Voltage and Amperage reduction

03/05/2010 5:25 PM

I need to charge a battery (12 Volts DC, 10 Amps MAX) but the closest source of electric power is an Electric Motor (250 Volts DC, 90 Amps). Is there any battery charge controller that I could use for this? If not, is there any other alternative?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
5
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Voltage and Amperage reduction

03/05/2010 10:45 PM

Sure there are a lot of options on how to charge a battery. It all depends on the battery type and the available power sources. But an electric motor is technically an electric load and not a power source. Yes, it can very easily be converted to a power generator if a prime mover spins the shaft, but then we call it a generator. So to use your electric motor, you must have some electric power source that is capable of driving this 22.5 kilowatt motor. This much power, almost never gets delivered by just a DC power distribution. So first, I would recommend using the standard AC power line voltages to run through a commercially available battery charger for the type of battery you have. Remember lithium, lead acid, NIMH and NICD batteries all have different charge characteristics so to maximize battery lifetimes you should use the appropriate style charging scheme.

But keeping to your stated restriction of only having a 250 volt source, one could easily design a linear dropping circuit to drop the 250V to 12V while drawing only 10 amperes. But this will dissipate a lot of lost power during the charging cycle since (250-12)volts * 10 amperes = 2.38 kilowatts. So to drop the voltage down to a practical value you should utilize a DC/DC switching supply before the charge controlling circuitry that will maintain the correct conditions so that your lithium battery doesn't ignite, your lead acid battery doesn't boil dry, or that neither your NIMH or NICD batteries fuse into a useless lump of chemical goo.

I hope that this helps, and that I didn't add to much information.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 5)
Active Contributor

Join Date: Mar 2010
Posts: 10
#3
In reply to #1

Re: Voltage and Amperage reduction

03/06/2010 12:27 AM

I'm sorry! When I'm talking about using the electric motor as a source I mean the power lines that supply the electricity to it. Those lines supply the motor with 230VDC and the load from the motor is around 90 Amps.

My idea is to charge the battery only when the motor is running so the motor gets must of the electric load and the battery only gets the small part that it needs.

Is this possible?

Thanks in advance for your comments...

Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#9
In reply to #3

Re: Voltage and Amperage reduction

03/06/2010 2:49 PM

It is a pity that your supply is dc, as this does complicate things. If it was an ac supply, then of course there would be no problem finding a suitable battery charger.

As another poster said above, the only efficient way to do this is to use a switchmode voltage reducer. A quick google suggests that these are not exactly common, so you may need to find someone who can design and build this for you. It is quite technically feasible, but by no means a simple task and is well beyond DIY territory.

__________________
paulusgnome
Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 10
#10
In reply to #9

Re: Voltage and Amperage reduction

03/06/2010 6:46 PM

Thank you!

Register to Reply Off Topic (Score 5)
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#11
In reply to #10

Re: Voltage and Amperage reduction

03/06/2010 7:11 PM

No worries Cheko.

Just to clarify, the reason that a suitable switchmode reducer is not available is due to the voltage of the supply. There are legions of 24-to-12V and 48-to-12V reducers out there, but 250vdc is a less common supply voltage.

Best of luck. If you need someone to help you with the design I may be able to steer you in the direction of an expert who does this sort of thing for a living...

__________________
paulusgnome
Register to Reply Off Topic (Score 5)
Member

Join Date: Sep 2011
Posts: 8
#39
In reply to #3

Re: Voltage and Amperage reduction

10/04/2011 9:44 AM

This is the situation. The only available power supply in such space area of installation is 230VDC which is intermittently turned on and off [75% continuously cycling ...] On this space area is a need to power a device drawing a 5A load at 10VDC. Actually I had one...and another one...but they all burnt because they are not designed for the intermittent factor of being turned on and off...24 hours all week...

any advice is a relief...I need help on drawing applicable circuit to utilize the existing

230VDC supply into 10VDC sufficient enough to feed 5A DC load cycling 75% continuously turn on and off without burning.

Register to Reply
Active Contributor

Join Date: Oct 2009
Posts: 14
#2

Re: Voltage and Amperage reduction

03/05/2010 10:58 PM

Have you thought about a solar panel?

Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 10
#4
In reply to #2

Re: Voltage and Amperage reduction

03/06/2010 12:29 AM

Thanks! We already had some but the place is isolated and those panels were stolen...

Register to Reply
3
Active Contributor

Join Date: Apr 2009
Posts: 14
Good Answers: 1
#5

Re: Voltage and Amperage reduction

03/06/2010 2:15 AM

I think you have 250VDC power and it drives a motor with load of 90A. Check whether a pully can be fixed to the shaft of the motor. If yes, then think of connecting an " Alternator with a regulator" to the pully, then every time you run the motor it will drive the alternator and it will charge the battery. The Alternators in different Capacities, hence you can select 12V, 10A Alternator.

This arrangement is available in Vehicles, ships etc.

Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Mar 2010
Posts: 10
#7
In reply to #5

Re: Voltage and Amperage reduction

03/06/2010 1:37 PM

Thank you!

Register to Reply Off Topic (Score 5)
Anonymous Poster
#6

Re: Voltage and Amperage reduction

03/06/2010 5:16 AM

Or solid state- Inverter+step down transformer+ rectifier.

Even DC Voltage choppers are available which will give you lower voltage once the output is smoothened (filtered)

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Mar 2010
Posts: 10
#8
In reply to #6

Re: Voltage and Amperage reduction

03/06/2010 1:38 PM

Thank you!

Register to Reply Off Topic (Score 5)
Anonymous Poster
#12

Re: Voltage and Amperage reduction

03/07/2010 3:48 AM

Hello the issue is relative simple to be solved. All AC driven switchmode power supplies have a rectifier at the input - so if this international operation notebook battery charger is capabile to handle for instance 100V to 270V - which is rather common (Notebooks etc). The 250V DC at you motor will be inside the permissible range of operation (AC 240V is internall rectified so the the operating voltage inside the notebook power supply is much higher anyway!)

You should be able to hook up the power supply mains cable (life and neutral) directly to the DC voltage. The power supply can be connected to the DC Voltage without any problems. The build in rectifier will even make sure that you do not mind about the voltage source DC + / - pole. The rectifier will make that the flow of the current is correct. If this notebook power supply is choosen to provide e.g 13.8 Volts you can use a cheap battery charger with 12V input (available in Marine / boating / toy model stores) to charge the battery.

But it needs to be a widerange 100 to 270V AC note book power supply and use for safety reson a fuse in front of it.!!!!!

Register to Reply
Active Contributor

Join Date: Apr 2009
Posts: 14
Good Answers: 1
#16
In reply to #12

Re: Voltage and Amperage reduction

03/07/2010 8:37 AM

I think this will not work for two reasons. First is that Notebook power supplies operates on AC, which means that the input is AC, but here we have 250DC. I don't have any idea about DC to DC rectifiers (If I'm wrong please correct me). The second is that current handling capacity of the Notebook power supplies. Generally Notebook power supplies handle less current than 10Amps. But our friend needs 10Amps, hence again I think notebook power supplies will not work.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#17
In reply to #16

Re: Voltage and Amperage reduction

03/07/2010 1:26 PM

As Guest indicated, the AC is normally converted to DC, so yes, the inverter in the notebook power supply can be made to operate on DC. I have several notebook supplies that are rated 90-240VAC input. I haven't yet taken one apart, so I don't know the voltage rating of the capacitors and other components inside, but it is common practice to simply pass the supply voltage through a bridge rectifier, producing a DC voltage significantly higher than the RMS voltage of the supply. If you put DC into the rectifier, the rectifier will drop the voltage slightly and guarantee the correct polarity, again as guest indicated.

As to the 10 Amps, is that the charging current for the battery, or is it the current required to be drawn from the battery? if it is the latter, then the 1-3 Amps commonly provided by a laptop supply would charge the battery quite nicely. Obviously the current available depends on the particular supply.

This is not limited to notebook/laptop supplies. Many desktop supplies are now made for universal input as well, but they may or may not have the output voltage you need. Laptops commonly use batteries in the 10-20 V range, so a laptop supply is probably the most appropriate, if you can be satisfied with their current output. It will just take longer to charge if the current is lower.

