Short Circuit Current

03/03/2010 10:20 AM

Hi everybogy,

Could you enlighten me on this case:

1. If i calculate the SC current in the power system and its showed 17kA.

2. What happen when I choose the MCCB with the SC current is 10kA? And what is exactly SC current on the nameplate of MCCB means?

Thanks,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Short circuit current

03/03/2010 10:48 AM

The rating on the circuit breaker or fuse is the amount of short circuit current that the device can interrupt properly. This rating must be greater than the calculated short circuit current available. In your example, the MCCB is inadequate.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Good Answer
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#2
In reply to #1

Re: Short circuit current

03/03/2010 11:01 AM

Tornado:

Thank you. If I have one MCCB with SC current rated at 30kA and a plan to buy a brand new one at 20kA,

Which is the better way? Can a 30kA MCCB is edequate to trip against such a low SC current in the system?

By the way, MCCb's overcurrent protection does nothing against the SC case?

Regards,

__________________
Anything that can go wrong, will go wrong
Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Short circuit current

03/03/2010 11:49 AM

There are two levels of current to be considered:

1. The level of over current that protects the motor (or other device) and the wiring to it. This may be a few amperes (or tens or hundreds of amperes).

2. The level of fault current, such as could occur if a metal object makes contact with any of the wiring. This is short circuit current, 17 kA in your case.

The first of these is the nominal rating of the circuit breaker or fuse, for example 50 A. The breaker or fuse must also be rated for the maximum current it can interrupt; some common ratings are 10 kA, 22 kA, 50 kA, 100 kA, and 200 kA. In your case, either the 20 kA or 30 kA breaker will work, so can choose the less expensive one. The breaker or fuse must also be rated for voltage at least as high as the system provides. Some common voltage ratings are 250 V and 600 V.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Good Answer (Score 2)
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4
In reply to #2

Re: Short circuit current

03/03/2010 11:53 PM

In MCCB if the rating is indicated as 3O kA for one sec, this device will withstand a current flow of 30 kA for one sec without any damge to the device.

Setting of MCCB is different, MCCBs will have fixed setting for shortcircuit or variable setting.

In the case fixed settings, the MCCB will act when the current flows 10 times the nominal current.

Generally the Fixed setting would be 10 times the nominal rating.

Supposing you have 100 A MCCB with fixed short circuit settings.The Nominal current of the MCCB is 100 Amps

This MCCB will trip only when the Short circuit current is More than 10 x 100=1000 A.

In the case of variable settings short circuit current settings of the MCCB can be set depending on the circuit .

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply Score 1 for Off Topic
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#5
In reply to #4

Re: Short circuit current

03/04/2010 12:03 AM

Ramvinod:

Thank you.

I understand that it can withstand the 30kA SC current e.g in 1 sec..

But if I choose the MCCB with SC current rated at 200kA (the biggest) as in Tornado's comment. So, there would be any acting from this one if my system is short circuited at 17kA?

Supposing this MCCB comes with fixed setting at 200kA. It is just supposition only because the 200kA SC would be very big in size.

Regards,

__________________
Anything that can go wrong, will go wrong
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #4

Re: Short circuit current

03/04/2010 12:39 AM

Almost none of that "information" was correct, although a thermal-magnetic circuit breaker works sort of like that.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#7
In reply to #6

Re: Short circuit current

03/04/2010 1:22 AM

please point out the mistakes so that I can get corrected

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply Score 1 for Good Answer
3
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8

Re: Short Circuit Current

03/04/2010 1:58 AM

I will try to give a capsule description of how a circuit breaker works. Imagine that you have a motor protected by a thermal-only circuit breaker of nominal rating 50 A and interrupting rating 20 kA. If the motor (and its circuit) draws 50 A, the CB will remain closed indefinitely. If the current is 55 A, such as if the motor is overloaded or there is moisture in the wiring, after a time of maybe several minutes, the CB will open, interrupting current to the motor. If the current is 60 A, the CB will open more quickly. The more the current exceeds the rated 50 A, the faster the heat-sensing elements in the CB warm up, tripping the breaker.

The technical data for CBs typically shows a graph of current versus time, which tells how quickly the CB opens at various levels of overcurrent.

Continuing with our example, a current of 100 amps might trip this breaker in something like a second; 150 amps in half a second; etc. The terms "overload" and "overcurrent" are used to describe currents that moderately exceed the ratings of appliances, wires, and nominal CB ratings.

