Cable Runs and Current Rating

02/04/2010 5:26 AM

Hello All, Above how many amperes of current rating it is advisable to go for more than one run for cable laying?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Deciding No. of Cable Runs with respect to Current Rating.........!

02/04/2010 6:35 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: Deciding No. of Cable Runs with respect to Current Rating.........!

02/04/2010 9:11 AM

The "current" carried by a cable is not the answer to your question. The process of rating a cable for its safe current handling capacity looks closely at the ability of the cable to dissipate heat. Overheat a cable, you stress its insulation, stress it far enough and the insulation breaks down and fails. When it fails, the "magic smoke" (as one forum member calls it) gets released to the atmosphere.

So... the mutual heating effect caused by the bundling of multiple cables is what you have to prevent. The Canadian Electrical Code rule 4-004(11) speaks to this issue. How we regulate this issue in Canada is by controlling the maximum length of the "bundled" section of "multi-conductor cables". The length specified is 600mm.

If the length of the bundled section is less then 600mm, we do not care how many cables you bundle together. Why? Because in a distance less then 600mm, the mutual heating effect is considered negible. If the length of the bundled section is over 600mm in length, here in my jurisdiction, we do not allow multi-conductor cables to be bundled together.

What does "multi-conductor cables" mean? We allow no more then 6 current carrying conductors (3 x 2 conductor cables) to be bundeled together for a distance longer then 600mm.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Deciding No. of Cable Runs with respect to Current Rating.........!

02/04/2010 1:41 PM

It really depends on the electrical standard you are working to, and the application.

The actual de-rating value (not current as current varies depending on numerous de-rating factors applicable to your application and the way you mount or enclose the cable(s)) for parallel cables sharing current should be indicated in the applicable electrical standard you are working to. You may also find it in cable manufacturer literature available of their website.

__________________
jack of all trades
Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

jack of all trades (1); North of 60 (1); PWSlack (1)

Previous in Forum: Neutral-Ground Voltage   Next in Forum: Electostatic Charges in Gas Turbine Compressor
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement