what is best solution for air fule control of annaline furanace.
Is there any online control system?
Re: Furnace
02/18/2010 9:40 AM
Maybe Annealing furnace?
Good Answers: 19
Re: Furnace
02/18/2010 12:01 PM
Air/Fuel Control of an Annealing furnace is what you mean.
You got to have a proportioning Temperature Controller and Modulating Motors with in-built balancing relays on both your fuel + air line to modulate the air/gas ratio of the burners. A NAMCO Air/Gas ratio controlling valve would be an added advantage.
If the burners are new packaged type then you can additionally add an O2 Controller to maintain on-line optimum combustion burning efficiency ensuring that the excess air has upto 1-4% O2 at the exhaust.