"Fault current", on the other hand, is about very large currents, such as if a conductor comes loose and touches a grounded/earthed component, or two line conductors come into contact with each other. In these instances, the currents can be thousands of amps. In your case, the electrical system (transformer or generator) is capable of delivering 17 kA in the event of a "dead short", and thus your CBs must be able to interrupt ("withstand" is a wrong word) this amount of current. Greater interrupting ratings such as 100 kA or 200 kA are not necessary, but they will work fine to interrupt smaller currents like 200 A, 2000 A, or 20 kA.

I'll try to continue this later....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Good Answer (Score 3)
Anonymous Poster
#9
In reply to #8

Re: Short Circuit Current

03/04/2010 2:33 AM

Nice answar, can u pls send me some soft copy or suggest some book on Short circuit current, casecading effect of switch gear,

my email id is spunit@godrej.com

i am from india & working in a power intensive plant

regards

punit

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #9

Re: Short Circuit Current

03/04/2010 3:18 AM

Thank you for your interest.

Unfortunately, I do not have this information in any one book to recommend. I once designed UL-508 industrial control panels, and I got information from a variety of sources. Bussmann Fuse literature is really good. The US Navy book on Basic Electricity likewise. The NEC. Most manufacturer's catalogs for motor starters, circuit breakers, transformers, wiring supplies, etc. have a technical section. I have pieced together lots of stuff from those. I tend to forget details, but the more interesting principles seem to stick.

The OP seems to be new at some of this, but is asking excellent questions. With a little guidance, he is likely to learn well. Two of the real CR4 electrical experts would be JRaef and msamad. Anyone would do well to study their posts carefully.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#11
In reply to #10

Re: Short Circuit Current

03/05/2010 10:48 PM

I read this thread till Tornado's comment # 3 and found it was very well answered, and it was me who first voted GA for it. For curiosity, I just took a look into it now and definitely Tornado's further explanation is also excellent.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #11

Re: Short Circuit Current

03/06/2010 12:03 AM

Thank you kindly. I am not an EE or other high-level expert, but I try to understand theory. Some of that may seem counterintuitive at first, so when I attempt to explain something, I look for common-sense descriptions at a non-technical level, yet still technically correct.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Active Contributor

Join Date: Feb 2010
Posts: 16
Good Answers: 2
#13
In reply to #12

Re: Short Circuit Current

03/06/2010 11:37 AM

Your answer is an excellent explanation on how a CB behaves.

The one thing that the questioner asks, and doesn't seem to understand, is that if the fault current is larger than the rated interrupting of the CB then on the chance that an SC happens, the CB will need to be disposed of because of damage. So he would have a VERY expensive fuse.

So to probably say what has already been said, the MCCB must be rated to withstand the maximum anticipated fault current or you have defeated the purpose of having a circuit breaker as it should not (and may not be able to) be reset after a fault current trip (as opposed to the other trips described).

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#14
In reply to #12

Re: Short Circuit Current

03/06/2010 8:41 PM

Yes I understood the problem.I should have given more elaborate answer.

What I meant was that in the case of MCCBS where only instantaneous releases are provided the setting value of the release matters.

In the case of MCCBs where LSI releases are provided the tripping of MCCB will follow inverse time curve.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#15
In reply to #14

Re: Short Circuit Current

03/07/2010 9:10 PM

Dear all,

I appreciate your effort supporting me especially Tornado's although EE is not his specialty.

But, I back at here with a confusion. All of us know that with 22kA MCCB and 17kA SC in the system, it totally can handle the SC current safely.

Things would be different if I choose 200kA MCCB. Because with such a high interupting capacity. The SC current in the system is much lower than the tripping range of the MCCB. I think that, it is somewhat difficcult for this MCCB to sense the SC. It might got wrong function and let the CS get through (God knows), or might the SC lasts long enough to make this MCCB tripped or the other MCCB in the system (with lower SC current rating) acted. All of us know that this is a coordination problem.

It is worth for consideration in a while.

Regards,

Hien

__________________
Anything that can go wrong, will go wrong
Reply
Active Contributor

Join Date: Feb 2010
Posts: 16
Good Answers: 2
#16
In reply to #15

Re: Short Circuit Current

03/07/2010 10:10 PM

The short circuit withstand rating has nothing to do with the trip rating.

