Illumination Requirements

02/10/2010 9:22 AM

Can anybody tell me the formula for Calculating No. of Light Fittings inside & outside of an Industrial Plant.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Illumination

02/10/2010 10:02 AM

Work with the designer of the plant and/or your lighting fixture vendor. They are supposed to know all of the critical attributes required to construct your plant's lighting concerns. Here is a partial list of concerns:

  • Lux level minimum for local safety code and for tasks specific to this plant
  • Height from fixtures to surfaces
  • Explosive atmosphere
  • Weather exposure
  • Backup safety lighting
  • Color temperature concerns for tasks

Your designer will also have a grasp of simple optics intensity calculations, like the inverse squared law.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Illumination

02/10/2010 12:31 PM

Use this formual:

Average Maintained Illumination (Foot-candles) = (Lamps/Fixture x Lumens/Lamp x No. of Fixtures x Coefficient of Utilization x Light Loss Factor) ÷ Area in Square Feet

This website will be additional help:

http://www.lightsearch.com/resources/lightguides/formulas.html

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Anonymous Poster
#3

Re: Illumination Requirements

02/10/2010 10:47 PM

The Illuminating Engineering Society, IES, or the IESNA.

The IES handbook

Register to Reply
Associate

Join Date: Nov 2007
Posts: 50
#4

Re: Illumination Requirements

02/11/2010 9:04 AM

www.visuallightingsoftware.com

Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); msamad (1); NoEngr (1); redfred (1)

Previous in Forum: Output Voltage of Three-Phase Transformer   Next in Forum: Shaft Current
You might be interested in: Hose Fittings, Tube Fittings, Gas Fittings

Advertisement