Copper Busbar Sizing

02/07/2010 10:33 PM

Please confirm the Size of Copper Bus Bar For 4 Pole, 1600 Amp & 4 Pole 500 Amp

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: ENQURY

02/07/2010 10:47 PM

Unless you provide a value to check there is no value to confirm.

You can check here http://cr4.globalspec.com/search/sitesearch?do=show&sort=textmatchrank&srch=bus%20bar%20ampacity&srchobjs=t%2Cc&fs=12&order=asc

Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: ENQURY

02/08/2010 4:02 AM
__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#3

Re: Copper Busbar Sizing

02/09/2010 12:19 AM

for 50 deg C ambient you can use for 1600 Amp120x10mm bar or 80x15mm; and 50x8mm for 500 amp, this will give a bar temperature rise up to 90 deg c

__________________
dont say it, write it
Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#4

Re: Copper Busbar Sizing

02/09/2010 1:06 AM

Bus Bar Design Considerations

TABLE 2. QUICK BUSBAR SIZE SELECTOR

Required Ampacity*

Busbar Dimension, Inches**

30 °C Rise

50 °C Rise

65 °C Rise

100-149

1/16 x 1/2

1/16 x 3/4

1/16 x 1/2

150-199

1/16 x 1

1/8 x 1/2

3/16 x 1/2

1/16 x 3/41/16 x 1/2

200-249

1/8 x 3/4

1/4 x 1/2

1/8 x 1/21/16 x 3/4

1/8 x 1/2

250-299

1/16 x 1 1/2

1/8 x 1

3/16 x 3/4

1/16 x 1

1/8 x 3/4

3/16 x 1/2

1/16 x 1

300-349

1/16 x 2

3/16 x 1

1/4 x 3/4

1/4 x 1/21/8 x 3/4

3/16 x 1/2

350-399

1/8 x 1 1/21/8 x 1

3/16 x 3/4

1/4 x 1/2

400-449

1/4 x 1

3/8 x 3/4

1/4 x 3/41/16 x 1 1/2

1/8 x 1

3/16 x 3/4

450-499

1/8 x 2

3/16 x 1 1/2

1/16 x 2

3/16 x 1

1/4 x 3/4

500-599

1/4 x 1 1/2

3/8 x 1

1/8 x 1 1/2

1/4 x 1

3/8 x 3/4

1/16 x 2

1/8 x 1 1/2

3/16 x 1

600-699

1/8 x 2 1/2

3/16 x 2

1/2 x 1

1/8 x 2

3/16 x 1 1/2

3/8 x 1

1/4 x 1

3/8 x 3/4

700-799

1/8 x 3

3/16 x 2 1/2

1/4 x 2

3/8 1 1/2

1/4 x 1 1/21/8 x 2

3/16 x 1 1/2

3/8 x 1

800-899

1/8 x 3 1/2

3/16 x 3

1/4 x 2 1/2

3/8 x 2

1/8 x 2 1/2

3/16 x 2

1/2 x 1

1/4 x 1 1/2

900-999

3/16 x 3 1/2

1/4 x 3

3/16 x 2 1/2

1/4 x 2

3/8 x 1 1/2

3/16 x 2

1/2 x1

1000-1249

3/16 x 4

1/4 x 3 1/2

3/8 x 2 1/2

3/8 x 3

1/2 x 2

1/2 x 2 1/2

1/8 x 4

3/16 x 3

1/4 x 2 1/2

3/8 x 2

1/8 x 3

3/16 x 2 1/2

1/4 x 2

3/8 x 1 1/2

1250-1499

1/4 x 4

3/8 x 3 1/2

1/2 x 3

3/16 x 3 1/2

3/16 x 4

1/4 x 3

3/8 x 2 1/2

1/2 x 2

1/8 x 4

3/16 x 3

1/4 2 1/2

3/8 x 2

1500-1749

1/4 x 5

3/8 x 4

1/2 x 3 1/2

1/2 x 4

1/4 x 3 1/2

1/4 x 4

3/8 x 3

1/2 x 2 1/2

3/16 x 3 1/2

3/16 x 4

1/4 x 3

3/8 x 2 1/2

1/2 x 2

1750-1999

1/4 x 6

3/8 x 5

3/8 x 3 1/2

1/2 x 3

1/4 x 3 1/2

1/4 x 4

3/8 x 3

1/2 x 2 1/2

2000-2499

1/4 x 8

3/8 x 6

1/2 x 5

1/2 x 6

1/4 x 6

3/8 x 5

1/2 x 4

1/4 x 5

3/8 x 4

1/2 x 3 1/2

2500-2999

1/4 x 10

3/8 x 8

3/8 x 6

1/2 x 5

1/4 x 6

3/8 x 5

1/2 x 4

* For 60 Hz current.