You can get a 200kA circuit breaker and put a trip rating plug of 400A in it. It will trip at some level above 400A depending on how long the overcurrent condition exists and at what level (inverse time rating). It will however, trip instantaneously (for all intents and purposes) if you give it a bolted fault. With 17kA current available, this circuit breaker will just yawn at this level of current and can be reset after the fault is corrected with little need for concern.

However, if you have a 10kA circuit breaker in the same service with a 400A trip rating, it too will trip above 400A after a period of time inverse to the load passing through it that is above 400A. This device will not safely withstand a bolted fault. With 17kA available current available, a bolted fault will damage the circuit breaker, probably beyond serviceability.

The short circuit withstand capability is NOT functionally related to the trip current of the device. Unless you want to assume the trivial case that the trip rating must always be below the short circuit withstand rating.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#17
In reply to #15

Re: Short Circuit Current

03/07/2010 10:34 PM

This may be a bit tricky to understand, but a circuit breaker or fuse will "sense" and interrupt any current above its nominal rating, provided that it can also interrupt the maximum current that system can deliver.

For instance, a 50A circuit breaker or fuse with an interrupting capacity of 200kA will (according to its current-time curve) open at any sustained current over 50A. If the current is only a little over 50A, this will take some considerable time. The greater the current is, the less time it will take for the CB or fuse to trip.

A 50A CB with 20kA interrupting capacity and a 50A CB with 200kA capacity will behave about the same for currents up to 20kA. But above 20kA, the first of these may fail to interrupt the current, probably because its dimensions are too small to provide sufficient arc separation. But there will be no problem with a CB of large interrupting capacity placed into a lower ampacity system. It will still interrupt lesser currents just fine.

You are asking excellent questions in a topic that is subtle to explain. With patience and time, you will become an expert in this.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
3
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#19
In reply to #17

Re: Short Circuit Current

03/07/2010 11:41 PM

What I realized, the OP is confused about the 'short circuit rating (or interrupting capacity)' and the 'short circuit setting' of CB. It is again further explained by JSCadman and Tornado but let me add some additional help with the example of a CB whose rating is 100 A and short circuit rating is 10kA (10,000 A).

CB Rating: The CB is rated 100 A. It means that the CB can carry 100 A current and it will not trip with 100 A or less current passing through it.

Short circuit rating (or interrupting capacity) of CB: This is the maximum amount of current the CB can safely interrupt the circuit when passing through it. A CB of 10 kA short circuit capacity is able to interrupt the current path safely when 10kA or less than 10kA current flows into it. If this CB is used in a circuit where the short circuit current can be up to 17kA (as the OP mentioned in the original posting), the CB will not be able to interrupt this current by extinguishing the arc, when the fault occurs and the CB trips. There will be continuous arching within CB and a disaster can happen.

Short circuit setting of CB: The short circuit setting of the CB is generally expressed in multiples of CB rating. A short circuit setting of 8 means 8 x 100 A = 800 A setting. In this case, the CB will trip instantaneously when more than 800 A current pass through it. So, a short current between 800 A to 10,000 A, this CB will trip and safely disconnect the circuit (with extinguishing the arc within it). Any current beyond 10 kA (10,000 A), the CB will trip but it will not interrupt the arc created within it.

The CB will trip any current between 100 A and 800 A but there will be time delay and the delay depends on the amount of current. This range of current falls within the overload characteristics of the CB.

Hope it is clear now.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 3)
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#18

Re: Short Circuit Current

03/07/2010 11:38 PM

For understanding you have to assume MCCBs into 3 catagories

1) MCCB with over current trip device

2) MCCB with trip device instantaneous setting only

3) MCCB with out trip device.

Let us assume a circuit where the Sc level is 17 kA.

a)when you connect the MCCB without trip device of 20 kA rating - nothing will happen to the circuit and to the MCCB.

b)When you connect the MCCB without trip device of 10 kA rating- the MCCB will get damaged because it is rated for 10 kA only and the MCCB can not be reused even after repair.

c) If the MCCB of 20 kA with instantaneous trip device is coneected with setting of say 10 kA, during the fault (fault current is 17 kA) this will trip instantaneously.No damage occurs to the device.

d) If the MCCB of 20 kA with over current trip device is connected with a setting,during the fault the breaker will trip after some time (follows inverse time characterstics),no damage occurs to the device

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Reply to Forum Thread 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); hien.nguyenquoc (3); JSCadman (2); msamad (2); ramvinod (4); Tornado (7)