Anonymous Poster

VFD ESP application

02/20/2010 12:13 PM

Greetings,

I have a question about running an esp motor off a vfd. My output frequency and motor speed are never the same, is this normal, if so why? If I tune the drive to rated motor speed(3450), my output frequency is 3450, but my motor speed is lower. The drive is a Yaskawa F7. Any response would be greatly appreciated.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: VFD ESP application

02/20/2010 4:03 PM

I think maybe you do not understand how an AC induction motor works.The motor can NEVER spin at the exact same speed as the frequency applied to it. You must always have slip (the difference) in order to create torque,

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Participant

Join Date: Feb 2010
Location: Cin, ohio
Posts: 2
#2

Re: VFD ESP application

02/20/2010 4:07 PM

Motor nameplates give a rpm rating based on a no load condition. Once the motor is under load it will not spin at the rated rpm of the nameplate at the rated hertz. The drop is fairly insignificant.

ie 1700 rpm @ 60 Hz no load

1680 rpm @ 60 Hz load present

I assumed when you said output frequency is 3450 you were referring to the motor's rpm not the actual frequency.

There are some things you left out. How much of a difference is there? How are you measuring the motor rpm? Did you preform an auto tune with the drive? If so, was the motor under a load during tuning? Did you double check the nameplate info you programmed into the drive? You know the usual suspects.

__________________
The only thing more important than knowing the correct answer is knowing how to find the correct answer.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: VFD ESP application

02/20/2010 4:23 PM

I always understood that rpm ratings were at rated load, and slightly less (by percentage of slip) than synchronous speed.

For instance, synchronous speed of a 60 Hz 2-pole motor would be 3600 rpm. At full load, it might be 3500 rpm. Unloaded, it would run at something like 3590 rpm (load never being exactly zero, on account of friction.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Participant

Join Date: Feb 2010
Location: Cin, ohio
Posts: 2
#4
In reply to #3

Re: VFD ESP application

02/20/2010 5:13 PM

I was not questioning anyone. I was simply replying with my thoughts to the threads original post. Hoping to help answer the stated question. I thought the purpose of replying was to guide the person posting the original question in the right direction so that they may find a satisfactory solution for their problem. Not to antagonize like minded individuals with a common goal of trying to assist one another in reaching our own answers.

I never assume anyones knowledge level. Doing so would only prove the lack there of on my part.

__________________
The only thing more important than knowing the correct answer is knowing how to find the correct answer.
Reply Off Topic (Score 5)
Anonymous Poster
#6
In reply to #2

Re: VFD ESP application

02/20/2010 6:32 PM

Thanks for the reply! The drive is set for 60hz, when auto tuned, converts 60hz to motor rated speed. Auto tune to nameplate rpm (3450), full load amps, # of poles, voltage rating, and kw. No rotate tune. Drive display scaling is set to 3450. Set rpm at 3450. With display scaling set in rpm's, drive converts hz to rpm. 60hz should equal 3450rpm. Start pump. output frequency read from drive (U1-02) shows 3450. Motor speed from drive (U1-05) shows 3324. Not sure how drive gets this reading. Pump depth at 1200'. 1200' of drop cable have anything to do with it? I have PC pumps, motors on surface, convert hz to PRS(polish rod speed). Set to 300prs, motor speed shows 300prs. Thats why I'm confused.

Reply
Anonymous Poster
#5

Re: VFD ESP application

02/20/2010 6:03 PM

I think you're confused but you're not the first one I've heard who had the same line of thinking. The motor's rpm or speed is not the same as frequency. Check your motor's name plate again. It should have frequency of 50 or 60Hz. That's the figure that you should put into your drive not 3450.

Reply
Anonymous Poster
#7
In reply to #5

Re: VFD ESP application

02/20/2010 6:45 PM

The motor is rated for 60hz, this is plugged into the drive during the auto tune. I do a no rotate tune. Plug in nameplate voltage, FLA, hz, poles, rpm, and kw. I have 3 options for display scaling, hz, rpm, prs. I set to rpm. The drive then converts the hz to rpm. I think 60hz should equal 3450rpm. This might be were I'm confused. It then shows my output frequency at 3450, but gives me a motor speed of 3324. My motor speed is always lower, not sure which reading to go off of. I have PC pumps, motors on surface. Read PRS. Output and motor speed are the same on these. Thanks for the reply, if you have any other ideas or advice please let me know.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #7

Re: VFD ESP application

02/20/2010 7:40 PM

You are misinterpreting.

When you change the VFD display to say Hz or RPM etc., you are just changing the scaling of the display, which is based on the basic motor speed formula: RPM = 120 x Applied Freq./ Motor Poles.

TO THAT, you have t apply the slip percentage to get actual no-load speed, then that varies with load as well. So if you WANT the motor to run at 3450RPM unloaded, you would set the output frequency to 3600.

In a vector drive, which is what it appears you have, it is measuring the slip based on feedback information from the motor's current and voltage vectors, so it then tells you what the calculated speed of the motor is under load.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Anonymous Poster
#10
In reply to #8

Re: VFD ESP application

02/20/2010 9:18 PM

So why on my PC pumps are out put frequency and motor speed the same?

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11
In reply to #10

Re: VFD ESP application

02/20/2010 9:51 PM

They are probably not the same, unless driven by a synchronous motor. This is possible, but not likely.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Member
Ireland - Member - New Member

Join Date: Nov 2009
Posts: 9
Good Answers: 2
#20
In reply to #8

Re: VFD ESP application

02/22/2010 12:06 PM

Surely if you set the slip to achieve the no load speed when loaded, you set 3600rpm and get this in both cases +/- tolerance??

..and vector drives measure the current, (knowing the output voltage as this is generated by the VSD), so the slip is estimated according to the load calculation in the vector mathematical medel therein? Estimated speeds are only as good as the information and the VSD modelling techniques, but these are normally just readouts of frequency (scaled or not as you said) before or after slip is applied in the open loop case.

Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#9
In reply to #7

Re: VFD ESP application

02/20/2010 8:04 PM

If you have set the VFD correctly including slip speed and you are still short of speed, either the torque calculation is wrong, so adding the incorrect amount of slip (Hz) or the motor is slipping more because of reduced motor voltage increasing its slip at the same load. So, the motor may have a 60Hz slip speed of 3450 but if presented with a lower than nameplate voltage (cable volt drop) you will get reduced speed (increased slip). So, you accept this and rescale either your setpoint or slip or voltage to get you a more predicatble result.

What do you have connected to the VFD output to allow such a long cable length? If you're using an output choke OK for this distance, you will have a volt drop across this in addition to cable volt drop.

__________________
Something new every day!
Reply
Anonymous Poster
#12
In reply to #9

Re: VFD ESP application

02/20/2010 9:57 PM

I'll try tuning to 3600. I have #4 copper from drive to pump. 10hp motor FLA 19. 480volts coming into drive. The motor is rated for 460volts. Would this create large enough drop to increase slip? How do you figure motor slip? Should I try tuning with load? Sorry if these questions are preschool level to you all. I'm not an engineer, nor electrician.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13
In reply to #12

Re: VFD ESP application

02/20/2010 10:50 PM

The 480 volts is one of the nominal voltages furnished by utilities in the US and other places. Motors for this are rated at 460 volts to account for typical voltage drop (wire resistance) from the service to the motor.

Slip is another issue. To pick an example, a 3500 rpm motor operating on what would otherwise be synchronous speed of 3600 rpm is running at (3600-3500)/3600 ≈ 2.78% slip. This is quite normal. The torque produced by the motor (and the current it draws) are proportionate to the slip. If the motor is lightly loaded, the torque, current, and slip are less, and thus it runs closer to synchronous speed. (In my previous post I used the example of 3590 rpm). If heavily loaded, the torque, current, and slip are more, and the speed slower.

Most VFDs can display the frequency they are putting out, but I don't know if they can tell what the motor is actually turning. If so, that's pretty neat. If you set a VFD to 3450 rpm (57.5 Hz), the normal motor slip would give you a little over 3300 rpm at the motor itself.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#17
In reply to #12

Re: VFD ESP application

02/21/2010 1:30 PM

I'm not familiar with #4 but I guess it may be similar cross section to 6mm² and the volt drop would be in the region of 40V for 360m distance (1200 feet) so you will be a bit shy on voltage wich you could compensate for by programming motor voltage higher to see if this helps e.g. try 500V 60Hz 19A 10HP 3450rpm as motor data. You can look up volt drop calcs for your cable locally, what current does it actually draw?

Can you also monitor actual output Hz to see if slip is added correctly for your load e.g. at 19A load (some part is extra earth leakage so reduce switching frequency of VFD to 2kHz, say) you should expect +150rpm for the slip = 2.5Hz equivalent. So if you asked for 3450 this is 57.5Hz synchronous which would actually mean running at 60Hz but full load slip is 150rpm giving 3450 output.

In real life, motor slip is normally about 70% of motor data at this power, so motor nameplate is 3450rpm but it probably runs at about 3500 at full load at rated voltage.

So, is it Hz or volts its short of?

I take it you have no choke between VFD and motor as you did not reply to this point. I would normally recommend a choke at this cable length to avoid overcurrent tripping and afford the motor some protection to the volt doubling that the insulation will experience.

Good luck and hope you achieve a decent result. Hope the info is several posts have helped.

__________________
Something new every day!
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#14

Re: VFD ESP application

02/21/2010 2:32 AM

Dear Guest. It would help if you'd included your name, however, I would point out while you are worrying about the speed of the motor, you are not looking at the pump curve.

Many other contributions have pointed out to you how you calculate the actual motor speed, and how a VFS/VSD controls the RPM of a motor.

I am assuming that as you said "esp motor" you are using a submersible pump from a known supplier, and it would have the relevant documentation, pumps curves, test results etc, etc. Looking at any pump curve for a downhole pumps, you must consider the size of pump and its production rate, either gal per min or barrels per day.

So from the pump curves you now have the flow rate of your pump at a certain RPM How do you know its producing as per the pump curve? You can either measure the flow at surface or with a downhole monitoring tool, measure the discharge pressure and adjust the RPM on your VFD to give you the BEP of the operating range of the pump.

I assume you have knowledge of the Laws of affinity, if not I have included a part from Schlumberger Technical Service Manual

60 Hertz Versus 50 Hertz Operation

A submersible motor rotates at a nominal speed of 3500 RPM at a frequency of 60 Hertz. At a frequency of 50 Hertz, it rotates at a speed of 2915 RPM. For each individual pump series, the diameter of the stages cannot be changed so the only variables available to vary performance within a series are the different types of stages, the number of stages and the speed (RPM) at which they rotate. The rotational speed can only be changed by varying the frequency. When this speed change occurs, it varies the pump's operation according to mathematical relationships known as the affinity laws.

Affinity Laws for a Speed Change

50 Hertz Capacity Flow = 50/60 X 60 Hertz Flow = 0.833 X 60 Hertz Flow

50 Hertz Head = (50/60)2 X 60 Hertz Head = 0.694 X 60 Hertz Head

50 Hertz HP Pump Load = (50/60)3 X 60 Hertz HP Load = 0.579 X 60 Hertz HP Pump Load

50 Hertz Motor HP Load = 50/60 X 60 Hertz HP Rating = 0.833 X 60 Hertz HP Rating[p/] 50 Hertz Motor Voltage = 50/60 X 60 Hertz Motor Volts = 0.833 X 60 Hertz Motor Volts

50 Hertz Motor Amps = Same as 60 Hertz Motor Amps

50 Hertz Pump Efficiency = Same as 60 Hertz Pump Efficiency

Note: These laws only apply to pump behavior - not to well or system performance.

Now before anyone comes back and asks about TDH losses, first lets not get to complicated and second TDH calculations take into consideration the required stages to lift fluid to surface and therefore the motor HP, please lets take this as a given

Guest.... Just remember that what you see on paper is NEVER what you get in practice.

__________________
The square root of nothing is what you make it!
Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#15

Re: VFD ESP application

02/21/2010 6:23 AM

and while I think about it you must also ensure that your motor speed in relation to your pump curve is not so low that you do not achieve the correct motor cooling.

An ESP motor is ONLY cooled by the velocity of the well fluid passing over it as the pump lifts the fluid to surface, so be careful of what you adjust the minimum speed to and what size pump you install. If the pump is to big then you will burn the motor PDQ as you lower the speed

__________________
The square root of nothing is what you make it!
Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#16

Re: VFD ESP application

02/21/2010 12:13 PM

Revisit the programming of Ur drive.

Dickson

__________________
There is peace in silence and achievement in plans.
Reply
Participant

Join Date: Feb 2010
Posts: 3
Good Answers: 1
#18

Re: VFD ESP application

02/21/2010 9:05 PM

Hi Guest,

I´m not and expert in electricity, but i know something about controlling those kind of Motors, i have had some troubles controlling them.

I have just one question for you,

- when you say that the speed of the motor is not the same of the VFD, what is measuring the speed of the motor?

Comment: most VFD send a feedback of the speed of the motor to the motor controller throught a 4-20ma signal (that is the one you configure to show in the HMI or display). if your VFD works like that you should make a loop test to be sure that when the VFD is stopped (0 RPM) it´s sending you exact 4mA, if this measure is over or below this (according to your comment it could be below), you should fix this, maybe grounding the shield of the cable can help you. or changing the cable with shield, beldfoild and braid shield could help you.

hope my comment can help you.

Excuse my english, it´s not my foreing language, Like celia said " My english is not very good looking",

Yohan Axel Moreno S.

Reply
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#19

Re: VFD ESP application

02/21/2010 11:42 PM

Gentlemen one and all.

while every comment is correct and on point, everyone is concentrating on the motor speed and not the application. I note that everyone is offering answers that while are very correct, slightly miss the point that the application is for a submersible pump.

The application is not the same as for surface motors, I know I do this for a living, and I have offered several times to give a master class in ESP's to anyone that wants it.

ESP's require whole new way of looking at the application of motors.

First, ESP motors are ONLY cooled by the well fluid passing over the outside of the motor housing at a minimum velocity of 1 foot per second. This is achieved by matching the inflow of the well and production rate of the pump, the size of the well casing & using the correct OD of the motor. The resulting space between the motor and casing together with the flow rate will give you the velocity of the fluid over the motor. We have table for this.

Second, we don't use a 4-20mA signal to tell us the speed of the motor, the speed in the application is only of secondary concern, as the flow rate is primary. I will explain.

In an oil well, the pump MUST match the well inflow rate, if the pump production rate is higher than the inflow rate, then you empty the well as you have exceeded the amount of fluid flowing into the well thru the perforations, a "Pump off" situation. If the motor protection is set correctly then hopefully the motor will trip due to underload before you reach this point.

How do you match pump to well. Using something called "swabbing" where water is pump into the well to see how much can be absorbed by the the well (this is completed by Drilling Rig), hopefully it will give you a ball park figure to work with regarding the inflow rate. Then select the pump size in barrels per day, then the number of stages required to lift fluid to surface, then the motor HP for the number of stages.

So why use a VSD? With new wells it has been known that the well can produce more over time, especially if there is water injection into the resivour pushing well fluid (and oil) to the ESP. Any change in the frequency of the motor (and speed) will result in the movement of the pump curve. Typically any ESP motor can run from 45Hz to 65 Hz with no adverse effects on the motor. So using a VSD and one size of pump means that you can produce more (or less) from your well without having to change the pump every few months. In a nutshell, each frequency change gives you a new pump. Practically, you want that ESP to stay in that well for at least 2 years if not more

Yes typically in ALL applications of any ESP motor there is a volts drop across the cable. however that is calculated into the final equation for the "surface voltage".

Surface volts = required motor volts + volts drop of cable (per 1000 ft) (+/- 10%)

The voltages for VSD's are adjusted by have two high power transformers at surface, one step down to the VSD, the other to step up the VSD output to surface voltage. Please lets not get to complicated over transformers, lets accept they are the right ones for the job!

So we have the right pump and the right motor, its installed and running, how do we know its working correctly?

You need to monitor the production rate at surface to ensure that;

1: you are producing in the curve of the pump, you don't want the pump in upthrust or downthrust as the pump won't last 2 months.

2: your production rate is acceptable as per pump curve for the Hz you are running the ESP at, therefore you have the correct velocity of fluid cooling the motor

3: the motor running current is stable and the motor protection is set correctly to prevent motor damage.

Each time you want to make changes to the Hz, you first have to calculate if the voltage will change, typically ESP motors can handle a voltage change of +/- 10% before you have to think about changing the step-up TransX taps. A small frequency change will not bother the motor, but you MUST let the running current settle and adjust the underload and over load to the NEW running current.

So to sum it up... get the right pump, calculate the right motor required to do the job, ensure you are in the pump OR at the frequency you've set and you will have trouble free pumping for at least 2 to 3 years, providing no-one plays with it!

__________________
The square root of nothing is what you make it!
Reply Good Answer (Score 2)
Reply to Forum Thread 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); brich (3); Carol (1); Dickson (1); johanmorenolds (1); JRaef (2); MalcolmK (2); Tornado (3); travisslc500 (2)