Previous in Forum: Causes of Circuit Breaker Flashover   Next in Forum: Distance Between Cables
Clean Earthing vs. Dirty Earthing
03/05/2010 3:14 AM
Please someone tell me about the difference between
System / Clean Earthing (CE)
Instrument Signal Earthing (IE)
Power / Safety / Dirty Earthing (PE)
Re: Types of earthing system required
03/05/2010 3:34 AM
Earth is earth is earth.
However, the principle between power and instrument earths is to gather all the power earth conductors onto a busbar and bond that to earth, then gather all the instrument earths onto a separate busbar, and bond that to earth via a separate conductor. The earthing point can be the same.
Grouping the earths onto separate busbars minimises the risk of noise on the power earth conductors affecting the instrument earth conductors and inducing unwanted signals onto those circuits.
Re: Clean Earthing vs. Dirty Earthing
03/05/2010 11:56 PM
Electronic equipment are sensitive to raise in Earth potential, which in turn is due to increase in Earth resistivity.
Hence, a separate "Treated earth pit" is assigned for terminating all Clean Earthing Signals. Resistivity is to be monitored and periodic maintenance is to be made (adding water to the pit). In a big plant, it is not possible to consider "Treated earth pits" for all points.
Noise is another concern.
Good Answers: 170
03/09/2010 9:25 AM
As per IEEE 1100, there is no such thing as Clean Earth, Dirty Earth, Signal Earth, etc. To quote verbatim:
Vide Cl. 9.10.12.2 of IEEE 1100, "the use of any separate, isolated, insulated, dedicated, clean, quite, signal, computer, electronic or other such improper form of earth grounding electrodes for use as a point of connection of the EGC (Equipment Grounding Conductor) is not recommended".
Even IEC does not permit this.
Vide IEC 60364-7-707: The use of independent, "isolated" earth electrodes for computer or
electronic systems is not recommended/
permitted.
Register to Reply 3 comments
Anonymous Poster (1); electricalexpert65 (1); PWSlack (1)
You might be interested in: Clean Benches, Liquid Leak Detectors