In any case, you do need an appropriate charge controller for whatever kind of battery you are using.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 10
#20
In reply to #17

Re: Voltage and Amperage reduction

03/07/2010 6:40 PM

Thank you! The 10 Amps is the MAXIMUM allowed to charge the battery. A charge above that will damage the battery! The electronic device that will use the battery has a load of 3-5 Amps.

Thanks again!

Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#21
In reply to #20

Re: Voltage and Amperage reduction

03/07/2010 7:32 PM

Cheko Try looking a bit further. The Phoenix model charger also has a universal input and can handle as high as 400V DC input Furthermore both Skylla and Phoenix models can be used with a remote control panel that has a control knob that reduces the maximum output current. Although this is intended to reduce the load on the incoming power supply it can equally well be used to limit current to protect the battery being charged.

Both Skylla or Phoenix will work but the Skylla has digital control whereas the Phoenix is analog. The Phoenix also has an analog meter on the face which may be of use to you. both units have adaptive charging.

As I said to begin with; download the data sheet and READ it completely. If you have 250 V DC as your supply and desire to charge either a 12 V or a 24 V battery at a maximum rate of 10 amps then the Victron products are ready made for your application. No need to reinvent the wheel or custom make something special. The controller can dial down the amps to whatever you want.

Just order it off the shelf wire up and GO!. Victron is used and sold around the world. Designed in Holland but built in India. I use their chargers and inverters because no matter where in the world my clients are located the equipment will suit local power supply.

At present I have systems being built in Turkey, China, and the USA, all of which use the same type Victron equipment and is purchased locally. Now if you happen to live up the Amazon or Zambezi river delivery is going to be a bit longer but in most countries where they already have electric power you can expect reasonable delivery times.Can't vouch for what customs will charge. One good thing about Victron is the fact they use switching technology so is lighter weight tjhan comparable old style transformers equipment. Weight saves on freight bills.

__________________
Elnav
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#24
In reply to #21

Re: Voltage and Amperage reduction

03/07/2010 9:10 PM

you will need minimal 13,2 V for Lead Acid and to have a complete load 14,4. Lead acid doesn't like the 10 amps at the end.

__________________
Plenty of room here
Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#33
In reply to #24

Re: Voltage and Amperage reduction

03/08/2010 2:55 AM

Which is why these chargers have adaptive charge regimes. It is common practice to only state the maximum bulk rate knowing that All batteries require tapering off towards the end of the cycle. that is what adaptive charging mean. Depending on where you set the limits and transitions you can also charge a battery that requires a nearly constant current right to the end and these chargers have a temperature sensor so as to avoid over heating the battery.

This technology is a decade old. Doesn't everyone know about it and use it?

__________________
Elnav
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#35
In reply to #33

Re: Voltage and Amperage reduction

03/08/2010 6:11 AM

Regards.

Constant current chargers are suitable for LeadAcid batteries as charging alone [Not in an automobile or as in Back-ups].

these types are used from the 1970s/ or sometime before when NiCd batteries came in. But these chargers have timer to bring it to trickle charge after specified time.

LeadAcids are charged on contant voltage; as the condition of battery improves it end voltage rises charging -current decreases and at full charge condition the current is as low that it does not damage the battery even if remains on charge for long times.

These barries raise the end voltage linearly with actual charge.

NiCd & latest batteis has a problem of raising end voltage almost instantly [say some minutes of charge] so cannot be charged on CV but need CC chargers.

There are lots of other refinements in these chargers like sequencial testing on load condition etc etc.

Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#38
In reply to #35

Re: Voltage and Amperage reduction

03/08/2010 10:29 AM

okay, so what is it about the Victron chargers you don't like and why don't you feel it is suitable to the intended application?

__________________
Elnav
Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 10
#29
In reply to #21

Re: Voltage and Amperage reduction

03/07/2010 11:06 PM

Thank you very much! I found the information and that's what I´m looking for.

Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#34
In reply to #29

Re: Voltage and Amperage reduction

03/08/2010 3:02 AM

Cheko have a look at the Skylla. It also has provisions to work as a power supply without a battery being needed. I sometimes use it as a battery substitute when the old battery is toast and the replacement has not yet arrived. Very handy product.

__________________
Elnav
Register to Reply
Anonymous Poster
#13

Re: Voltage and Amperage reduction

03/07/2010 4:51 AM

I read and eyes can not believe how simple answer to a small problem, you can create a whole poem.

