I am looking for a US standard that dictates the wire sizing leaving a fuse block (ie NEC, NFPA, IEEE, UL). The question is; is the wire sized for the maximum capacity of the fuse block or the fuses installed.

For example;

I have a fuse block rated at 400A with 225A J-type fuses installed. This feeds a AC Siemens Drive rated at 205A. The manufacture recommended the fuse sizing but I have conflicting information on the wire sizing between the fuse block and the drive.

Any help is appreciated.

Thanks,

Rick S.

__________________
Very funny Scotty, now beam down my clothes!
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Fuse block/Fuse wire sizing

02/25/2010 10:43 AM

I see not difference in this installation than a 400 amps main switch with 225 amps fuses. The code only requires you to install a conductor rated at 225 amps. It does not require a 400 amp conductor based on the possibility that some one in the future might change the fuses to 400 amps. Is this what you were thinking?

Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Fuse block/Fuse wire sizing

02/25/2010 11:16 AM

NEC 240.4 (B)(2), page 70-83 (2008) has a guideline for the conductor protection based on fuse rating, not the fuse block (fuse holder) rating. So, if you use the 225A fuse and conductor ampacity is above 225A or immediate below 225A, it should be fine.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Fuse block/Fuse wire sizing

02/25/2010 1:18 PM

225A would likely be too small of a fuse for a 205A rated VFD, but that's just me.

The NEC requires that wire be sized for a minimum of 125% of the max amp rating of the drive. Fuses should then be sized for the wire. So you need conductors rated for 256A minimum. Fuses could be smaller but a VFD can draw up to 150% current for up to 1 minute, so make sure that fits under the fuse curve. In other words, look at the fuse curve and look at 308A (150% of 205), then follow across the time axis at 1 minute to make sure that you have not crossed the fuse melt curve.

Personally I would start with 250A fuses and wire before I even start looking at the fuse curve. Copper is not as expensive as down time.

Most major name VFDs such as Siemens are now rated as "Short Circuit Protective Devices" for their LOAD, so the only thing the fuses do now is protect the conductors leading to the VFD and the VFD front-end (converter).

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: May 2009
Location: Western PA, US
Posts: 22
#4
In reply to #3

Re: Fuse block/Fuse wire sizing

02/25/2010 3:23 PM

That is my understanding; that motors and drives require the wire to be sized to 125% of the load.

But...I cannot find the specific section that says this.

Rick S.

__________________
Very funny Scotty, now beam down my clothes!
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5
In reply to #4

Re: Fuse block/Fuse wire sizing

02/25/2010 5:08 PM

Your concern is now different. You original question was 'is the wire sized for the maximum capacity of the fuse block or the fuses installed'. Now your concern is about 'motors and drives require the wire to be sized to 125% of the load'.

Here is the NEC reference for 125% cable size for VFD and Motor:

VFD (or Adjustable Speed Drive): NEC 430.122

Motor: NEC 430.22

The previous thread http://cr4.globalspec.com/thread/36311/Sizing-Circuit-Breakers may help for sizing the cable and circuit breaker (or fuse).

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Active Contributor

Join Date: May 2009
Location: Western PA, US
Posts: 22
#6
In reply to #5

Re: Fuse block/Fuse wire sizing

02/26/2010 7:47 AM

You are correct, my question morphed. It all seems to depend on which direction you are looking at the circuit from, if you start at the motor and work your way back to the feeder fuses you end up with one size of wires and fuses but if you start with a mfg recommendation for the fuses and look at the circuit from the feeder to the motor you end up with another set of sizes.

I guess that is the primary problem here. Our electrical production has "decided" that all cable is underrated by some percentage and that matching the current on a fuse to the current rating of the cable to the "rated" current of a drive is acceptable.

This is why the question asking the location of the standard and why all the help is so greatly appreciated.

__________________
Very funny Scotty, now beam down my clothes!
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #6

Re: Fuse block/Fuse wire sizing

02/26/2010 2:06 PM

Pay close attention to that NEC section. The 125% applies to the MAX AMP RATING of the VFD, not the load connected to it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (2); msamad (2); rstanley3105 (2); wareagle (1)

Previous in Forum: Auto Recloser   Next in Forum: Dimmable Fluorescent Ballasts
You might be interested in: Fuse Holders, Pillow Block Bearings, Terminal Blocks

Advertisement