Distance Between Cables

03/05/2010 4:36 AM

We have to lay cables for 11 KV/ 132 KV ,80 MVA generator transformer.

We think that 12 runs of 400 sqmm ,3core ,XLPE,Alu cable will be suitablefor 11 KV side on GI trays on Air.We would like to know whether the increase in number of runs will derate the cable.what shall be the distance between one cable and another cable on a horizontal tray. What is the maximum allowable bending radius of the 400 sqmm cable.Can any one give guidance in this regard.

Sriram

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: sriram

03/05/2010 4:49 AM

Which country code is to be followed?

Ambient conditions?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jan 2010
Posts: 2
#2
In reply to #1

Re: sriram

03/05/2010 11:06 PM

We are in India .The ambient temprature is from 45 to 48 deg cent.

Sriram

Register to Reply
Associate

Join Date: Jan 2010
Location: Singapore
Posts: 26
#4
In reply to #2

Re: sriram

03/05/2010 11:48 PM

Refer to IS-1255

You may choose any spacing (greater than minimum required as specified in IS) & accordingly your derating factor changes. You may get lesser no. of runs requirement for higher spacing (if you are looking from ampacity perspective only). There are other aspects like voltage drop during normal running, during highest motor starting..

go to any cable manufacturer's website, you will get derating table.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#3

Re: Distance Between Cables

03/05/2010 11:47 PM

Current rating furnished by manufacturers assumes "1 D" (D= Diameter of the cable) between two runs of cable, an ambient of 30 deg.C. You have consider derating due to both. For India, better consider ambient as 50 deg.C. If you decrease the distance between the cable, separate derating applicable. Consult with Cable catalogue / vendor.

It is better if you consider single core cable in tre-foil formation instead of three core cable. This saves cable cost as well as helps in better layout. Usually 3C cable is good upto 240 sq.mm. for easy laying. You may need 6 runs of 1C-630 sq.mm. / Ph only.

Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#5

Re: Distance Between Cables

03/06/2010 12:20 AM

For bending radius, if you have single core cable then the radius= 20D and for three phas cable, radius=15D

Where D= overall diameter of the cable(including insulation and everything).

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#6

Re: Distance Between Cables

03/07/2010 4:32 PM

Ur free to lay Ur XLPE cable side by side with a slit gap of of 5mm or more to allow for air circulation or one suspended on top of another. The important thing is to allow for free air circulation that enhances heat dissipation.

For the bend, take any bend of appropriate internal radius that will not be injurious to the cable.

Dickson.

__________________
There is peace in silence and achievement in plans.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Distance Between Cables

03/09/2010 9:20 AM

As per Clause 5.3 of IS 1255, the minimum bending radius of 11kV Multi core XLPE Cables is 15 D, where 'D' is the over all diameter of the cable.

Though the IS does not specify any spacing between cables laid horizontally on a cable tray, cable manufacturers do give appropriate de-rating factors, for carious cable spacings right from touching to many clearance distnaces. This is given both for horizontal spacing as well as vertical spacing. This has to be referred to and the cable to be de-rated accordingly.

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Dickson (1); electricalexpert65 (1); nshingate (1); PWSlack (1); sidhu16 (1); thiagusriram (1)

Previous in Forum: Clean Earthing vs. Dirty Earthing   Next in Forum: Transformer Tertiary Winding

Advertisement