Installation of 110V/60Hz Alongside 230V/50Hz

01/18/2010 7:19 PM

Hi all, I'm living in a country with 230V/50Hz. I frequently travel to the US and would love to be able to purchase US electrical goods for use back home. For the most part, that is no problem as modern goods mostly accept 110-240V/50-60Hz especially for transformation to DC internally. However, quite a number of kitchen hardware and gaming consoles are quite particular about their 110V/60Hz input. I'm renovating my place at the moment and thinking of installing a 110V/60Hz network alongside the mains 230V/50Hz. Any idea how I can go about doing it? Thanks in advance for your suggestions! Cheers Ben

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Installation of 110V/60Hz alongside 230V/50Hz

01/18/2010 11:33 PM

A transformer and a VFD perhaps?

Or a motor-generator with 5:6 step-up gear ratio? (More cumbersome, I would think.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#2

Re: Installation of 110V/60Hz alongside 230V/50Hz

01/18/2010 11:39 PM

You can use a step down transformer from 230/110Volts and then a frequency converter from 50 Hz to 60 HZ in one combined unit.

CVS Murthy

Reply
Anonymous Poster
#16
In reply to #2

Re: Installation of 110V/60Hz alongside 230V/50Hz

03/27/2010 8:19 PM

Hi

Where can I find something like this. Separate items are easy to get, but teh fewer boxes the better...

Sandy

Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#3

Re: Installation of 110V/60Hz alongside 230V/50Hz

01/19/2010 1:25 AM

guest; i would go for the step down transformer, & not worry about the 50/60 HZ. many items are listed 110 volts @ 50 HZ/ 120 volts & 60 HZ. American electric ranges are 120/240 volt, the 120 volt is for the light bulbs, clock, etc ,now days the clock/timer are electronic. dish washer/disposal 120 volt, microwave 120 or 230 volt. perry

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Installation of 110V/60Hz alongside 230V/50Hz

01/19/2010 2:48 AM

A plug-in electric clock (shaded pole motor type) won't get away with this, unless you change some gears!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#5
In reply to #4

Re: Installation of 110V/60Hz alongside 230V/50Hz

01/19/2010 8:46 AM

Quite right!

The US Air Force sent me to several countries where 220/60 was the standard and we could get small to medium plug-in transformers that let me use most of my U.S. electronics. The only problems arose with devices that were dependent upon the speed of an electric motor.

As long as you purchase electronics that are not exactly speed dependent you should be fine. I was told that my microwave would not like the change in htz but the model I had worked fine for 3 years in England. Cd-players and computers posed no problem either, but I think a record player might.

If you have the finances, airport magazines sell many devices that are mult-voltage. If you are military or have friends that are you can get multi-voltage and mult-system electronics at the Base Exchange. The multi-system is required if you want to work with PAL and NTSC television signals. Some DVD players are region specific and will only play certain disks.

Drew

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Reply
Anonymous Poster
#8
In reply to #4

Re: Installation of 110V/60Hz alongside 230V/50Hz

01/20/2010 6:09 AM

or go to a 28.8 hour day

Reply Off Topic (Score 5)
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#12
In reply to #3

Re: Installation of 110V/60Hz alongside 230V/50Hz

01/20/2010 11:12 AM

Pls. do the normal 220V wiring and use step down tranformer were necessary. Doudle circuit in same house could be misleading to ur detriment.

Take care

Dickson.

Abuja, Nigeria.

__________________
There is peace in silence and achievement in plans.
Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#15
In reply to #12

Re: Installation of 110V/60Hz alongside 230V/50Hz

03/27/2010 11:07 AM

The wire/conductor size is to be taken care since when the voltage comes down by half, the current will be double to that of at 22o volts.

DHAYANANDHAN.S,

CR4 MEMBER,

INDIA.

Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Installation of 110V/60Hz alongside 230V/50Hz

01/19/2010 1:58 PM

Changing voltage is easy, changing frequency is not. But the question is, do you really need to change frequency? Maybe, maybe not. About the only things that are affected by frequency are motors and transformers. Things with switch mode power supplies (in general) and heaters are only interested in voltage.

First you must be a little more exacting in your voltage ratings. I don't think any new US appliances are really "110V" any longer, because in the US, household voltage levels can vary from 110V to 127V. So if your house has 127V and the appliance was rated 110V, you are exceeding it even if you have a +-10% range. So a long time ago, motor manufacturers "standardized" (not really, but in effect) on either 115V or 117V because it falls within that +-10% range either way.

