LT Switchgear Upgrades

03/01/2010 12:30 PM

Dear all,

we have 5.5KW LCP module in LT mcc but we have the motor of capacity 22kw, 415v, 3ph, full load current: 39A. No other spare modules are available. now i want upgrade the 5.5kw module to 22kw module. what are the things to be considered for conversion. I had doubt in dimension of the modules.

Is there any possible ways to solve this problem.

__________________
tsk
Register to Reply
Pathfinder Tags: Lt switchgear
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: LT Switchgear Upgrades

03/01/2010 4:45 PM

Quote "now i want upgrade the 5.5kw module to 22kw module."

I am not sure what you mean by module. Are you referring to your panel?

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: LT Switchgear Upgrades

03/01/2010 7:01 PM

I think 'module' here is MCC cubicle for the motor starter.

In this case, space (dimension) definitely will be a problem. In addition, the starter terminal connection (plug-in bushing) will be under-rated. I would suggest you to contact the MCC vendor. The vendor may have compact starter to fit in smaller space and the plug-in bushing can be replaceable with higher rating.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: LT Switchgear Upgrades

03/01/2010 11:26 PM

It is possible.However you have to do little bit of study.

Is it draw out module or fixed module ?

If it is fixed module ,you have find out the size of the module and ascertain whether the bigger size components can be accomodated.

List out the components and wires required for 22 kw starter.

Remove the existing components of 5.5 kw starter.

Fix the new components for 22 kW starter and rewire the circuit.

If it is drawout module check the fixed contacts of the module which gets contact with the busbar for adequacy of rating.

in my opinion for 5.5 and 22 kw ratings the contacts will be same rated to 100 Amps if so no problem.

Please ensure 22 kw is also DOL starting.

If it is going to be Stardelta starting the module size may not be adequate to accomodate all the components since for SD starter the number of components are much more than the DOL starter.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#4

Re: LT Switchgear Upgrades

03/02/2010 2:32 PM

Before making any changes, you will need to verify the capacity of each affected part of the MCC. Most MCC's have one horizontal main bus, and several vertical branch buses (one for each module stack). The main bus is designed for the full load capacity of the entire MCC. The branch bus is usually lower capacity.

Sum the currents of all the existing loads on the branch bus where the new load is to be attached, then add the current of the new load. Compare that total to the capacity of the branch bus. Repeat the same exercise with all loads on the MCC compared to the capacity of the main bus. I suspect that the branch bus, and possibly the main bus, will be overloaded.

If you can't use the existing 5.5 KW cubicle, but the main bus has available capacity for the 22KW motor, there are a couple other options available.

1) You may be able to expand the MCC by adding another vertical stack at the end. If the MCC is not designed for expansion, this is usually not practical.

2. You can attach a separately-mounted starter on the side (end) of the MCC and run cable from the main bus to the line side of the new starter. I've done this a couple times where the cost of upgrading the MCC was more than the project was worth.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Member

Join Date: Dec 2006
Posts: 7
#5

Re: LT Switchgear Upgrades

08/26/2014 7:28 AM

Dear all,

Would be better to specifically mention the MCC type for example AB. As per NEMA standard, starters defined by sizes, at 480VAC, size 1 (2 -10HP), size 2 (15-25HP), size 3 (30-50HP).

Simply size 1 can not be replaced by size 3 because space requirement would be different according to NEMA.

Rest of the factors like diversity, loading the vertical bus, overload relay and cable need to be considered.

Register to Reply Off Topic (Score 5)
Register to Reply 5 comments