Firstly - the battery is charging current pulses rather than voltage.

Secondly - this engine is the only source of electricity, which does not draw more power than it determine its parameters. Less power, you can always download.

Thirdly - the best charger is thyristor device, because here it is easy to adjust the pulse width or duration, and amplitude or volume of electricity. Also the supply voltage input can contain virtually within 5 VDC to 400 VDC

Fourth - in the network are presented of such schemes chargers and adapt them to suit your needs should not be difficult, even for non-expert.

regards

Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#18
In reply to #13

Re: Voltage and Amperage reduction

03/07/2010 3:58 PM

Please read the original post once more.

Have another poem & its last stenza is

" supply is 250V DC DC DC who has converted it from AC AC AC !!! "

Have a nice day !!!!!

And where fits Thyrister in AC excpet GTO which is itself a complicated one.

And if it had died out I am out of touch for some time !!!

If somebody gives it latest position in Power-Electronics !

Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#14

Re: Voltage and Amperage reduction

03/07/2010 6:10 AM

Lot of DownConverters may be in market.

Ask for your requirements:

zahn@zahninc.com

Register to Reply
Anonymous Poster
#15

Re: Voltage and Amperage reduction

03/07/2010 7:36 AM

220-250volts entry/12amps maximum if it fits your needs,look for in the web;electric charger 12 volts, maximum 10 amps

when amperimeter shows 10 amps.u stop it

I hope this helps u

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#25
In reply to #15

Re: Voltage and Amperage reduction

03/07/2010 9:12 PM

If a transformer is present, don't use it.

__________________
Plenty of room here
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#28
In reply to #25

Re: Voltage and Amperage reduction

03/07/2010 10:54 PM

Your post is incomplete! Virtually all switching mode supplies use a (high frequency) transformer to step the voltage up or down after the switching device.

What you should have said is something like: "If it has a 50/60 Hz input transformer, don't use it.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#31
In reply to #28

Re: Voltage and Amperage reduction

03/07/2010 11:34 PM

Virtually: except the algorithm "n"th order harmonics chopper, that only has coils, resistors and capacitors. Your comment however is (virtually) appreciated.

__________________
Plenty of room here
Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#19

Re: Voltage and Amperage reduction

03/07/2010 4:24 PM

Checko; Go to www.victronenergysystems.com website. click on Pruducts then Chargers and you will see they have a Skylla model charger which is advertised as universal input. Not only will it accept any frequency and voltage from 90 to 265 V AC but it can accept 200 volt or so as well. Read the specs carefully data sheet is downloadable.

I suspect this is going to work for you.

__________________
Elnav
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#23
In reply to #19

Re: Voltage and Amperage reduction

03/07/2010 9:00 PM

DC - choose it has no frequency DC is not transformable with AC equipment such as transformers only.

__________________
Plenty of room here
Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#32
In reply to #23

Re: Voltage and Amperage reduction

03/08/2010 2:48 AM

Try reading the whole thread. He is looking for a charger for a battery that is powering a computer. Doesn't matter what the battery is the Skylla is programmable for any battery voltage you can possibly want within th enominal range. Go look at the data sheets which details the adaptive charging routine for these chargers. I have been using these chargers for many years now and doing things conventional wisdom said was not possible. Yes I realize transformers are not usable on DC but these are switch mode designs and somebody else mentioned that for this kind of applications you need switch mode. design. Running a belt driven alternator from the 250V motor is a needless complication.

