PLC vs. DCS

01/28/2010 11:59 AM

Hi,

I am new to Automation field, I want to know what is the difference between PLC and DCS. And what parameters decides whether to take PLC system or DCS system.

Thnx

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: PLC Vs DCS

01/28/2010 12:50 PM

The gist of this issue is found about midway through that Wiki: PID control loops.

PLCs can process a few, maybe a few dozen. But a processing plant such as a chemical manufacturing facility or a complex bio-pharma process may have hundreds or thousands of control loops. That is where a DCS will seriously out perform a PLC.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#3

Re: PLC vs. DCS

01/28/2010 2:08 PM

From the wiki article above

"As PLCs have become more powerful, the boundary between DCS and PLC applications has become less distinct".

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: PLC vs. DCS

01/28/2010 4:04 PM

A little bit of wishful thinking probably, remember that Wiki articles are written by regular folks and that one on PLCs was likely written by a PLC supplier. The Wiki article in DCS is likely written by a DCS supplier.

Still, from a hardware standpoint this is somewhat true, in fact Siemens' DCS system, the PCS7, is based on their S7-400 PLC hardware. But all similarities stop there. The computer interface capabilities and processing power of the DCS is far greater than what anyone would be willing to pay for in a PLC.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#5

Re: PLC vs. DCS

01/28/2010 7:21 PM

Dear all,

PLC for logic control such as limit switch input, motor start output, replacing hundreds of (or thousands of ) hard wire relays by only one PLD. For analog control, you may need an additional analog control board. It works much faster than DCS. So If your system is mainly logic control, use PLC.

DCS for analog control, such as temperature input and control valve position output, replacing hundred's of analog loop controllers. It can do the logic control same as PLC , but working slowly. If your system is mainly for analog loop control use DCS.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply Score 1 for Good Answer
Anonymous Poster
#6
In reply to #5

Re: PLC vs. DCS

01/30/2010 10:47 AM

Thanks for the information, but the no of I/Os also works as deciding parameter for selection system such as PLC or DCS?

Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#7
In reply to #6

Re: PLC vs. DCS

02/02/2010 4:16 AM

Dear all,

Number of I/O is not really related.

If the I/O is mainly on-off (binary) such as factory automation, PLC is selected.

If the I/O is mainly analog such as in process control in refinery, DCS is selected.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Anonymous Poster
#8
In reply to #7

Re: PLC vs. DCS

02/02/2010 10:19 AM

Thanks...

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Akihito Shigeno (2); Anonymous Poster (3); JRaef (2); Yuri B. (1)

Previous in Forum: p.f. of a locked-rotor ind. motor   Next in Forum: Standards for Estimating Demand

Advertisement