Current protection

02/20/2010 11:09 AM

Hi all, hope you can help,

I have an incoming supply of 2 x 160A TP&N MCCB it supplies an external bypass unit which contains 2No 200A TP&N MCCB's, from there it supplies a 2 x 30KvA UPS via 160A Fuses, the output of the UPS returns to external bypass switch via another 200A TP&N MCCB out to 2No Dis Boards which are installed with 250A MCCB incomers.

#Note all MCCB's are of Merlin Gerin NS range

Please could you provide any information regarding what would be the first to break during fault conditions.

Many thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Current protection

02/20/2010 12:43 PM

1. It depends on the location of the fault. If the fault is "downstream" of some of these components but "upstream" of others, only the former will trip.

2. Among the breakers or fuses of the same type, those of lesser amp ratings would trip first.

3. For items of different types,the time/overcurrent trip curves need to be compared. In this case, the 160A fuses would be likely to trip first. However, if they are time-delay fuses, it is conceivable that even one of the 200A breakers would trip faster. Hence the need for comparing the curves.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#2
In reply to #1

Re: Current protection

02/21/2010 12:29 AM

You have to grade those fuses properly. In Incomer, you have 160A Fuses or MCCB's and in down streams, you have MCCB's of 200 or 250A. Grade it properly. Use the max rated MCCB at I/C and then gradually decrease the value as per requirement. This will help system to isolate the faulty part only and all other part will reaman live.

SC calculation is not possible without few data.

Register to Reply
Anonymous Poster
#3

Re: Current protection

02/21/2010 11:51 PM

I agree with with Sidhu's explanation. In case you are designing the system, u need to redesign the same with highest rating of of upstream Incomer , to downstream incomers in decreasing order, based on the equipment/consumer requirement on each stage. However the sytem is laready designed then I doubt there will proper co-ordination between the breakars durng fault conditions and u need to check with person who has designed the sytem.

Register to Reply
Participant

Join Date: Feb 2010
Posts: 2
#4

Re: Current protection

02/22/2010 5:18 AM

Thanks all for your help, I think what I really require is the curves for each, as I am pretty sure that due to a MCCB being more sensitive than a fuse there is a means of discrimination here. Also I may have found a reason/explanation for the lack of protection, if the main fuse is to be the sole source of protection and all other MCCB's are to be classed as equipment i.e. switch disconnectors, and not as they are intended then this would be correct.

Many thanks for all your responses.

Kind regards

Rossk

Register to Reply