So assuming you have 115V rated appliances, then the next thing to consider is maintaining the V/Hz ratio. So divide the V by the frequency in Hz, which gives your 115V 60Hz appliances a V/Hz ratio of 1.92 to 1. Then apply that to a 50Hz supply, and you end up with 95V. So, in order for you to realistically run appliances with AC motors in them at 50Hz, you need to reduce the voltage to 95V (+-10%) or risk burning them up. But if your appliances have DC motors or what are called "universal AC motors" in them, as many do, then again, it may be problematic because DC motors are voltage dependent and lowering the voltage may adversely affect them as well.

Getting a frequency converter (inverter) for small appliances is a bit of over kill, but if you insist, get one for each device that absolutely needs it the way to do it. DO NOT run separate wiring inside of walls to run dual sources throughout your house, you are asking for trouble, and most likely it will be illegal wherever you are anyway. One of the many problems with running wires side by side with different frequencies is what is called "Mutual Induction". Normally, premise wiring is always at the same frequency from the same source, so parallel runs have no effect on each other. But if they have different frequencies, there is a relative different, so they will mutually induce currents, an impedances, on one another. the net effect could be heating of the wires, voltage instability, spikes, noise, all kinds of things that appliances and electronics DON'T like.

Better yet, find things in your new country that are designed to work there...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 5)
Participant

Join Date: Feb 2010
Posts: 1
#13
In reply to #6

Re: Installation of 110V/60Hz alongside 230V/50Hz

02/09/2010 2:11 PM

Hi

Does this apply to household appliances such as vacumm cleaners, or will I get away with simply stepping down the voltage from 220v 50hz to 110v 50hz?

Thanks

Sandy

Reply Off Topic (Score 5)
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#14
In reply to #13

Re: Installation of 110V/60Hz alongside 230V/50Hz

02/09/2010 5:00 PM

I had no problems using my American vacuum and some other small electronics while living in England.

I can't say for all electronics you might use, but your vacuum should work fine.

Drew

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Reply Off Topic (Score 5)
Active Contributor

Join Date: Jan 2010
Location: I am at Chennai India. Retired Dy General Manager - Power Plant Automation
Posts: 23
#7

Re: Installation of 110V/60Hz Alongside 230V/50Hz

01/20/2010 12:12 AM

Hi You can order for a 110Volt 60Hz sinewave inverter of the required capacity from any local manufacturer operating on 230 V AC input and wire up the whole house with american sockets. So all your equipments can be plugged in without any fear of damage. Now most of the equipments like PCs have an adapter for 90 to 290Volt 40 to 65Hz. Hence there is no poblem of operating them on 230V 50 Hz. May be AC 60Hz operated motors (in washing machines, food processors in Micro ovens etc)or any frequency sensitive equipment cannot be operated. The above I have implimented in my house. Which is satisfactorily working for the last 5 years.

Seetharaman.

seethasub@hotmail.com

Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#9

Re: Installation of 110V/60Hz Alongside 230V/50Hz

01/20/2010 7:39 AM

Since u are now residing in country with 230/50Hz,Buy goods rated for 220,230,240/50Hz/60Hz.

U can buy small individual stepdown transformers for your internal small loads already aquired with 60Hz,to step down the power for such loads to 110V/60Hz.

Patrick Whowha

__________________
Patrick Whowha
Reply
Anonymous Poster
#10
In reply to #9

Re: Installation of 110V/60Hz Alongside 230V/50Hz

01/20/2010 8:07 AM

hi mr. patrick how will you take care of frequency sensitive devices like synchronus motors etc.

seetharaman

Reply
Power-User

Join Date: Mar 2006
Location: Valdosta, GA
Posts: 361
Good Answers: 8
#11

Re: Installation of 110V/60Hz Alongside 230V/50Hz

01/20/2010 9:28 AM

Use a 12 volt battery charger. I assume they have those in 220 volt 50 HZ models. Once you have 12 volts DC you can use one of those devices that plug into your cigarette lighter on your car and output 117 volt AC. All standard stuff.

__________________
Always use protection.
Reply Score 1 for Good Answer
Reply to Forum Thread 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); dhayanandhan (1); Dickson (1); Drew K (2); JRaef (1); Keywalker (1); Patrick Whowha (1); perry (1); seethasub (1); sforsyth (1); Tornado (2)

Previous in Forum: Signal Flow Architecture   Next in Forum: Capacitor Voltage for Power Factor Correction

Advertisement