Insulated Ductwork

01/24/2007 10:56 AM

I am looking for information on vapour retarders on insulated ductwork.

What types of vapour retarders are there? Are they simply a jacket on the outside of the ducts?

Where do you need to apply vapour retarders on ducts? What I have read is that you don't need a vapour retarder on warm ductwork but you do on cold. Why is that?

Also, from what I have seen is you put 2" of insulation on cold ducts and 1" on warm ducts. Why is that?

Any useful information on ductwork would be appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - Engineering Consultant Popular Science - Evolution - Understanding

Join Date: Nov 2006
Location: Bay Shore, NY
Posts: 715
#1

Re: Insulated Ductwork

01/25/2007 3:38 PM

PatyO:

Typically a vapor "retarder" or barrier will be installed over the insulated ductwork for A/C. This is to prevent moisture in the air from contacting the cold duct, and condensing on the duct and in the adjacent insulation (if fiberglass or similar "wettable" material), which could damage the duct if it is steel, cause the insulation to become wet and lose its insulating ability, and also possibly result in the condensed water dripping onto whatever is below the ductwork. There are standard products made for this purpose, and often the vapor barrier is incorporated with the insulation itself for ease of installation. What the vapor "retardants" or barriers all have in common is that they prevent the passage of moisture through them, are strong enough to survive normal installation intact and allow their seams to be taped or otherwise sealed.

As far as the thickness guidelines you refer to, they are a factor of economics. The heavier insulation is justified on ducts carrying cooled air, but not on ducts for heating. But, that is only a general guide for typical ductwork, and any specific case should be decided on its own merits based in part on the, temperature differential of the air in the duct and ambient temperature surrounding it, length of run, etc.