DC/AC Inverter for Off-Grid Solar Station

02/27/2010 4:40 AM

Dear All,

I am searching for the DC/AC inverter for solar off-grid station, AC output 230V 50Hz, 3000 VA (max), Dc input - 200-400 V DC from batteries

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: DC/AC Inverter for Off-Grid Solar Station

02/27/2010 8:47 AM

You may not find this easily. PVPowered could possible fabricate this. The DC input from the batteries being above 50V would require the NEC Chapter 480 t0 be applied. 480 says this must have restricted access and meet greater safety precautions. 48V nominal is commonly found as the input to most PV power centers (inverter/rectifiers). Switch to a 48V nominal. Use multiple Outback Flex80's in tandem to govern your batteries

Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#2

Re: DC/AC Inverter for Off-Grid Solar Station

02/27/2010 10:29 PM

Check wih Victron Energy Systems in Holland they may have something in their off grid product equipment

__________________
Elnav
Reply
Anonymous Poster
#9
In reply to #2

Re: DC/AC Inverter for Off-Grid Solar Station

03/02/2010 4:27 AM

Excellent advice!

Reply
Anonymous Poster
#3

Re: DC/AC Inverter for Off-Grid Solar Station

02/28/2010 2:04 AM

Check with American Superconductor (www.amsc.com).

Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#4

Re: DC/AC Inverter for Off-Grid Solar Station

02/28/2010 10:01 AM

That is some Big & Bad inverter!! If it was 100% effective, you would be talking about 250 amps......probably nearer 300 amps at 12 volts with an average effective unit.....that will have to be some battery(s) to supply that for more than a few minutes or so.....

Are you certain you need that much power, if yes, buy a diesel generator!! it will be cheaper than buying the correct batteries.....I mean - don't try using car batteries for this job.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Anonymous Poster
#5

Re: DC/AC Inverter for Off-Grid Solar Station

02/28/2010 10:11 AM

build one your self, ther is a lott of chematics on the www to work with.

Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6
In reply to #5

Re: DC/AC Inverter for Off-Grid Solar Station

02/28/2010 10:26 AM

At that current!!!! Please show me such a link!!! I am disbelieving though.....

It is slightly possible I suppose......I've been wrong before, I am sure it will happen again....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Power-User
Hobbies - CNC - New Member Hobbies - Musician - New Member

Join Date: Jan 2007
Location: South Africa Johannesburg
Posts: 187
Good Answers: 3
#10
In reply to #6

Re: DC/AC Inverter for Off-Grid Solar Station

03/03/2010 10:50 AM

Andy, It's 3KVA at 200 - 400VDC supply

__________________
Think and move like an electron
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12
In reply to #10

Re: DC/AC Inverter for Off-Grid Solar Station

03/03/2010 11:19 AM

OK. ...and your point was?

I was asking for a circuit diagram for a "real powerfull" DIY version, somewhwere on the web ( a guest said it was possible to find)......but I really do not believe that its possible....but FULLY prepared to be wrong if need be.....as ever!!

I certainly would not even try to make one of that sort of power......the small DIY ones are dangerous enough!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Power-User
Hobbies - CNC - New Member Hobbies - Musician - New Member

Join Date: Jan 2007
Location: South Africa Johannesburg
Posts: 187
Good Answers: 3
#11
In reply to #6

Re: DC/AC Inverter for Off-Grid Solar Station

03/03/2010 10:57 AM

Sorry, just could not resist the temptation

__________________
Think and move like an electron
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#13
In reply to #11

Re: DC/AC Inverter for Off-Grid Solar Station

03/03/2010 11:21 AM

WOW!!!!

Well "found", but "where" did you find it, I need a readable copy (if its for real!!)

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Power-User
Hobbies - CNC - New Member Hobbies - Musician - New Member

Join Date: Jan 2007
Location: South Africa Johannesburg
Posts: 187
Good Answers: 3
#14
In reply to #13

Re: DC/AC Inverter for Off-Grid Solar Station

03/03/2010 11:38 AM

Found it a few years ago when i had more time on my hands and stashed it in my "circuits" archive. I have viewed it and looks feasible however, i fully agree with you on NOT using 12VDC for this kind of application, current as you pointed out WAY to much. Its saved as a .gif on A4 size. Tell me where to sent it and its done. BTY i see in the bottom left hand corner the "author" is W.G Gfroer and some of the text looks German.

Gotto go now will check in later

Craig

__________________
Think and move like an electron
Reply Off Topic (Score 5)
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#7

Re: DC/AC Inverter for Off-Grid Solar Station

02/28/2010 11:29 AM

Are you certain it is only 3000 VA? That is a small system. Why do you want to run it at 200-400VDC? It presents an excessive danger for the application. As suggested above by other respondants, a safer <48VDC would require about 100A peak capacity when the DC is at its lower value. This is easier to find in commercially available inverters / UPS.

If you meant 3000 KVA, send me an email, this is real power electronics, we can help you.

Marco

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#8

Re: DC/AC Inverter for Off-Grid Solar Station

03/01/2010 6:08 AM

Why not using a normal VFD for electric motors in your application ?

Is you disable the input rectifier and connect a DC voltage (230 x sqrt 2) to the capacitors, you can get a variabel AC voltage at the output.

Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#15

Re: DC/AC Inverter for Off-Grid Solar Station

03/05/2010 6:06 PM

Why would you want to build one? For 170 quid ($250) you can buy one! Making an inverter is simple. Making a reliable inverter is another story.

You will need to wind a transformer because the ratio required is not a standard 230V:12+12. Getting a 3kVA transformer to start with will probably cost you near this sum. Protection against shot circuits, overloads, overheat and inductive spikes will all be neccesary if you want your device to run for a usable time.

This came out on the top line of a search...ebay.

__________________
En la casa del herrero, cuchillos de palo!
Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#16
In reply to #15

Re: DC/AC Inverter for Off-Grid Solar Station

03/05/2010 6:28 PM

Hey Cap Blanc, Are you set up as a Victron dealer as yet? noticed yesterday that their 100 amp chargers are now set up as universal input including 400 V DC presumably for their off grid PV installations. And they now have a 5000 watt inverter which can be parallelled for huge outputs.

Considering the original request was for 230V 50 HZ I would guess the poster is looking at an installation outside the US of A and therefore NEC does not necessarily apply.Might be in your area of the world. You guys are doing some really great PV projects over there.

Hyperion belonging to Jim Clarke is getting a refit with something like a dozen victron inverters plus a few chargers. From the pictures it looks to be wired as 3 phase at somewhere around 50KVA power levels.

Do you have any better info on their off grid systems?

__________________
Elnav
Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#17

Re: DC/AC Inverter for Off-Grid Solar Station

03/05/2010 8:28 PM

Hi Elnav,

Yes we have the Victron agency now also. Where is Hyperion, on that side of the pond?

I'll be a bit fedup if they do the change from chargers and inverters to combis over there as I had suggested the idea and put a proposal forward with the arguments for it.

regards

Chas

__________________
En la casa del herrero, cuchillos de palo!
Reply Off Topic (Score 5)
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#18
In reply to #17

Re: DC/AC Inverter for Off-Grid Solar Station

03/05/2010 10:58 PM

I do not know where she is being refitted. I saw the promo picture on Victron's website ( I think) and then thought of you. I was guessing it might have been somewhere in the Med possibly in your yard.

My next question is who uses 400 DC battery banks?

__________________
Elnav
Reply Off Topic (Score 5)
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#19
In reply to #18

Re: DC/AC Inverter for Off-Grid Solar Station

03/06/2010 2:27 AM

Hi Arild,

This is an old bit of advertising. In fact they have a bad reliabilty problem with this system because of the way that chargers of that generation don't share properly. It means that one of each bank of three chargers ends up being flat out while the other two are in float mode.That equipment space is very small and it gets very hot, even with airco.

Funny you should talk of 400V banks, we are just re-configuring a system of 400 down to 24V. There was a NZ company called Santon who made freq converters which were really UPSs. These had banks of 385V(nom) at about 200Ah. These were about the same era as the Helionetics converters from California.

Regards

Chas

__________________
En la casa del herrero, cuchillos de palo!
Reply Off Topic (Score 5)
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#20
In reply to #19

Re: DC/AC Inverter for Off-Grid Solar Station

03/06/2010 9:33 AM

You wrote: we are just re-configuring a system of 400 down to 24V. There was a NZ company called Santon who made freq converters which were really UPSs. These had banks of 385V(nom) at about 200Ah. These were about the same era as the Helionetics converters from California.:

So is this a case of dated technology and the latest thinking being 200V - 400V DC is not such a good idea. Back in the early nineties I worked at a power transformer station and we had 200 V DC back up in case the grid went down totally. The DC battery bank would allow us to operate the switch gear and get the power transformer station back on line. We always considered the battery room one of the most hazardous places in the station to perform work in.

Too bad the original poster was a 'guest' We will never know if this thread is being seen by the OP. Sounds like Helionetics is a company with a product that fits the OP's original request criteria

__________________
Elnav
Reply