Power Consumption Calculation

02/27/2010 11:49 AM

i have an mold temperature controller.

and it is run for 24 hours.

its ratings are as follows

I=5.5 amperes

V=440 volts

it has no resistance.

I want its power consumption for a day.

please help me.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: power consumption calculation

02/27/2010 11:54 AM

Check this out:
Power Computations

Reply
Anonymous Poster
#2

Re: Power Consumption Calculation

02/27/2010 1:26 PM

Based on Ohm's Law:

Vt = 440V

It = 5.5A

Rt = 80ohms

Pt = 2420W

KwH (12hrs) = 29.04 KwH

Kwh (24hrs) = 58.08 KwH

Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #2

Re: Power Consumption Calculation

02/27/2010 1:41 PM

The voltage system 440V indicates that it is a 3 phase system and I am assuming it is 3 phase heater. Since the heater load is resistive, the power factor (cosφ) is 1.

The power consumption

= 1.732 x V x I x cosφ = 1.732 x 440 x 5.5 x 1 = 4,191 W ~ 4.2 KW

The daily energy consumption = 4.2 x 24 Kwh ~ 100 Kwh

This is the maximum consumption for the heater. The heater may not consume the full load all the times and the actual consumption will be less than this.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #4

Re: Power Consumption Calculation

02/27/2010 1:46 PM

Yeah, I forgot that 440 is likely a three phase circuit.

(For those that don't know 1.732≈√3)

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Power Consumption Calculation

02/27/2010 1:41 PM

I presume that when you say "it has no resistance" that you mean that you are not given a value for the resistance. From the information you have, one cannot calculate the actual or anticipated power consumption for the whole day. This temperature controller will certainly not be heating the mold each and every second of your 24 hour period of time. If you did need it heating for every second of a constant 24 hours, you would not need a controller then. The only thing you can calculate is the maximum energy usage which is a very simple straight forward calculation of:

V*I*T=Energy → 440 V*5.5 A*24 hr≈58 kWh ≈209 mega-joules

I'm certain your ambient air temperature, insulation, mass of the mold and contents will alter your actual usage to a number less than this.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Power Consumption Calculation

02/27/2010 1:43 PM

You need to make a distinction between the controller and the heater it is controlling.

The controller consumes very little power; it is the heater that is the major power consumer.

The controller may be rated at 5.5 amps, but what does the heater actually draw? If possible, find out the kW rating of the heater. Note also that the controller will cycle the heater intermittently, or will modulate the voltage to the heater. In either case, the heater does not draw its full rated power all the time. To get the actual energy usage of the heater you would need to determine what fraction of time it is on, or perhaps put a kWh meter or other instrument on it.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Good Answer
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); lyn (1); msamad (1); redfred (2); Tornado (1)

Previous in Forum: DC/AC Inverter for Off-Grid Solar Station   Next in Forum: 24V Motor with 90:1 Gearbox - Change to AC Motor?

Advertisement