plant auxiliary and 6.5 MW Cement Plant auxiliary ) 4. after getting clearance from GRID, going synchronised 5. Before Close the Breaker we observed following parameters TG-2 active power : 9.5 MW Reactive power : 2.1 MW Power factor :0.987 Lag Voltage : 11.25 KV ( matched with Grid voltage) Frequency : 49.99 to 49.98 ( matched with Grid Frequency) after getting Synch permit we are closing breaker then immediately Load was hunting from 13.5 MW to 1 MW here we are observed turbine actuator Hunting rapidly. and unable observed frequency of the Generator and Speed of Turbine

Register to Reply Off Topic (Score 5)
Anonymous Poster
#2

Re: Steam Turbine is Hunting

01/18/2010 11:51 PM

Even if it is a diesel engine or the steam turbine, the governor control module is doing the job of keeping the engine /turbine speed constant by varying the fuel/steem supply under variable load conditios. In this case the turbine RPM is hunting due to distrubbed setting on the gain control and stebility control pots which are required to be set till the hunting stops. The gain and stebility controls are the integral parts of Governor control modules.Also the body of governor control module to be earthed for its safe and efficient function.

CVS Murthy

Register to Reply
Anonymous Poster
#5

Re: Steam Turbine is Hunting

01/19/2010 10:36 AM

Dear,

The above mentioned problem I have faced recently in one of our turbine.When sensitivity of governor is high and governor valve travel required is very low to meet out your load,governor try to respond quickly to control to your set speed and it will create hunting.To ,solve this problem try to increase governor droop setting step by step which will decrease sensitivity slightly but hunting will be reduced.This is my experience and it can be adjusted at site or test stand.Procedure given in TG governor maintenance catalogue.Any how you have to get permission from your higher official to do adjustment.This is my suggestion only.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2009
Location: Ontario Canada
Posts: 930
Good Answers: 31
#8

Re: Steam Turbine is Hunting

01/23/2010 9:35 AM

We have seen turbines and gas and diesel engines hunt when there has been some binding of moving components in the governor mechanism. One case was a bad bearing on a tractor and another was galling of components on a steam turbine. If everything moves smoothly look elsewhere.

__________________
The fine line between cuddling and holding one down to prevent escape must be learned
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#9

Re: Steam Turbine is Hunting

01/11/2011 1:09 PM

Dear Mr.Fahad,

Did you try to increase the SLUGGISHNESS OF THE GOVERNOR, slightly.

If not please try and you may succeed and come out of your problem.

Thanks,

DHAYANANDHAN.S,

CR4 MEMBER, INDIA.

Register to Reply
Participant

Join Date: Apr 2019
Posts: 4
#10

Re: Steam Turbine is Hunting

04/02/2019 11:21 PM

We have 2*38.5 MW coal based steam turbines, both always runs at 25 MW individually, Auxiliary consumption 5 MW and inter connection cement plant 9 MW and export to GRID is 36 MW Whenever grid disturbance occurred the grid circuit breaker opening and plant came to home load at TG-1: 3.5 MW and TG-2: 5.8 MW after that points are noted as bellow 1. TG-1 load rapidly dropped to 0 MW and Generator tripping on reverse power protection.( if we are in alert position TG-1 breaker manually opens while load dropping condition and saves from Turbine trip) 2. Whenever TG-1 load dropping, TG-2 load raising rapidly. 3. TG-2 withstanding home load at 9.5 MW ( 5 MW power plant auxiliary and 6.5 MW Cement Plant auxiliary ) 4. after getting clearance from GRID, going synchronised 5. Before Close the Breaker we observed following parameters TG-2 active power : 9.5 MW Reactive power : 2.1 MW Power factor :0.987 Lag Voltage : 11.25 KV ( matched with Grid voltage) Frequency : 49.99 to 49.98 ( matched with Grid Frequency) after getting Synch permit we are closing breaker then immediately Load was hunting from 13.5 MW to 1 MW here we are observed turbine actuator Hunting rapidly. and unable observed frequency of the Generator and Speed of Turbine plaese tell me any suggestion reason behind Turbine hunting

Register to Reply Off Topic (Score 5)
Participant

Join Date: Dec 2025
Posts: 1
#12

Re: Steam Turbine is Hunting

12/15/2025 11:46 PM

Dear,

Have the issue got resolved, because i am also facing the same issue. Please confirm what was your action plan to rectify the hunting.

Thanks in advance...

Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: