DC Contactors vs. AC Contactors

02/25/2010 7:47 AM

hi, I wonder what is the difference between dc and ac contactors? in fact i dont know if there is different products as such ?

What i know is just dc current breaking is more difficult...

__________________
jinxnao
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: DC contactors

02/25/2010 1:04 PM

A DC contactor needs to have more separation (air gap) and possibly a magnetic blow-out to interrupt the arc that forms when opening. In AC, the current passes through zero 120 times per second, which facilitates quick arc extinguisment. With DC, that doesn't happen.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#2

Re: DC contractors

02/25/2010 3:46 PM

jinxnao; 24 volt D.C. contractors are quieter, A.C. contractors hum after a while . pac

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: DC contractors

02/25/2010 6:34 PM

You are referring to the coil operation, not the switching capacity.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4

Re: DC Contactors vs. AC Contactors

02/25/2010 10:24 PM

As well, the alloys used for DC contactor contacts have more silver in them.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#5

Re: DC Contactors vs. AC Contactors

02/26/2010 3:52 AM

so can we use dc contactors with a.c supply??

__________________
jinxnao
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #5

Re: DC Contactors vs. AC Contactors

02/26/2010 4:26 AM

Usually yes, but you will pay more for them compared to a contactor rated for AC only.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7
In reply to #5

Re: DC Contactors vs. AC Contactors

02/26/2010 10:25 AM

From an electrical stansdpoint, yes. From a legal one, perhaps.

Here in my jurisdiction (Canada) you could only "legally" use a DC contactor on an AC sourse, "IF" the contactor is also rated for AC. If it is only rated for DC use then you are prohibited from using it on anything other then a DC system.

Check the legal issues where ever it is you wish to use this equipment.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #7

Re: DC Contactors vs. AC Contactors

02/26/2010 10:27 AM

Good point.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply