Calculating Maximum Demand

03/05/2010 11:17 AM

I have a problem to calculate max demand for a factory.
in normal case we calculate max demand in this way for 15 minute windows
P=√3.V.I.cos@
kW = v3 supply V I cos@
86 = 1.73 380 131 1.00

but in my case, the factory receive it's energy by 3 line, that each line connected to different substation.
every line have it's one max demand in 15 minute, but i need one demand value for all energy that the factory received.

I know that, it is wrong if i sum up these 3 max demand,
but if i calculate KW for each line separately in start of every minute by a device that have a clock, synchronized by GPS, so i can sum up KW of these 3 line and then calculate Max Demand based on it.
Is this correct?
or is there any better way?


Thanks

Register to Reply
Pathfinder Tags: substation demand
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Calculating Maximum Demand

03/05/2010 4:41 PM

Quote "if i calculate KW for each line separately in start of every minute by a device that have a clock, synchronized by GPS, so i can sum up KW of these 3 line and then calculate Max Demand based on it. "

If I am understanding you correctly, your method appears to be right. Each sub will have its own 15 minute demand during the day but that may not be the maximum system demand. The max system demand occurs at some point in time during the day. So you will need to record each sub demand and pick the time when the sum of the three subs is the greatest. There are many recording meters that can do this for you.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Mar 2010
Posts: 4
#3
In reply to #1

Re: Calculating Maximum Demand

03/06/2010 1:33 AM

what type of meters can do this for me?

Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#2

Re: Calculating Maximum Demand

03/05/2010 11:46 PM

Pls elaborate your power scenario. Do all three supplies are synchronised or isolated? Do each line supply to different mills or areas? Do all the three areas work simultaneously?

Register to Reply
Participant

Join Date: Mar 2010
Posts: 4
#4
In reply to #2

Re: Calculating Maximum Demand

03/06/2010 1:47 AM

about power scenario, i must say that the factory receive all it's power from one supplier and because of that, the supplier needs to calculate one max demand.

but the problem is that, the factory receive all it's power by 3 line from 3 substation.

every substation have it's one meter to calculate demand for that line but it is not synchronized by the other meters for other lines.

the factory try to share required power on it's input line to minimized it's demand.

I think we must have all demand data for all line in one place to calculate max demand.

or having a meter that can share data with other meters to do that!

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: Calculating Maximum Demand

03/06/2010 11:41 AM
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6

Re: Calculating Maximum Demand

03/06/2010 5:45 PM

Maximum demand is measured in kVA which is UxIxSqrt(3) and no power factor since =1.00 here.

The way the Maximum demand works: There are Two items used: the Total Time of Measurement T1 and the Periodic time for integration tp. These differ from metering company to other, or from country to country. Let us say that T1 = 15 minutes and that T1 has been divided into 30 sec intervals. That makes 15 x 60 / 30 = 30 intervals or periods of measurement.

Then: during every 30 sec, the meter measures the maximum demand kVA and records it. Each time this is measured, for every interval of 30 sec thereafter, the M.D. value is recorded untill the 15 minutes are elapsed. Then the Highest value of all these periods is recorded and displayed. The separate registers for the 30s intervals are zeroed and the process repeats.

Every 15 minutes, the M.D. value is Updated to the highest only.

At month end, the M.D. register is read and billed then the register is zeroed to start a new month billing period.

Now Your Problem: If I Understood you, You have 3 Supply lines to your factory. If the 3 supplies are supplying at the same time 3 different area of your factory, then they are billed separately (3 metering devices, one for each separate zones. In this case, the 3 Maximum demand values will be added or billed separately with the kWh values for 3 bills.

If the 3 supplies are used to supply the same Zone (same circuit with the same machinery) and used to switch over to each supply when the others failed, then the maximum demand should not be added but the maximum of the 3 meters will be considered.

On the other hand, all depends on who are the 3 suppliers: 3 different power suppliers or the same company? And how the arrangement has been done with them.

........................

Register to Reply Score 1 for Off Topic
Participant

Join Date: Mar 2010
Posts: 4
#7
In reply to #6

Re: Calculating Maximum Demand

03/07/2010 11:22 AM

Thanks for your complete response.

But the problem is that we have one supplier, and the factory receive it's power from many lines because they needs all lines power at the same time.

there is no switching, the factory use all 3 line power for it's production together.

and this is because the factory have many improvement in last years, and may need more power in feature.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#8
In reply to #7

Re: Calculating Maximum Demand

03/08/2010 7:43 AM

I am Glad to have been of help.

And as explained, the 3 maximum demand will be added by the supplier.

If you could put all the lines into One of bigger capacity (transformer, Supply source...) so as to force the supply company to meter you from one single source, then you will lower the maximum demand if the 3 zones supplied do not have their peak demand at the same time (which will be most of the times)!!

Also, Try to start the biggest motors (or loads) before the smaller ones and in sequence so as not to have too much peak demand.

This will also help reduce the maximum demand.

Register to Reply
Anonymous Poster
#9

Re: Calculating Maximum Demand

03/08/2010 9:11 AM

Check out what is known as a totalizer. Your three sources probably each generate pulses for the meter, collect the pulses over a 15 minute period, and determine the demand for that period. A totalizer just adds the pulses from each source and then you can compute the total demand for the plant. It will almost always be less than the peak from each source, unless they just all happen to hit their peak during the same 15 minutes, which is possible if the entire plant load is tied together and the three sources act as a network. If different parts of the plant are isolated and served by a single source, then they probably won't occur at the same time.

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!