__________________
Elnav
Register to Reply
2
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#22

Re: Voltage and Amperage reduction

03/07/2010 8:56 PM

It is not THAT simple. First you need to let us know, besides your max. load current, how big your battery is. This is expressed in Ah (Amperehour = the product of the loading current times the time to reach full capacity) Second tell us what type of battery you are using. Is it Lead-Acid, wet or gel, deep-cycle or not, is it NiCa or someting else, and how do you organize your consumption? Your battery will only work long when correctly handled. How many hours you need the battery and how many hours do you run your motor? You have many ways to load your battery, but giving you a solution depends on the information you supply. -You can: work electromechanic: let a 12 volts alternator spin when the motor runs. Have the regulator do the job to charge a Lead- Acid battery. Stick one or several magnets on the pulley and capture voltage with a coil. work electronically: You have 250 Volts - that is 250/ 14,4 volts= 17,36 times to much. You can chop your DC and use only that part to send to your battery. Practically you better send it to a electrolytic condenser (rated about 300 volts) This condenser (parallel to the battery tries to load up to 250 volts with the battery) You need a thyristor and a trigger device. And also a switch at 14,4 volts to disconnect the system when the battery is charged. This is a cheap solution but requires some "standby testing". Do not start this up unless you know how to go. Here you have very little loss. (heat dissipated to the heat sink of the thyristor) Stepping down with a resistor is throwing power away and create a heater. Existing chargers, the so called chopped ones, do not all step down in the DC section, but in the AC part (compare with a triac- based dimmer) Before using this, do your homework. Give us some more info to work further.

__________________
Plenty of room here
Register to Reply Good Answer (Score 2)
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#26
In reply to #22

Re: Voltage and Amperage reduction

03/07/2010 10:13 PM

You're absolutely correct. You get a GA from me.

But I asked what battery type would be charged in the very first reply. Still no answer.

I warn you, often critical questions don't get answered by people around here, particularly guests. If you stick around here, you'll find lots of people with little understanding of what they're really asking for. You try to get the truly pertinent information out of them to either do the whole design for them or what I try to do is help them to realize what they're asking. Occasionally if you're lucky you find somebody whose temporarily lost in solving there problem and you can help them find their own solution. These instances have made for me many a good friend here, albeit sometimes an anonymous friend but still a good one.

As long as I don't see the potential for a really hazardous situation happening or the possibility of a flagrant criminal act, I let people wander off with the fraction of my knowledge they could grasp without answering my questions. Maybe they'll try to implement the basis of my idea and only realize they have only part of the story when a minor part quickly fails. Like burning up a quarter watt resistor because they didn't realize the value was right but it would briefly try to dissipate ten watts, or in this case boil the water out of a lead acid battery. Remember, we all did something in hindsight dumb because we didn't listen completely to somebody who knew better. I know I've seen many things literally go up in smoke.

Cheko here while not completely forth coming with all of the pertinent information, has been very pleasantly polite. I appreciate that. In hindsight I should warn Cheko that wiring to the supply side of a 250V DC motor that draws 90 amperes can be much more dangerous than he thinks and trickier for a power supply to deal with the wide variations in voltages that will happen in normal operations. For as I mentioned earlier, a motor will also act as a generator. When the power supply is turned OFF, the motor will not instantly stop moving. The motor with at least the stored kinetic energy of its rotor mass and anything moving attached to this rotor shaft will now become a generator until all of this kinetic energy dissipates.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#27
In reply to #26

Re: Voltage and Amperage reduction

03/07/2010 10:29 PM

Maybe we should ask where he gets the 250 Volts DC from? Is it a remote nuclear plant? GA to you too.

__________________
Plenty of room here
Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 10
#30
In reply to #27

Re: Voltage and Amperage reduction

03/07/2010 11:22 PM

Thank you both! Thank you all!

I don't have the battery yet, and originally I was thinking in using a deep cycle, but that is the easiest part.

"elnav" recommendation is to use a Victron Battery Charger. I found the specs for that equipment and it is capable of doing what I need it to do, so I'll look for a battery that works better with those chargers.

Thanks again to all of you for all your suggestions and recommendations to help me solve my problem.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#36
In reply to #30

Re: Voltage and Amperage reduction

03/08/2010 7:36 AM

You are very welcome, Cheko.

I had a feeling from how you've handled yourself here that the unanswered question on battery type was because you were handling this part of your puzzle. You are by allowing this to be a degree of freedom in your system selection. I look forward to hearing about your final solution.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 10
#37
In reply to #36

Re: Voltage and Amperage reduction

03/08/2010 10:15 AM

Thanks! I'll let you know the final results of this solution. Thanks again...

Register to Reply
Register to Reply 39 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); Cheko (9); dkwarner (2); dvmdsc (6); elnav (6); Haajee (3); Neb Nolba (1); Paulusgnome (2); redfred (3); shyren (2); twomoons (1)

Previous in Forum: Battery Sizes and Codes   Next in Forum: ESP

Advertisement