Neutral-Ground Voltage

02/04/2010 3:50 AM

it is said that if you mount a capacitor ( about 0 ,5 microfarad for a 230 volt ac distribution system) across neutral and grounding bar the difference of about 2-3 volt will go down.in fact i dunno the details but do u think it sounds reasonable?

__________________
jinxnao
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#1

Re: neutral- ground voltage

02/04/2010 4:10 AM

he says the voltage will be lower than 1 volt.

__________________
jinxnao
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: neutral- ground voltage

02/04/2010 6:37 AM

No, it doesn't sound reasonable. It sounds abstruse.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#3

Re: neutral- ground voltage

02/04/2010 7:46 AM
Register to Reply
Anonymous Poster
#4

Re: Neutral- Ground Voltage

02/04/2010 7:50 AM
Register to Reply
2
Anonymous Poster
#5

Re: Neutral- Ground Voltage

02/04/2010 9:02 AM

The 0.5uf capacitor simply represents a 500 ohm load to 60hz. If the V difference is because of voltage drop in the neutral line (most likely) then that is very low impedance and I don't expect 500 ohms to do much. If the voltage difference is because of leakage or capacitive coupling etc. that is higher impedance, then the 500 ohm load will drop the voltage difference.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Aug 2006
Posts: 4484
Good Answers: 246
#6

Re: Neutral-Ground Voltage

02/05/2010 1:32 AM

Seems that in certain conditions it could... in others, it would have virtually no measurable effect.

__________________
There is more to life than just eating mice.
Register to Reply
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#7

Re: Neutral-Ground Voltage

02/05/2010 2:55 PM

What's the problem you are trying to solve?

I have an electrical engineer friend that lived in the UK that had this condition. He installed a transformer between neutral and ground and stepped up the voltage to power his refrigerator. When he was young and poor, the money he saved was significant.

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#8
In reply to #7

Re: Neutral-Ground Voltage

02/05/2010 6:28 PM

a transformer?? i cant imagine such a thing in reality, what will do a transformer and also why he boosts the supply voltage to the refrigirator? İ Think you must first of all tell about the problem of the refrigerator.By the way with capacitor i think the aim was to lower the neutral-ground voltage so that sensitive devices dont get burnt,

__________________
jinxnao
Register to Reply
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#9
In reply to #8

Re: Neutral-Ground Voltage

02/05/2010 7:47 PM

He turned a problem, voltage between neutral to ground, into an oportunity. The neutral to ground voltage was 9vac. He boosted it with a N = 9:230 turns ratio transformer that he made so that he could steal electricity. I am not stating that this is what you should do.

If I had a floating neutral problem, I would check to make sure that the electrical service panel had a proper ground, ground rod placed into the ground and also connected to the water pipes. I would also make sure that the neutral coming from the utility was also connected to the ground at the electrical service entry.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #9

Re: Neutral-Ground Voltage

02/08/2010 6:30 AM

Well, it depends upon the earthing system applied locally. Connecting neutral to earth/ground in an IT system will have no measureable effect whatsoever.

Connecting neutral to earth/ground downstream of an RCD will result in the device tripping on occasions.

Earth/ground is a safety conductor, first and foremost.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 127
Good Answers: 3
#16
In reply to #12

Re: Neutral-Ground Voltage

06/13/2016 9:17 PM

See #14. Neutral to Equipment-Ground shorts are not permitted (outside of the Service Entrance).

__________________
avid0g
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#10

Re: Neutral-Ground Voltage

02/06/2010 4:06 AM

I do agree with U that a neutral voltage exist but only in an unballanced system. So what do you intend to do with it? Connecting a capacitor accross neutral and ground for a 2-3 volt to go down is for what purpose?

I will like to hear more of this.

Dickson

__________________
There is peace in silence and achievement in plans.
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#11
In reply to #10

Re: Neutral-Ground Voltage

02/06/2010 7:32 AM

I think it is up to the IT systems and ground loops, i dont know exactly the case, just been told of it, in fact the high neutral-ground voltage (not because of imbalance but i think because of leakage return through neutral point) causes ground loops and they cause the electronics cards devices etc to burn, if i am wrong excuse me, it is said that a professor adviced to connect a capacitor across neutral and ground terminal of a devices so that the company which is supposed to give guarantee for the device would be contented to give it , (otherwise the company wont give the guarantee papers ), i am not so versed in these subjects and just share my opinions here...

__________________
jinxnao
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #11

Re: Neutral-Ground Voltage

02/08/2010 6:31 AM

"Snake oil"?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 127
Good Answers: 3
#14
In reply to #11

Re: Neutral-Ground Voltage

02/08/2010 7:05 AM

I spent several years inspecting the environmental, power distribution and grounding systems in the Tri-State area around Pittsburgh PA for the customers of a Super-Minicomputer Company.

Our concern was that the customers were not getting the best from our computers because the power quality, grounding and environment were not nominal for the computers. Since the top-of-the-line bleeding edge (at the time) computers used emitter-coupled logic, they were quite sensitive to ground loop currents passing between the computer racks.

Almost all the significant problems I encountered involved shorts between the neutral and equipment grounding conductors. I can categorically say that the capacitor shunt is a bad thing, and high neutral voltages never had a whit of detriment to data processing quality.

On the other hand, our switching-mode power supplies had everything to do with the high neutral voltages, since we originally produced them all in Wye configuration. The neutral current was typically 1.4 to 1.6 times the load current, and the frequency was 360Hz with large harmonics. Since then I have started to see the same thing happening with electronic ballasts.

__________________
avid0g
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 127
Good Answers: 3
#15
In reply to #10

Re: Neutral-Ground Voltage

02/08/2010 8:02 AM

Please note that with switching-mode power-supplies, even a perfectly balanced Wye load will produce very large neutral currents, with a theoretical upper limit of I(neutral)=Sqrt(3)*I(phase)=1.732*I(phase). This is the justification for derating such circuits to I(phase)*Sqrt(3)/0.8=I(phase)*2.165=I(capacity)

__________________
avid0g
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); avid0g (3); Blink (1); Dickson (1); jinxnao (3); PWSlack (3); Snave (2)

Previous in Forum: Fault Levels and Amp/Sec   Next in Forum: Cable Runs and Current Rating

Advertisement