ATLAS COPCO Voltage

03/06/2010 10:29 AM

Dear ALL,

We have air compressor of ATLAS COPCO with Electronikon Display. The motor used in the air compressor is 315 KW at 400 V and the current rating is 540 Amps. The problem is that when the compressor runs in loaded condition the motor gives imbalance of phase currents measured by tong tester. The phase currents on Red and Yellow terminals are 307 Amps while on Blue it is 295 Amps. The motor was already burnt and its winding was done a month before. But we also checked the same condition on the new compressor motor. Kindly suggest me the solution. Also tell the alternatives of options if you have.

Best Regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Jan 2010
Location: Bharuch , Gujarat , India
Posts: 17
#1

Re: ATLAS COPCO Voltage

03/06/2010 11:18 AM

Dear friend pls check your system voltage. New motor Resistance and inductance value chaeck with help of motor checker it should be ballance . pls sure that is there any D.C load or VFD connect same source . kindly give exact vale of system voltage , motor resistance , system harmonics . pls check Motor no load current . pls give result back all the best

__________________
jayesh b sathwara
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jan 2010
Location: Bharuch , Gujarat , India
Posts: 17
#2

Re: ATLAS COPCO Voltage

03/06/2010 11:21 AM

Dear friend pls check your system voltage. New motor Resistance and inductance value chaeck with help of motor checker it should be ballance . pls sure that is there any D.C load or VFD connect same source . kindly give exact vale of system voltage , motor resistance , system harmonics . pls check Motor no load current . pls give result back all the best

__________________
jayesh b sathwara
Register to Reply
Member

Join Date: Nov 2007
Posts: 7
#3

Re: ATLAS COPCO Voltage

03/06/2010 12:40 PM

The imbalance is less than 5% and that might not be such a huge problem (except some additional heating due to the slightly more pronounced negative sequence current. However, (a) are the line currents balanced in de-coupled condition? (b) what is the % imbalance when partly loaded? (c) is your system voltage fully balanced? (d) Does the compressor have a dynamically balanced fly wheel?

On receipt of your response, we should be able to look at the issue with more clarity..

Tilak Ghoshal

Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2010
Posts: 50
#4
In reply to #3

Re: ATLAS COPCO Voltage

03/09/2010 3:16 PM

Dear All,

Thanx for ur inputs. I have checked that motor in de-coupled position. The motor shows slight imbalance of current which is 192A in one phase and 212 A in other phases. We also checked the motor resistance and it was equal in every coil. The voltages are balanced.Kindly suggest more towards solution.

Best Regards,

AA

Register to Reply
Member

Join Date: Nov 2007
Posts: 7
#5

Re: ATLAS COPCO Voltage

03/10/2010 12:33 AM

As you can see, the variation in the NLC itself is more than 10%........motor winding resistance is so small, it will not tell you much either. What you need to check for really is the 'inductance' and there are instruments available for it. Also, have a look at the rotor for any cracks/partial discontinuities etc in the shorting bars (I assume it's a cage rotor). And above all, if the imbalance problem is being observed after the last rewinding, it might be worth having it completely re-wound afresh by a competent winder.

Tilak Ghoshal

Register to Reply
Register to Reply 5 comments