** Table gives busbar cross section which will probably be large enough for Ampacities within each range. Knowing required ampacity, determine possible busbar dimensions from the table. Then check Table 1 to verify that size selected has the necessary ampacity. Example: Assume that required ampacity is 185 amps at 30 °C rise. Table 2 indicates that 1/16 x 1 in. size would probably be adequate. This is confirmed by Table 1 which lists the ampacity of 1/6 x 1 in. busbar as 187 amps.

Busbar Ampacity Tables

Action

Table

Table Name

Ampacity

#1

Ampacities of Copper Alloy 11000 Busbars

You are here

#2

Quick Busbar Size Selector

Emissivity

#3

Effect of Emissivity and Number of Busses on Ampacity

Busbars Home | News | Search | Products | Send Prints | Bus Bar Design | Contact Us

Visit our Online Store

Ampacity Tables

Battery Connectors

Busbar

Copper Bar

Copper Specifications

Electrical Insulators

Glastic Insulators

Ground Bars

Grounding Kits

C o n t a c t :
Sheila Amburn
240 Industrial Drive
Decatur, TN 37322
1-800-394-4804
423-334-3389 Fax

Email bus bar@stormcopper.com

You get in touch with the above company or google search 500 or 1600 copper bar

Dickson

__________________
There is peace in silence and achievement in plans.
Reply
Commentator

Join Date: Oct 2009
Posts: 63
#6
In reply to #4

Re: Copper Busbar Sizing

02/09/2010 10:20 AM

VERY GOOD ANSWER. This help or advice is commendable. I will never give the reply---GOOGLE IT--.

Please refrain from such answers. This is my recommendation and not an advice. Please do not get offended.

Thakral Raj

Reply
Associate

Join Date: Dec 2008
Location: Kuwait
Posts: 27
#5

Re: Copper Busbar Sizing

02/09/2010 2:55 AM

N.E.C. 366.23 (A) - 1000 amps per square inch for copper bus bar.

1.6 x 1000 =1600, bus bar size would be 1.6 square inch copper bus bar.

.5 x 1000 = 500, bus bar size would be .5 square inch copper bus bar

For a round bus bar multiply the amps x .7854. Aluminum is 700 per sq. in.

Mark

__________________
Mark Abell
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#7

Bus Bar

02/10/2010 7:53 PM

Quote RAJ089 "VERY GOOD ANSWER. This help or advice is commendable. I will never give the reply---GOOGLE IT--. Please refrain from such answers. This is my recommendation and not an advice. Please do not get offended."

Why not. Many answers can be found by using a Google Search. An effort should be made to find the answer before posting here. I see nothing wrong in directing one to the answer to his question rather than spending time answering it on this forum.

Reply Score 1 for Good Answer
Reply to Forum Thread 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Dickson (1); Le_Noble (1); MasterEmaybe (1); RAJ089 (1); Tornado (1); wareagle (2)

Previous in Forum: Wiring Pressure Switch   Next in Forum: LAP Progressive Armature Winding

Advertisement